Best Of
AWHP - Plate heat exchanger or not?
Hello,
I'm looking at options for air to water heat pump systems. This would be for space heat and DHW using a reverse indirect buffer tank.
Some manufacturers system designs call for the AWHP to directly heat the buffer tank, with the entire tank and hydronic zone loops being glycol mix. Other manufacturers (US Boiler) suggest a plate exchanger between the AWHP and the buffer tank, with glycol only in the outdoor heat pump loop.
If I understand, the pros for the exchanger are:
- Less glycol. A buffer tank worth of glycol mix isn't cheap, and if you need to drain the system, you would need to deal with all of that mix.
- Better heat transfer / easier pumping in the hydronic zones and indirect tank without glycol.
Cons:
- More parts: heat exchanger, additional circulator, valves, etc. Probably eat up the cost of glycol savings.
- Loss of efficiency through the exchanger, critical to get flow rates / Delta T correct.
Thoughts?
Thank you.
Re: Another glitch on a steam install
No. That's a Burnham V-89, and the outlets are tapped 2-inch.
Re: Another glitch on a steam install
Make sure they know you do steam.
That way when it's leaking in the near future you'll get the call.
ChrisJ
Re: Another glitch on a steam install
Can't see how the equalizer is tied in. @GW
The hacks get away with it all the time. Anything over 2" black is a foreign object to them. I thought I was the only one. If I had installed it like that the boiler would have likely blown up on start up.
Re: Another glitch on a steam install
Maybe you can figure out a way to tell them you know steam and if they have problems to call you.
Re: Weird Noise from 3/4" Wilkins 350XL Double Check Valve
A follow up … I installed the replacement cartridge and its quiet as can be! I will take the old one apart later, but I would guess that one of the seats failed. I guess that's why the sell these kits because nothing lasts forever, except for your marriage 😎
Re: PTAC Air conditioner Blower fan hitting cover
depends on how it is designed. since you have many of these, why don't you find a service manual?
Re: I'll Fix It, Honey.
Those thermostats and relay were common place when I entered the field in 1968. Look how far we have come! They were so easy to trouble-shoot, wire, and repair/replace. Those were the simple days.
Re: PTAC Air conditioner Blower fan hitting cover
The whole blower assembly should be removable.
HVACNUT
