Re: Unico potable water furnace, expansion tank pressure
whats the normal static fill pressure? and does this system also provide DHW or is it heat only? a boiler system on a with an attached fresh water supply would have a pressure reducing valve installed, is there such a valve on this system or is it just taking in city pressure?
Re: Unico potable water furnace, expansion tank pressure
you set the pressure to the required cold static pressure of the system if its a closed loop hydronic heating system . and you can only check or adjust this charge with the tank completely detached from the system
Re: Unico potable water furnace, expansion tank pressure
Hi, A couple of thoughts. Try putting a gauge on the drain valves of the tanks and measure the actual pressure. That might help in getting to the truth a bit faster… I would want a drain and waste valve installed between the expansion tank and system, so you can check/charge it easily… The pump is mounted vertically in a way that can trap air and damage the bearings. I'd rotate it to sideways… The pump is pulling water away from an air vent. If pressure falls low enough, it could pull air in and cause problems… The older tank is nearly ten years old. It needs a new anode! Also, it's time now to check the anode on the newer tank.
Yours, Larry
Re: Unico potable water furnace, expansion tank pressure
that just looks like a backflow preventer, nothing on the heaters side of the system to reduce pressure from the street? if there is no pressure reducing valve on the heater side of the piping, then you need to set the pressure to roughly your street pressure, and either way you will want a DHW rated expansion tank
Re: Unico potable water furnace, expansion tank pressure
Hold on. You’re missing something here!
The pressure in the tank is supposed to be set to match the minimum pressure in the system. In other words, the system pressure determines the tank pressure, not vice versa. Therefore, there’s no fixed (one size fits all) pressure setting.
It makes no sense to set it at 15 psi if the minimum pressure is 60 psi or more. That would greatly reduce the acceptance volume of the tank and render it virtually useless.
It would appear from your description of flushing minerals out of the tank annually that potable water is also being heated by the water heater. Correct? That’s unfortunate because you run the risk of Legionella contamination in the heater from stagnant water from the heating system. However, there are a lot of these types systems out there from days gone by.
At any rate, you need to find the static water pressure on the water heater and set the air pressure on the expansion tank to the same. That must be done with no water pressure on the expansion tank.
Your circulator is also mounted incorrectly. It needs to be rotated to where the motor is horizontal, not vertical.
Ironman
Re: Unico potable water furnace, expansion tank pressure
If this is correct — that is, if that valve is just a backflow preventor and not a pressure reducing valve, then the pressure tank needs to be set to the domestic water pressure when the system is cold, and the pressure tank needs to be certified to operate at that pressure.
Re: Domestic hot water
As mentioned by some contributors it could be the check valve in circulation pump causing the problem.
I had this similar issue when i descaled this unit back in summers but that time I flushed water out from the plumbing system and it worked fine after that.
I am probably going to call a professional to take a look what exactly is going on.
Thanks everyone!
Re: Notification bell not clearing
sometimes mentions don't clear first time, I usually don't follow a whole post though. i wonder if notifications aren't clearing when a "new" comment has been edited multiple times. I know there are quite a few times I might have edited a comment several times because I'm bad at proofreading before I click post lol