Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
If our community has helped you, please consider making a contribution to support this website. Thanks!
Best Of
Re: Black Iron Pipe Reamer?
what size pipe? I have a ridgid 2s that'll go to 2" when I don't feel like dragging along the 300. haven't seen anything for 2" that'll go on the end of a drill.
Re: Which brand and model of steam boiler is the most reliable?
In general you want to match the installed EDR to the boiler st ft of steam rating. If the boiler is too big it short cycles and operates less efficiently, if it's too small it may not heat the house on really cold days. Remember the boiler sq ft of steam has a 33% pickup factor for piping so the boiler actually produces more steam than the label claims. The steam piping in the cellar all should be insulated with 1" steam pipe insulation.
A gas boilers ability to heat the house does not change with age unless you have bad combustion or serious water quality issues.
If your more comfortable with a larger boiler and don't mind the fact it is less efficient that is your call.
Bob
A gas boilers ability to heat the house does not change with age unless you have bad combustion or serious water quality issues.
If your more comfortable with a larger boiler and don't mind the fact it is less efficient that is your call.
Bob
BobC
5
Re: A.O. Smith water heater. Big problems. No help. (JohnNY) **Updated 3/27/15, 11:30am**
UPDATE:
A.O. Smith sent a technician from their Field Service Engineering team and it was like someone had opened a window. Having a knowledgeable technician there who was proficient and savvy in the language and design of where the Cyclone came from and how it functions today, was a breath of fresh air and all I really ever needed to put this thing into a state of reliable function for the application.
I’ll refrain from direct quotes because I wouldn’t want to wrongly convey the sequence of operation of this unit on this forum. There are a lot of non-industry people here that might misinterpret and then pass on inaccurate information.
In a nutshell, the Cyclone is a gas flame-modulating unit, a function that ultimately saves fuel and is a proven method of accurately meeting and maintaining a target temperature efficiently.
In this case, however, modulation takes several things into account such as two temperatures within the tank, time that it takes for those temperatures to change, and an algorithm to provide a run time at a specific flame intensity to meet the current demand.
The issue is that in this, or maybe any restaurant, that demand changes sometimes drastically and at unpredictable points in the recovery process.
When the tank temp drops quickly due to a large and sudden intermittent draw the integral logic is sometimes “caught looking” when it should be swinging for the fence.
In this particular case, modulating flame is not the best technology and that process is the only difference between the new water heater and the one that it replaced.
In A.O. Smith’s defense, the fact is that if my water heater were significantly larger, this almost certainly would be less of an issue or perhaps not an issue at all.
As a professional, I specify and install conservatively based on factors like proven math for the application, performance history, possible future changes in demand, and cost, without giving in to the common compulsion to grossly oversize.
I am set to receive two new replacement parts that will allow me to eliminate modulation and have the unit run in high-fire at any call for hot water. The potential disservice is that the water temperature in the tank will almost certainly overshoot at times by a few degrees. Our previously installed mixing valve will greatly minimize any scalding risk at the points of use, so I’m not concerned.
Clearly I’ve been very vocal about this whole episode and I’d like to take this opportunity to thank all of you in this wonderful and unique community of industry professionals and lay persons alike, Dan Holohan, my wholesalers at West Side Supply (Bill, Jeff, Jerry) and of, course, A. O. Smith (Thank you, Scott. Your professionalism is rarely seen these days) for all your support and for lending an ear.
When I get my new parts today or tomorrow, I’ll consider this whole issue resolved and closed.
My best to all,
John (JohnNY) Cataneo
New York
A.O. Smith sent a technician from their Field Service Engineering team and it was like someone had opened a window. Having a knowledgeable technician there who was proficient and savvy in the language and design of where the Cyclone came from and how it functions today, was a breath of fresh air and all I really ever needed to put this thing into a state of reliable function for the application.
I’ll refrain from direct quotes because I wouldn’t want to wrongly convey the sequence of operation of this unit on this forum. There are a lot of non-industry people here that might misinterpret and then pass on inaccurate information.
In a nutshell, the Cyclone is a gas flame-modulating unit, a function that ultimately saves fuel and is a proven method of accurately meeting and maintaining a target temperature efficiently.
In this case, however, modulation takes several things into account such as two temperatures within the tank, time that it takes for those temperatures to change, and an algorithm to provide a run time at a specific flame intensity to meet the current demand.
The issue is that in this, or maybe any restaurant, that demand changes sometimes drastically and at unpredictable points in the recovery process.
When the tank temp drops quickly due to a large and sudden intermittent draw the integral logic is sometimes “caught looking” when it should be swinging for the fence.
In this particular case, modulating flame is not the best technology and that process is the only difference between the new water heater and the one that it replaced.
In A.O. Smith’s defense, the fact is that if my water heater were significantly larger, this almost certainly would be less of an issue or perhaps not an issue at all.
As a professional, I specify and install conservatively based on factors like proven math for the application, performance history, possible future changes in demand, and cost, without giving in to the common compulsion to grossly oversize.
I am set to receive two new replacement parts that will allow me to eliminate modulation and have the unit run in high-fire at any call for hot water. The potential disservice is that the water temperature in the tank will almost certainly overshoot at times by a few degrees. Our previously installed mixing valve will greatly minimize any scalding risk at the points of use, so I’m not concerned.
Clearly I’ve been very vocal about this whole episode and I’d like to take this opportunity to thank all of you in this wonderful and unique community of industry professionals and lay persons alike, Dan Holohan, my wholesalers at West Side Supply (Bill, Jeff, Jerry) and of, course, A. O. Smith (Thank you, Scott. Your professionalism is rarely seen these days) for all your support and for lending an ear.
When I get my new parts today or tomorrow, I’ll consider this whole issue resolved and closed.
My best to all,
John (JohnNY) Cataneo
New York
JohnNY
7
Re: Help! Ubearable noise from Taco Hydronic Circulation Pump
Thank for posting the video with sound’ it really helps diagnose the problem. Although not conclusive, I’ve listened to it several times to determine the origin of the noise, and it appears the impeller is hitting. The 100 series pump does need periodic servicing, and the lubrication schedule is dictated by run time. If the pump runs 24/7, as opposed to periodically, obviously the greasing intervals would be more frequent. Perhaps the sleeve bearing ran dry, and compromised the assembly. I was able to ascertain the motor model as a 120-105, which is a 1/6 HP motor used on a 120 pump equipped with permanently lubricated bearings, so the motor does not need servicing. However, the bearing assembly does have an oil port to lubricate the sleeve bearing. Not sure when the last time it was lubricated?? We do lubricate the bearing assembly when assembling the motor, and include on the maintenance instructions for servicing.
I would suggest replacing the bearing assembly so you can get some sleep. Sleep deprivation can lead to all kinds of issues unfortunately; mechanical products are dependent on resources to keep them mechanically fit. If interested, Taco offers a comparable maintenance free 0012 pump with the same performance characteristics as the 120 pump.
I am prepared to support the landlord, plumber, and you the suffering sleep deprived tenant and provide a replacement bearing assembly to mitigate the situation. Perhaps you, the landlord or plumber can contact me and let me know if you would like to take advantage of Johnny White’s generosity and have me send out a replacement bearing assembly.
I would suggest replacing the bearing assembly so you can get some sleep. Sleep deprivation can lead to all kinds of issues unfortunately; mechanical products are dependent on resources to keep them mechanically fit. If interested, Taco offers a comparable maintenance free 0012 pump with the same performance characteristics as the 120 pump.
I am prepared to support the landlord, plumber, and you the suffering sleep deprived tenant and provide a replacement bearing assembly to mitigate the situation. Perhaps you, the landlord or plumber can contact me and let me know if you would like to take advantage of Johnny White’s generosity and have me send out a replacement bearing assembly.
Re: A.O. Smith water heater. Big problems. No help. (JohnNY) **Updated 3/27/15, 11:30am**
We've run into this too. No longer can we count on supply houses to have what we need in stock.
This is why our shop resembles a mini-supply house. One example- we just started work on a building that had a bunch of Webster 02H traps (very common in this area) which had not been touched since they were installed in 1939 (yes, we found the date codes in them). No problem- we had parts in stock, and could fix them right away. AFAIK, no one else in Baltimore could make that statement.
A previous contractor had replaced some 02H traps with Hoffman 17C units, which made those radiators extremely slow. Talk about causing more problems than you solve. The 02H traps were gone, so we installed Barnes & Jones 122 traps which, again, we had in stock.
Somewhere along the line, the Hahvahd MBAs took over many suppliers, and they forgot how this business works. Customers don't want to hear that it'll take 2-3 weeks to get a part when their heating system isn't working (are you listening, mod-con vendors?). This was one of the problems with the company I worked for prior to starting All Steamed Up, Inc.- they didn't want to stock anything, choosing to depend on supply houses. We lost a lot of work as a result.
This is why our shop resembles a mini-supply house. One example- we just started work on a building that had a bunch of Webster 02H traps (very common in this area) which had not been touched since they were installed in 1939 (yes, we found the date codes in them). No problem- we had parts in stock, and could fix them right away. AFAIK, no one else in Baltimore could make that statement.
A previous contractor had replaced some 02H traps with Hoffman 17C units, which made those radiators extremely slow. Talk about causing more problems than you solve. The 02H traps were gone, so we installed Barnes & Jones 122 traps which, again, we had in stock.
Somewhere along the line, the Hahvahd MBAs took over many suppliers, and they forgot how this business works. Customers don't want to hear that it'll take 2-3 weeks to get a part when their heating system isn't working (are you listening, mod-con vendors?). This was one of the problems with the company I worked for prior to starting All Steamed Up, Inc.- they didn't want to stock anything, choosing to depend on supply houses. We lost a lot of work as a result.
Re: How to choose a good hydronic heating/cooling contractor...
I'll give the 'ignorant' homeowner's point of view of what I wished I would have known.
#1 - Any contractor who makes a recommendation without knowing the intricacies of the house - air infiltration, age, plaster or sheet rock - can't do an adequate heat loss.
If you have bad windows like I do (old single pane), and they don't even mention that, something is seriously wrong. Or even to not check the age of the windows if you have double pane is not wise. The best contractor will also check if you did an energy audit to assess the infiltration.
#2 Ask to see the heatloss estimates. I used this layman's calculator after the fact to do my own 'dumb' estimate. http://usa.hudsonreed.com/btu-calculator It's not manual J. But it gives some ballpark. Make sure he/she does a thorough heat loss. Most make a wild educated guess.
#3 Don't be shy to see their work. A happy client will be delighted to send pictures or do a reference call.
#4 Do they know all the heating emitter options and when to use what? I had many plumbers (even third generation licensed plumbers) who never heard of panel rads. Recessed sunrads are very popular in my area (long island), but recessing them while looks better does require additional BTU to be added to the heat loss. Also I was surprised to find to find out that panel rads were equivalent in price to sunrads and much nicer looking. The ones who did know of them were quick to say it's too expensive probably because of lack of experience.
#5 Do you really need a combi boiler? When I got quotes, 4 out of 6 people recommended a combi. None explained the hot water limitations. I would never do a combi boiler in a house over 1500 sq feet. They don't save that much space and need more servicing which isn't cheap. They are all the rage where I live. I had two people who went the traditional route and I unfortunately thought that since they were in the minority, so their plan was subpar. Majority doesn't always rule.
#6 - Be careful about radiant floor staple up under wood floor. It sounds good but what a mess if not done well. Also the creaking pex is irritating.
#7 More zones isn't necessarily better. I have 8 zones for a 2000 sq ft house. I needed 2, max 3. The added zones add no real value. My house isn't so big that I need run it cooler in one part vs another. I thought I'd run downstairs lower at night. It doesn't pay and then it takes all the more longer to heat it back up.
#8 Don't ever ever ever let a contractor diss a steam system especially in an old house. If they do this, run! Back to #1 - every house is different! There is no one size fits all rule.
#9. While price shouldn't be the decider, I found that high price doesn't always equate with getting the best result.
#10 Be an educated consumer on any major changes to a house. Don't put your trust completely in a contractor. They won't live in the house. They won't be paying the bill for the heating system. Don't feel that someone with a business knows more that you can learn. I'm not much more educated in hydronics than long time plumbers. Also every single person you talk to will have a different opinion. I think i've talked to 20 'experts' on my situation, each one was different. That's why education is important for the homeowner.
#1 - Any contractor who makes a recommendation without knowing the intricacies of the house - air infiltration, age, plaster or sheet rock - can't do an adequate heat loss.
If you have bad windows like I do (old single pane), and they don't even mention that, something is seriously wrong. Or even to not check the age of the windows if you have double pane is not wise. The best contractor will also check if you did an energy audit to assess the infiltration.
#2 Ask to see the heatloss estimates. I used this layman's calculator after the fact to do my own 'dumb' estimate. http://usa.hudsonreed.com/btu-calculator It's not manual J. But it gives some ballpark. Make sure he/she does a thorough heat loss. Most make a wild educated guess.
#3 Don't be shy to see their work. A happy client will be delighted to send pictures or do a reference call.
#4 Do they know all the heating emitter options and when to use what? I had many plumbers (even third generation licensed plumbers) who never heard of panel rads. Recessed sunrads are very popular in my area (long island), but recessing them while looks better does require additional BTU to be added to the heat loss. Also I was surprised to find to find out that panel rads were equivalent in price to sunrads and much nicer looking. The ones who did know of them were quick to say it's too expensive probably because of lack of experience.
#5 Do you really need a combi boiler? When I got quotes, 4 out of 6 people recommended a combi. None explained the hot water limitations. I would never do a combi boiler in a house over 1500 sq feet. They don't save that much space and need more servicing which isn't cheap. They are all the rage where I live. I had two people who went the traditional route and I unfortunately thought that since they were in the minority, so their plan was subpar. Majority doesn't always rule.
#6 - Be careful about radiant floor staple up under wood floor. It sounds good but what a mess if not done well. Also the creaking pex is irritating.
#7 More zones isn't necessarily better. I have 8 zones for a 2000 sq ft house. I needed 2, max 3. The added zones add no real value. My house isn't so big that I need run it cooler in one part vs another. I thought I'd run downstairs lower at night. It doesn't pay and then it takes all the more longer to heat it back up.
#8 Don't ever ever ever let a contractor diss a steam system especially in an old house. If they do this, run! Back to #1 - every house is different! There is no one size fits all rule.
#9. While price shouldn't be the decider, I found that high price doesn't always equate with getting the best result.
#10 Be an educated consumer on any major changes to a house. Don't put your trust completely in a contractor. They won't live in the house. They won't be paying the bill for the heating system. Don't feel that someone with a business knows more that you can learn. I'm not much more educated in hydronics than long time plumbers. Also every single person you talk to will have a different opinion. I think i've talked to 20 'experts' on my situation, each one was different. That's why education is important for the homeowner.
9
Re: A.O. Smith water heater. Big problems. No help. (JohnNY) **Updated 3/27/15, 11:30am**
@jonny88 @JohnNY dont be so fast to praise anyone, especially Lochinvar. I was in the same predicament a few months back when I walked in to repair a few large btu Knight boilers in a commercial setting. After talking with the reps and rep repair guys I got no where. I was going to come on here and make a similar thread to this however decided to sit it out and repair the units. Three months after I started I completed the task. Lochinvar said the system was not piped to spec after they couldnt find the issue. Utter bs. The boilers were piped as per manufacturers literature (I wasnt the unstaller). I solved the problem. The client smiled and still smiles ear to ear.
So before you listen promises and promises, just know every company does this to someone at some point, you just didnt hear about it.
I work on 'em all. Lochinvar, Viessmann, TT, NTI, Noritz, Rinnai, WM.... each company has its pros and cons.
Guys, this is a new complicated world.
So before you listen promises and promises, just know every company does this to someone at some point, you just didnt hear about it.
I work on 'em all. Lochinvar, Viessmann, TT, NTI, Noritz, Rinnai, WM.... each company has its pros and cons.
Guys, this is a new complicated world.
Re: A.O. Smith water heater. Big problems. No help. (JohnNY) **Updated 3/27/15, 11:30am**
And I repeat:
I will no longer use ao smith products because of the treatment you have received.
Please don't tell me not to jump to conclusions, not to bash a manufacturer and not to boycott. Because when you tell me that, you are telling me to lie down and take a beating without the benefit of self defense.
WE are out there, EVERY day, facing good customers. I should sell these people, who trust my judgment, a product that will not be backed up by the manufacturer if something goes wrong?
Sorry. Um, no. Not even sometimes.
My customers are the people who make a difference in MY life.
Al Corelli
ACA Inc.
"We Warm You in Ways You'd Never Imagine"
Serving Westchester County, NY and Lower Connecticut
I will no longer use ao smith products because of the treatment you have received.
Please don't tell me not to jump to conclusions, not to bash a manufacturer and not to boycott. Because when you tell me that, you are telling me to lie down and take a beating without the benefit of self defense.
WE are out there, EVERY day, facing good customers. I should sell these people, who trust my judgment, a product that will not be backed up by the manufacturer if something goes wrong?
Sorry. Um, no. Not even sometimes.
My customers are the people who make a difference in MY life.
Al Corelli
ACA Inc.
"We Warm You in Ways You'd Never Imagine"
Serving Westchester County, NY and Lower Connecticut
Re: Not good for plumbing in NYC
In one of the trade magazines there recently was a story of a problem sewer line with blockage. The camera man found a baseball bat lying in the horizontal run to the city sewer. With the camera and hooks it was removed. It was thought to have been purposely placed in there on the rough-in.
One time I pulled out a toothbrush with a closet auger, the 3 adults that lived there at the time were not home for this. I told them I just rinsed it off and put it back in the toothbrush holder. I'm really sure they all brought new toothbrushes that day.
One time I pulled out a toothbrush with a closet auger, the 3 adults that lived there at the time were not home for this. I told them I just rinsed it off and put it back in the toothbrush holder. I'm really sure they all brought new toothbrushes that day.
5

