Re: Main vent recommendation?
You aren't likely to ever see any pressure difference between the boiler and the end of the main, not in a house anyway.
Re: trying to understand steam heating
@DanHolohan 's "A one pipe system will often add humidity to your home whether you want it or not" is a joke. He is saying it will add appreciable humidity if it is leaking somewhere. If it is working properly it should only lose a small amount of water, like a gallon to a couple gallons a month, not enough that you have to feed it every day or even every week. If you have to add water more than once a month you have some sort of leak somewhere.
The water should be boiled in to steam in the boiler, be condensed back in to water in the radiators(and a little bit in the piping) and that liquid water should return to the boiler through whatever return system that particular system has, either dedicated returns or through the main to a return at the boiler or some combination of the 2.
It is essentially a closed system except it fills with air when it is off and that air is vented out when the system is running to make space for the steam. A little bit of water evaporates in to that air that is vented out, that is why you lose a little bit of water.
If you are adding water every day either you have large steam leaks and will likely have condensation on walls and windows and such, it is leaking out of a buried return where you can't see it, it is leaking out of a hole in the boiler and up the vent, or it is coming out of a vent or a relief valve as liquid water.
Note that on one pipe steam a partially closed radiator valve will frequently cause the radiator to fill up with water, valves must be all the way open or closed on one pipe steam.

Re: Types of Radiators
Then it is in the wrong spot. Up top it will tend to close prematurely before the radiator is properly filled with steam. This effectively makes the radiator smaller. What vents do you have on those small radiators? When you say they are making the hissing "when the heat first on" do you mean when first on during a morning recovery?
Re: BEST BOILER FOR NEW CONSTRUCTION
So many good boilers on the market. A mod con would be my choice for a radiant slab application.
I have used a number of the Lochinvar products, with 0 problems. The Knight series is a great unit, floor or wall mount. Built in Tennessee.
Ideally you would run a heat load calc to size everything. A wild guess around 60,000 BTU/hr?
I'd look at the Knight 85,000 BTU/ hr.

Re: Monoflow system does not heat well
Can you measure the temperature difference between supply and return water? That would tell you if there's a flow problem. Since the system is pressurized a high limit of 200° F should be fine.

Re: Leaking new vents?
At those pressures I wouldn't expect any hissing, and even less so at the start of a call for heat when the radiators are still getting heated by the steam. Closing off 1/3 of your radiators, though, will make your boiler even more oversized than it already likely is and that's not advisable.
Re: Mod Con Boilers Ranking
My picks from owning an HTP and reading the comments here would be Lochinvar, HTP, and Viessman. I think some of the HTP stuff gets rebranded under other names.

Re: Bleed air from gas boiler hydronic heat system
I don't see that working if the loop is totally air locked. If no water is moving air can't migrate back to the boiler.