Re: Favorite Primary Control
I guess I like the Carlin 70200 a little better than the adjustable safety timing of the Mercoid JMI Pyratherm. There have been more that one occasion where the diagnostics have helped me find something wrong with a burner that was intermittent, just by scrolling thru the past fault messages stored in that control. I like it better than the Beckett and Honeywell/Resideo
But somehow I still am amazed by those tilting mercury switch relay contacts in the Mercoid. It kind of reminds you of a pinball machine flipper, and the little spark inside the glass tube making the connections. Todays technicians will never experience that joy of watching the mechanical pieces flip and flop to make the world a safer place for us all.
Re: The Case of the Short-Cycling Boiler – Causes, Damage & Fixes This weeks video
@jesmed1 Thats some good detective work Its rarely one issue Its usually from years of someone tinkering
Re: The Case of the Short-Cycling Boiler – Causes, Damage & Fixes This weeks video
Thanks for that video, Ray. When I began maintaining the heating system in our 4-unit condo building with 2 Weil-McLain WGO-5 boilers and original gravity-conversion hot water radiators, I realized both boilers were short-cycling.
Your title "Boiler Room Retective" is very apt, because some of the reasons for the short-cycling were not obvious and took some sleuthing. The one that took me longest to figure out was the improper placement of both thermostats. The installer had conveniently run the thermostat wires inside one of the chases where hot water risers go up to the second floor. So of course, the thermostat got installed on the wall right at that chase location. When the heat came on, the riser heated the wall behind the thermostat, causing it to satisfy before the room reached the setpoint temp. That took an IR gun to figure out. The other factors were more obvious.
In the end, we had 4 factors contributing to short cycling:
- Oversized boilers (4x actual building heat loss at design day temps)
- Thermostat left on factory default setting for forced hot air, which resulted in too small a differential
- Thermostat improperly positioned on internally heated wall
- Draft inside wall blowing air into back of thermostat (fixed by foaming entry hole around Tstat wire)
The hardest problems to solve are the ones where you start with the default assumption that there's only one cause, only to find that you were wrong, and there's actually 2, 3, 4, or more contributing factors. I expect you've seen a lot of those in your career.
The Case of the Short-Cycling Boiler – Causes, Damage & Fixes This weeks video
Boiler short cycling is bad I've been told my entire career but they never explained how to identify short cycling and why its bad. This video helps you identity short cycling, why its bad, and how to remedy or at least reduced it.
Re: Gorton vents is there a way to test them?
The water isn't going to be boiling. It will be hot(ish)
It don't have to be fancy!
Re: Lord willin & no snowmaggedon next wkd, eating & cooling breakfast is back Tues of AHR EXPO
had coffee without caleffi today for the first time in a few daze cause i'm home, but look what @hot_rod cooked up besides the cappucino. convert from multiple pumps to multiple zone valves:
albeit coolest find of the show because of my interest in flammable refrigerants was spacepak R290 5 ton chiller style heat pump. still waiting to get the COP curves but 167deg F out. once they get me a cut sheet and availabilities i'll post.
they recommend 35% 1,2 propanediol (PG) for burst vs freeze protection since you are going to be in heat mode enough to keep it from slushing anyway unless something goes wrong in which case you want to protect against burst because of the portion of the hydronic circuit that is outside (although 1,3 propanediol (PDO) has lower viscosity. a little harder to find a direct specific heat comparison although AI says the thermal properities of PDO are superious. it's more expensive albeit less toxic. I wish I had spent more time at a few chemistry booths although we got installer show at javitts and eastern energy at mohegan sun coming up. don't know how many chemists will be at those.
I'm really impressed although i'll be even more impressed when they start using the lowest pressure isomers like isopentane because I think with the lower pressures you could even more easily make service compenents with isolation and modular unions that wouldn't be subject to leaks in the comparatively lower operating pressures. but guy at booth (damnation thought i got his card) said they didn't want to be too exotic seeming and propane has bigger installed base at the moment. true isopentane is more expensive but we're talking $400 for a metric ton of propane, $1300 for a metric ton of isopentane and $55,000 for a metric ton of R32- just sayin'.
brian
A little history recap
When you are prepping to teach you revisit the trusty beginnings (at least it was for me 20 years ago).
Steam venting from old vent on top of converted coal boiler
Hello all.
Relatively new first-time homeowner — this is my fourth winter in the house. I appreciate any help or advice.
I have an original coal-era cast-iron steam boiler in a 1925 Brooklyn house, converted to natural gas. It’s a one-pipe steam system with a pressuretrol on a pigtail, sight glass, and manual water feed (no automatic feeder). The boiler still has the original coal-era vent/cap on top.
Current issue
Steam is coming out of the old vent on top of the boiler. I believe this may have happened in the past (possibly during very cold spells), but under more typical Brooklyn winter temperatures I haven’t really noticed it.
Here’s what I’m seeing
- The steam sometimes sputters (steam with water droplets)
- Steam from that vent only occurs while the boiler is firing
- The steam stops completely when the burner shuts off
- Some radiator air vents vent small amounts of steam when this is happening
- Boiler water level in the sight glass remains stable
- The boiler continues to heat the house
- The issue is more noticeable during very cold weather with long run times
Questions
Anything I should be checking or doing immediately? What should I be looking at in the short term?
I do plan on updating the system, but that’s probably a separate discussion.
Pictures Below 👇
Thanks in advance.🙌
John B.
Re: How Do I Connect This Wire?
Well I am WHELMED with this response. I can't say overwhelmed since there are only four of you responding. Now if it were maybe eight of you then I might be overwhelmed but for now I am just whelmed. And I thank you all for your encouraging responses. I added another chapter today. it has to do with the old ways…. here is the first paragraph:
Chapter ? old forgotten ways
And new ways to trouble shoot, with new tools
When this idea was presented to me by a member of HeatingHelp.com this memory came jumping back to me. When I was a wee lad and Dad brought me to work on a Saturday, My job was to sweep the yard and empty the trash cans. I was able to meet the different employees and I remember a service technician named Howard Levy (pronounced Lee Vee) who had an index finger that was partially missing. Howard would test the electricity on a control or in a light socket with the index finger stump by touching the metal conductor. If he did not feel the current tingle on his finger, then he would put his finger in his mouth to get it wet for a better connection, and try again.
“Yep the switch is on. Can you go over there and shut the switch off so I can work on this control wiring?”
Let's see how this goes.
Re: HELP - I've had to replace my gas boiler TWICE - every 10 years
yeah we’d have to know how much water you were adding, that’s the number one metric that matters in my mind.
I can’t imagine those two boilers rotting out in 10 years without a massive amount of makeup water, regardless of your local water quality.
Did the peerless crack, or did it get a hole rusted through it? The difference is important
Also, is this steam, or hot water we're talking about? Although the concerns about fresh water are there for both kinds. Edit: OK it does seem to be a steam boiler situation