Best Of
Re: Sub floor radiant heat for primary heat source
You need to start with knowing what the insulation will be and doing a heat loss calculation, then you or someone else can use some radiant design software to design tubing to cover that loss.
You will have to insulate under the tubing to push the heat up through the floor.
It is done all the time with hardwood. I don't know what the limits on the surface or the tubing are. Not only will designing for too high a surface temp dry out the wood, it will also be uncomfortable to walk on.
Re: Sub floor radiant heat for primary heat source
Underfloor heat needs to be designed, there are no useful rules of thumb. It is possible for it to be the sole source of heat, it's also possible for it not to be, it depends upon your heating load and the layout of the house.
I would look at a system like Warmboard (not an endorsement, that's just the brand name of the most popular system).
Will you have air conditioning? It often works much better to deploy the heated floors strategically and supplement with forced air.
Floor thickness won't be an issue with doors, you can raise them. Where it may really be a problem is with stairs. Although if you do both floors you might be able to raise the entire flight by the thickness added.
Re: oops!!!!
Are there any more controls like this one? this is possibly the High Limit control but the setting is at 120° which in my mind is too low to be the HI limit
This photo indicates that your heating boiler is located near your clothes dryer, and that clothes dryer vent is allowing lots of lint into the boiler room area. All the telltale dust on the gas valve tells me that there is most likely dust on the actual burners inside the fire compartment, and the combustion air openings of the burners. That dust can lead to insufficient combustion air and incomplete combustion. That can lead to the boiler heat exchanger getting a build up of soot and carbon that will cause more problems that you do not want to deal with, some day this winter.
This shows that you have three 24 volt transformers. You only need one to operate that heating boiler. Without seeing the bigger picture I have to ask how many thermostats you have? That may explain the reason for more than one transformer.
But getting back to your wiring problem, If you have only one thermostat for the entire home, then at least one of those transformers is not for the heating boiler. So I am guessing that the door bell is connected to the transformer on the left That leaves the upper transformer with a relay, to operate the circulator pump, and the other transformer on the lower right looks like it has the same 3 wire that is near the high limit control in the top picture.
Now let's just say that you get a professional to come to make sure the 1949 boiler is operating safely and properly and that professional is not experienced on older model equipment. They might tell you that you need new equipment (and they would probably be right when it comes to operating cost) by telling you that this old stuff is unsafe. (that would be wrong information) and you didn't mind the "operating cost" gas bill which you feel is very affordable, and therefore no amount of fuel savings will justify the cost of a replacement boiler. You will need to know how to put the wires back…
I am only guessing at this point as to what you might have… but this is a safe wiring diagram that will shut off the gas burner in the event the water in the boiler gets hotter that the High Limit Setting. I would like to tell you the put the red wire here, and the green wire there but you only have gray wires, so I have placed colors on the diagram for clarity, but electric is color blind and will travel thru any color wire. I have made the assumption that the top transformer/relay is connected to the thermostat. When the thermostat calls for heat, the relay in the silver box will connect 120 VAC to operate the circulator pump. There will also be a connection in that same relay using low voltage (24 volts) to make the gas valve operate the burners.
This is most likely where you have the three disconnected wires. I have indicated that one of the three wires is Red and connects from the transformer to the R terminal on the aquastat. The W on the Aquastat will get connected to the TH on the gas valve indicated by the white wire in the drawing. Then the TR on the gas valve will get connected to the transformer indicated by the blue wire on the drawing.
I hope this helps. And I really recommend that you call a professional to check your boiler. It is probably in need of some professional maintenance. Hopefully you will get someone experienced that will actually do a good job for you.
Mr. Ed
By the way, when I did gas boiler maintenance I never found it necessary to remove the wires you removed. This might tell you something…
Re: Annual Tuneup, now horrible burning smell
Sounds like the boiler is short of draft. Has anyone looked in the chimney or checked it?
I agree the flue pipe should be fixed now but if only a small hole the draft should be pulling in not out.
@EdTheHeaterMan when I started they wanted me to do 4 a day. The stuff I worked on was 1920s and 30s equipment real soot makers and oil was cheap enough no one would buy a new burner until after the embargo.
Most days it was 3 for me
Re: oops!!!!
Take a photo of the burner control to which the wires were attached… and post that. And then figure out where the other end of each wire is and what it attaches to and post that. Someone will figure it out ( @EdTheHeaterMan is a genius at that!)
Re: Vacuum taking a long time to stop dropping
Moisture evaporating would be in the 1500 + range
pecmsg
Re: Taco Zone Valve hack?
even if DC it won’t work.
power open spring closed
Power closed spring open
pecmsg
Re: best acrylic tub
americast is a steel tub with plastic to keep it stable never been a fan of it. i always put something under to support it usally strucolite
Re: Finding replacement baseboard metal components
i once made wooden replacements for those covers after a contractor made off with the parts from our basement. Any metal replacements seemed crazy expensive at the time and probably weren’t going to fit right.
I was afraid they would warp out of shape but held up at least until we sold that house 5 years down the road. Hope they’re still doing ok.
That may not help you but its an idea if you’re stuck.
Re: Annual Tuneup, now horrible burning smell
I'll go with the tool. And you need to get your new man out there to find it and fix it.