Another glitch on a steam install
GW
GW Posts: 5,259
I was out this house today casing out air conditioning. The people just bought the home. A very nice home. I’m curious how this big old 9 section boiler wil gets its steam to the system
the header is supposed to be 3 inch, they bullheaded the 2 inch into one 2 inch connector, into the mains
Gary Wilson
Wilson Services, Inc
Northampton, MA
gary@wilsonph.com
    pecmsg Posts: 7,634
    not your job
    Not your problem
    wuyuzizi000
  • Ironman
    Ironman Posts: 7,975
    It’s also piped wrong with the main tapped between the risers.
    Bob Boan
    mattmia2wuyuzizi000
    If it works without problems, it serves to show how forgiving steam can be…
    wuyuzizi000CLamb
    "works" can have a lot of meanings. I wonder how close the output of that boiler is to the actual connected edr
    wuyuzizi000Ironman
  • GW
    GW Posts: 5,259
    yes and yes. It seems like if I goof something up, the demons and vipers are biting at my heels. But when somebody else does a goofy job, everything works out just fine.
    Gary Wilson
    Northampton, MA
    gary@wilsonph.com
    wuyuzizi000IronmanEdTheHeaterMan
    Maybe you can figure out a way to tell them you know steam and if they have problems to call you.
    GWwuyuzizi000
    Are those risers bushed down at the outlets of the boiler?
    wuyuzizi000
    Can't see how the equalizer is tied in. @GW
    The hacks get away with it all the time. Anything over 2" black is a foreign object to them. I thought I was the only one. If I had installed it like that the boiler would have likely blown up on start up.
    GWIntplm.wuyuzizi000Ironman
  • ChrisJ
    ChrisJ Posts: 17,763
    Make sure they know you do steam.
    That way when it's leaking in the near future you'll get the call.
    GWmattmia2delcrossv
    edited July 2025
    Looks like a reducer or bushing and tee at the end of the header to make sure no condensate or carryover goes in to the equalizer…
  • GW
    GW Posts: 5,259
    the header is full 2 inch, all the way to the 90 that drops to the equalizer. It’s turned 45 but it is not trapping any water.
    Gary Wilson
    Northampton, MA
    gary@wilsonph.com
    wuyuzizi000
    Steamhead Posts: 19,007
    No. That's a Burnham V-89, and the outlets are tapped 2-inch.
    Semi-retired
    mattmia2Intplm.wuyuzizi000
    It's butt ugly.
    wuyuzizi000delcrossvGW