Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
If our community has helped you, please consider making a contribution to support this website. Thanks!
Best Of
Re: Live steam from the condensate return
Traps, Traps, and more traps. You need to impress on the school system how much fuel your wasting. Not only dumping BTUs to the atmosphere your also
adding a ton of fresh make-up water (and oxygen) to the system that you have to bring from 40 deg. up to steam temperature at least 212 deg. The oxygen will start to rot out the piping --boiler feed piping is the first to go followed by the boiler and the condensate piping. If this keeps going you can loose a boiler, if your lucky only the feed water piping between the boiler feed tank and the boiler will be shot.
adding a ton of fresh make-up water (and oxygen) to the system that you have to bring from 40 deg. up to steam temperature at least 212 deg. The oxygen will start to rot out the piping --boiler feed piping is the first to go followed by the boiler and the condensate piping. If this keeps going you can loose a boiler, if your lucky only the feed water piping between the boiler feed tank and the boiler will be shot.
Re: Gorton Vents #1 or #2
As far as venting a rule of thumb on this board is 1 Gorton #2 vent for every 20' of 2" main. So if your mains are 2" that would be at least 2 per main. If you wanted to use #1 multiply that by 3. As long as the pressure is kept low spitting shouldn't be an issue. This was stated by KC_ Jones . My mains are length 46' and 47' . Is this meaning I should have two on the end of each of my mains ?Yes, they should both be at the end of the Mains. You can build an antler or use Tee's to put them on the same opening in the main as long as that opening is 1/2" minimum (for 2 Gorton #2's)
5
How to choose a good hydronic heating/cooling contractor...
There has been some discussion lately about how a homeowner knows whether the person and or company they are dealing with is qualified and skilled to do a proper job of "Place task here", including boiler replacements, hydronic additions, radiant additions etc.
Inasmuch as 95% of the world comes here seeking answers, I think it would be a great idea to come up with a list of questions that the homeowners could and should ask of their bidding contractors so that they at least have a chance of getting the system of their dreams that works without issues and doesn't cost an arm and a leg in energy.
My hope is that Dan will add these recommendations into a category that homeowners coming here seeking advice can use in moving forward, and ask their potential contractors the right questions, and get the right answers to aid in the proper installation of a system. I will kick it off with something I found on the web the other day, that is a good start, and let other willing contractors contribute to the list. Our way of paying it forward if you will. I will eventually take the recommendations, and incorporate them into a document that the RPA will offer to homeowners to assist them in making their decisions about what contractor to use for their hydronic projects.
http://www.deltafaucet.com/inspiredliving/infographic/12-things-ask-contractor-saying-youre-hired
Inasmuch as 95% of the world comes here seeking answers, I think it would be a great idea to come up with a list of questions that the homeowners could and should ask of their bidding contractors so that they at least have a chance of getting the system of their dreams that works without issues and doesn't cost an arm and a leg in energy.
My hope is that Dan will add these recommendations into a category that homeowners coming here seeking advice can use in moving forward, and ask their potential contractors the right questions, and get the right answers to aid in the proper installation of a system. I will kick it off with something I found on the web the other day, that is a good start, and let other willing contractors contribute to the list. Our way of paying it forward if you will. I will eventually take the recommendations, and incorporate them into a document that the RPA will offer to homeowners to assist them in making their decisions about what contractor to use for their hydronic projects.
http://www.deltafaucet.com/inspiredliving/infographic/12-things-ask-contractor-saying-youre-hired
Re: Gravity? Not?
Pumping didn't come along in homes until the thirtys, so it's a converted gravity system. Had it been available, you wouldn't have needed 3" mains.
Ironman
5
Re: New Steam Boiler Install - Black Liquid in Gauge Glass
One other observation; those droplets of water in the sight glass, above the water line are a give-a-way that a skim is in order.
5
Re: New Steam Boiler Install - Black Liquid in Gauge Glass
Also, concerning the venting. The damper will probably need a spill switch. This is code in my area, but wasn't included with my boiler. The manufacturer should be able to tell you which you need if you need one. Call their tech line. This shutz down the boiler in case the flue gets blocked so you don't die of co poisoning.
vaporvac
5
Re: New Steam Boiler Install - Black Liquid in Gauge Glass
Yes, The Hartford loop is there and looks good too. Do investigate how the boiler and water heater flue are tied together and, if necessary, have them seperate them and vent them seperately into the chimney. other than that it looks pretty good.
5
Re: New Steam Boiler Install - Black Liquid in Gauge Glass
Yep the bypass is very clear in that picture! Yes I think you have it. If you are curious about skimming you can search this site and find plenty of information about the process. Remember it's time consuming (think in hours). If you feel comfortable it is a very DIY friendly task. I look at it this way do you want to pay them their hourly rate to stand there and watch water flow? Also it is very likely on a new install that it will need to be done more than once. This is because it can take time for all the oils from new piping to work it's way back to the boiler.
5
Re: New Steam Boiler Install - Black Liquid in Gauge Glass
The vent damper comes with the boiler they should have installed it. You will lose some efficiency without it. The piping looks a lot better then most of what we see around here. As near as I can tell it's at least to minimum manufacturers specs. That wiring wouldn't pass in my area romex run without support like that is a no no I have always seen it run with conduit or armored cable. Not sure what the codes are in your area on that. Looks like you have an auto feeder, is there a manual bypass for it? There should be a way to manually feed the boiler without using the auto feeder and be able to valve off the feeder. I can't really tell in those pics for sure, but it looks like the only water line goes through the feeder? Without the bypass skimming will be impossible.