Best Of
Re: A2W heat pump as primer for 4 bank hydrothermo ( 864,000 btu )
Assumption is that COP of 4 would mean 50% cost of the BTU from heat pump.
Swapping 864,000 BTUs over to an a2w heat pump would require more land space, more money and more electricity than the building currently has available. Ideally we'd start with something and see how it goes before 100% committing. Too often projects are contemplated in an all or nothing scenario resulting in nothing.
We have our domestic preheating with 3 HPWTs before final heating with a gas hot water tank. The proterra units are each 4200 BTU. The gas hwt is 385,000 BTU. While the HPWTs aren't providing a huge portion of the hot water it did enable us to reduce from 2x 385,000 BTU tanks to one and leave the redundant one as backup. The setup likely was overkill to start with but the hybrid solution has saved ~10% off the overall gas bill with minimal impact on the electric side.
In order to justify the project I'd want to see making the money for the installation back in 10-15 years (ignoring interest). I can't see a full swap ever paying back so a full swap point could only happen once the current hydrotherm hits end of life. 1985 cast iron - it might be around for another 25 years? The heat pump tech is still in flux so it is nice to start small and realize the improvements in the technology rather than bleed out on the cutting edge.
The HPWTs are an easy win as they are used year round whereas the boiler is only used Oct-April and I think the heat pumps will generally have a hard time heating water at 127F a lot higher before the boiler while maintaining a high COP.
My sense is that given the project requirements a heat pump can't work for this application but I thought I'd post and get a sense from the experts. Can assume 46F+ as air temperature during the majority of the heating season.
Re: In imminent danger of house freezing (Minnesota) - solutions?
Chances are the right guy could get it running. Sounds like the "TECH" that looked at it couldn't be bothered
Re: 2 Pipe Steam Boiler Pressure Reading 8psi
show us the Ptrol and pigtail, and the sight glass
Re: troubleshooting milwaukee press tool 2763-20
send it in to be factory rebuilt or replace it.
if it’s not right the liabilities are high.
pecmsg
Re: Insulating steam pipes in the basement
First question: is your basement warmer than you want/need it? If not, forget the insulation. If you do decide you want your basement cooler, get it from this place. 1" is fine
Re: Burnham millivolt replacement gas valve, part discontinued?
Maybe this will help you troubleshoot.
The parts you may need are available. You will have to search for them as millivolt is not common for boilers any longer. @Tim McElwain
Re: Burnham millivolt replacement gas valve, part discontinued?
You need to start by measuring the output of the thermopile. You may have a bad replacement or there might be a problem with the pilot burner or where it is located in the pilot burner.
You will need a good gas tech if you replace the valve to set it up properly.
Re: Boiler is gurgling and wont run
there are some treatments for copper boilers that you inject and leave in. It cleans and keeps particles in suspension. Silver King was one brand. They have a nice hand pump also.
I prefer to run a cleaner, flush, refill and add a conditioner. I like to see the crud flush out.
If air is purged out, and pressure is adequate, based on age, dirty heat exchanger tubes are common in that type of boiler.
hot_rod
Re: In imminent danger of house freezing (Minnesota) - solutions?
Why don’t you have the house winterized?
Pipes drained and blown out with air, then filled with antifreeze. Make sure you get someone who’s competent and thorough.
There’s no cheap work around if you need a new boiler. Maybe look into financing options.