Best Of
Re: Counterflow steam system
agree that’s why I’m here. Feel like I’m close. Most are saying never seen a system like mine so of course it’s going to take a lot of questions and back and forth. I guess I should have went with the 50s ranch with hydronic heat!
JoshP
Re: I'm getting solar panels. I'll let you know how it goes in this discussion thread.
Interesting that the went to the roof edge on the left side. I thought code required a walk path around the entire array. Maybe two sides is all that is required?
It passed inspection, so it must be code compliant, and they maximized the roof area.
hot_rod
Re: Undersized steam supply causes carryover, right? Right??
I really enjoy your videos. Is it practical to replace the bushing coming out of the boiler so that the supply starts out immediately reduced down? That would bring the higher velocity down closer to the steam chest.
Re: Undersized steam supply causes carryover, right? Right??
Your experiments are fascinating and entertaining… but, forgive me if I look at it from the standpoint of an engineer… you have too many variables involved to draw general conclusions, since your are not varying some of the more important ones.
As I have said, residential and small commercial heating steam systems are incredibly forgiving. Arrangements work just fine which seemingly have no business working at all, and which violate many guidelines. In fact, there aren't that many guidelines which really are all that critical.
That said, the guidelines and general rules of practice are of value, as coming reasonably close to them almost guarantees the system will work, at least "well enough".
Sizing steam radiators
: I need help sizing a steam radiator. the current radiator in the room is 16 sections, 26 inches high, 5 regular tubes. I'm trying to find out how many BTU's this radiator is and I want to replace it with the highest radiator available so I can maximize wall space. please help
thank you
Re: Radiator vent loudly sucking air INWARD after boiler turns off
You explanation IMHO is flawed. It's a matter of Physics that when the steam collapses the air has to get back in the system.
Do you agree?
Nothing in the statement you posted:
"It has to do with do you understand what is going on and what methods to correct it. If the pressure is high, lower it. If the vent is not operating properly, test it and replace it with one that was tested. If you need a steam control device to operate the boiler instead of a thermostat, get one. Basic problem solving:"
gives any information or tells anyone how to fix the problem we are talking about.
"It has to do with do you understand what is going on?
Yes, I do, the change in volume from steam to condensate is 1700x
"If the pressure is high lower it"
I agree low pressure is better in most cases. But as @ethicalpaul mentioned this has 0 to do with steam collapsing and the resulting vacuum.
"If the vent is not operating properly, test it and replace it with one that was tested."
Vents vent air and let air in. They close when they sense steam. They should not leak water. They should not pass excessive steam. That's all there is to it.
There is no mystery here. Air has to get back in the system when the boiler cycles off.
Re: Navien condensing boiler settings troubles
How long were your thermostat cycles when it was close to -23C that night? In other words, was the thermostat calling for heat for for 2+ hrs straight or did it cycle off? I'm wondering if you can turn down your high setting even further, below 72C. You might not know for sure until you have a design temp of -40C outside?
Turning that lower setting to 28C should really help out with the overheating problem you described. Is 28C the lowest option?
Re: Hydrostatic 3250-Plus C wire
You can get what Honeywell calls a fan center which is a relay and transformer in one.
The rib relay is about $20, a transformer is about $30 maybe. So a fan center is about the same $. I like the rib relay because it has an idiot light to tell you the relay is calling. A fan center complicates thing but thats just me.
You mount a 4" square box bring 120v to it. Mount the rib relay and the transformer on the box bring the thermostat wires to it and two wires to start the boiler and your done.
See the attached fan center
Re: I'm getting solar panels. I'll let you know how it goes in this discussion thread.
It's not a cult, I am free to leave any time.
Re: Navien condensing boiler settings troubles
Okay, here's an update on what I've done so far… From the service menu, I lowered the absolute minumum and absolute maximum supply temperatures to 28C and 72C respectively. From the regular menu, I set the outdoor reset to the user-defined curve, changed the outdoor high temperature setting(for outdoor reset control) to 18C, and disabled the WWSD function. From last night's low of -23C to today's high of -11C, the boiler seems to be following the thermostat setting nicely. Things seem to be on the right track now, but I'll have to wait for some wider variations in the outside temps to know for sure. In the meantime, I'd like to thank all of you again for the guidance and great suggestions you've given me!

