Re: Replace: TPR valve or hot water heater?
Do you know for sure that the pressure in the expansion tank was checked? It might not be set for the correct pressure needed for your system. Also, I have had new bladder tanks where the bladder was stuck to the side of the tank, and therefore not working. One way you can possibly check that is to close the feed valve to the water heater and open a hot faucet. If you have good pressure for a few seconds, and then it just dies, then the tank is probably fine.
Rick
Re: Dual Element Smith HE2 Baseboards
No not an option. I the bathroom is only have about 3 wide x 6ft and in the other area 24" is my max width by 24 high and 2.5 in deep.
So I think given what everyone has stated i can y the feeds on supply and return and probably be okay. Since I am early in this loop feed. I am still going to check my water temp at first rad and last fin in the series but I think as long as I stay within 10 degrees I am good.
Thanks
TerrS
Re: Can a new steam system be installed in a new residential house?
Good question! No. The building has a boiler. So I guess it was a whole system…minus a boiler. I cheated.
JohnNY
Re: Copper pipe radiator design
@Intplm. , after doing some math, I give you credit and I think I'm going in that direction. The piping only would cost me almost $300. I actually have a small baseboard radiator already that is wrongly sized for where it's installed, I could put that in the bathroom and swap it out with a more appropriate size in the original location.
Re: Viessmann Vitocal AWHP for hydronic baseboards or retrofit floor heating?
I would first do a heat-load for the home
Make any energy upgrades, you can. The lower the heat load the better tir the hp and energy cost going forward Then determine how much fin tube you have. The actual fin, not just the enclosure
Then use an output chart to see how the fin tube matches the heat load
Dual fuel is a good option if the HP cannot make the load in the coldest periods
I have that exact HP in my shop. With radiant slabs I can run the system 115f or lower
hot_rod
Re: New build radiant infloor 3 out of 5 loops not getting flow
Just to be sure. When you tried blowing through them, did you have the other end opened, for sure? If you did it one at a time , and only took off the line you are using, maybe something is crossed. In the bad situation you are in, I would take every line off and use air on each one to make sure both ends are open. I have a hard time believing you had that many loops get that compromised.
Rick
Re: Expensive Check Valve
I added a pump to the zone that wasn't heating and installed a pump controller. And I left the existing zone valves operable at hr's suggestion that they provide a reliable check valve.
The hard part was the wiring: I only wanted the pump to come on after the zone valve was open. At first, I thought about adding a RIB (Relay In a Box), but then thought that I could do it with just the bare bones pump control and came up with this. Seems to work fine.
Re: steam radiator leaking water from the vent
unless it’s the makeup water valve on a steam boiler. Eventually it would certainly increase the pressure in the system! Right about the time water started shooting out the vents 😅
Re: Baseboard heaters lukewarm despite boiler being hot
the circ inside the boiler needs to be a non ECM type
It has a tekmar variable speed control operating it, so only the old style PSC pump will work
Grundfos 15-58, 007, Wilo Star 21, etc
In a bind you could jut wire a cord to the pump inside the boiler and let it run until you troubleshoot the control
hot_rod