Re: Delay of boiler firing?
You can try it with 1" but you may need to increase if you need more than 80,000 BTUh to heat your home. That 1" or 1-1/4" is not written on stone tablets that were delivered to a mountain in a desert.
The pipe sizing is based on keeping the flow speed below 6 feet per second in order to keep the velocity noise below a noticeable level. Above 6 feet per second will become loud enough to hear. It is not that bothersome when water moves faster than that 10 FPS when you open a faucet because the noise stops when you close the tap. With a heating system that noise would be unacceptable. The next thing is the amount of gallons per minute will flow thru the pipe and this is directly related to the FPS number. And finally the temperature drop (∆T Delta T) of that water flowing thru the boiler or the radiator as the amount of heat that is added or removed from the water. With the industry standard of one gallon per minute for every 10,000 BTU based on a 20° temperature change (∆T), we can come up with some rules of thumb for pipe sizing based on the amount of heat you need to transfer.
If you change the flow rate or the ∆T, you can also adjust the pipe size. So it is possible that 1” can be made to work for you by FPS or GPM, or by changing the ∆T in order to get the system to work.
For example you can get 100,000 BTU to go through 1” pipe if there is a 25° ∆T in the design. But when the water gets to the emitters (the radiant floor for example) it must move slower in order to release more heat to the floor. The longer the water stays in the emitter the more heat it will release. You also need to let the water stay in the boiler longer in order to change the ∆T in the boiler. So slowing down the water may be able to move more BTU through the smaller pipe.
The best person to make those calculations would be hot_rod if he is interested, since he does that stuff all the time, and I have stopped designing systems since I retired and might make mistakes and don't want you to rely on my numbers where dollars and cents are involved. But It may work with 1” with the proper flow and ∆T. It may also be just fine if you only need 80,000 BTUh on the coldest days. Without a proper load calculation, we may be discussing a point that does not really matter.
15 boiler room noises you should never ignore, this weeks video
This video was delayed because of a technical difficulty. I was babysitting the grandkids LOL Anyway thanks to @retiredguy for the idea. Have a great long weekend
Re: Delay of boiler firing?
One final note. this transformer is rated at 24v. 15 VA and may not be strong enough for the Honeywell thermostat, the Honeywell HPSR101 relay and the RIB U1C relay. If that happens you can purchase a 20 VA transformer that will fit in that same position. Amana 24v. 20VA Transformer from SupplyHouse.com. I think you should be fine, but if the transformer fails after a few months of use, get the stronger transformer.
Re: Thin Tube Steam/Hot water in Barre VT
No, Fix what you have. it would cost a fortune to make it two pipe and you will need a new boiler in the future.
Re: Thin Tube Steam/Hot water in Barre VT
You could make it 2 pipe but it would be a big job, a lot more than just moving some radiators a few inches. it wouldn't be worth it unless you had a good reason to do it.
the near boiler piping looks pretty close although a little odd, it is hard to see, it is probably close enough, especially on 1 pipe.
the biggest issue is the moisture in the basement and the rust on the boiler and what appears to be asbestos in poor condition with something over it.
make sure there aren't corroded and leaking returns out on the wet basement floor.
Re: Thin Tube Steam/Hot water in Barre VT
Don't think about going to two pipe. One pipe is a little trickier to get everything working well — but it does work perfectly well.
The two key things are venting — particularly mains — and getting all the pipe pitches correct or at least reasonable. From the time frame you are mentioning, I'm thinking that some main venting either isn't adequate — or isn't there at all. For radiators, the name of the game is getting each one heating the space the way you want it — and it's much better to start by slowing spaces which are getting too warm.
Re: Thin Tube Steam/Hot water in Barre VT
20 minutes to get heat.
i don't think the boiler replacement is far off with all that moisture.
Re: Thin Tube Steam/Hot water in Barre VT
Mostly looks like normal fiberglass insulation to me. If pipes were never painted they will rust after 100 years. Their exteriors don't mean much relative to state of system or boiler. What if any are the heating issues you are currently having? Can certainly help with your venting and balancing issues if you have any... You can do a leak test (fill till water in boiler comes up the riser) on the boiler to see if it is leaking. If it isn't it may be fine for a while.