Re: Debate me Bro-3/8 inch pex 150 foot lenths AOK for high delta T radiant
All of my radiant projects that are underfloor are done in 3/8" pex. So much easier to run compared to 1/2".
Yes, your loop lengths will be shorter compared to 1/2" but your delta T should still be 10-15 degrees for the comfort factor and maintaining an even surface temp of the floors.
The average loop lengths from the manufacturers are based upon standard, safe circ selection without having to go to crazy high head circs.
But if you do the math, you can go past the recommended lengths, in my own house, I installed 3/8" underfloor (with and without plates) with 400' loops and a standard circ.
I used 1/2" for my slab for the same reasons, I wanted longer runs and less connections to a manifold and less actuators. I wanted to make sure each room I was installing tube in that it had one loop instead of two (easier all around)
Dave H_2
Re: Repiping monoflo returns, how does this look?
MonoFlo® systems are not a purgeable design. Each radiator must be vented individually. Purging implies that you are forcing water thru a loop to entrain the air and cause it to exit at a valve near the lower end of a system. This only works on a series loop. When there are tee fittings in the mix (like MonoFlo® tees) the water has two paths, and the water will take the path of least resistance, and the other path will stay air bound.
Can you explain to us what you are attempting to accomplish?
Re: Wirsbo Manifold Pin Valves
I can't believe they are not all broken yet.Agreed.
I had a couple where the plastic frame/shuttle inside broke.
Many where the end switch got carboned up and started chattering my relays ( replacing the internal end-switch on a bunch ).
Finally got tired of doing the switches and started swapping out to thermals.
Thermals are soooo slow, but they just quietly do their job.
FYI, the adapter to make a thermal actuator fit those valves doesnt come with the thermal.. it's a different ring.
Re: Honeywell Media Filters GAP at the door
Typical of the Junk they make today. Save $.10 cents and be a hero. No common sense and inadequate factory testing. bean counters and engineers.
Re: Oil Water Heater for Disabled Couple on Long Island
Oil Heat Cares?
Re: Radiator conversions in Canada?
An electric resistance heater by any other name… will still use a lot of electricity!
Re: Gorton #2 or Hoffman 75
Multiple Gorton #1's as they appear to be more reliable.
I could never justify the cost and vent rate of a Hoffman 75.
ChrisJ
Re: My three worst jobs sites. What are yours?
any home or building that need a sewer ejector pump service or replacement
hot_rod
Re: Dunham valve rebuild?
i thought the air eliminator was essentially an f&t trap, but looking at the dunham catalog it is just a float to close off the return and let pressure build so that the condensate can return to the boiler if the water backs out to that level