Best Of
Re: Difficulty in Properly Sizing Equipment - 2140 Sq Ft New Construction Spray Foam House
For new construction, done to current code, in your climate, 2140 square feet, 39K heating and 29K cooling actually sounds kind of high.
Re: Difficulty in Properly Sizing Equipment - 2140 Sq Ft New Construction Spray Foam House
minis have low static ducted units that are 1-Ton or less.
Please
2 stories
2 systems.

Re: Sanity check plan new zone
sounds like you need to shop for a better brand of zone valves.😉
There is not a lot of difference between a zone valve and a zone actuator on a manifold. Often they are the exact same operator as one another
Zone valves with a short life span are often short cycling themselves to death
On the average a ZV cycles 5000 times a heating season. Quality valves, gear trains, motors and switches are designed for 100,000 cycles. Or 20 years of service.

Re: Difficulty in Properly Sizing Equipment - 2140 Sq Ft New Construction Spray Foam House
That is a problem with Oil Heat equipment. The smallest input Equipment is often too big for the building. That said, the EK has the best control to reduce the short cycling associated with oversized equipment. So explain your concerns to the nice folks at EK and they will help you to design a great 2 zone system.
And the thing about 1.5 ton cooling as the smallest available… There are some Variable speed inverter outdoor units that are usually associated with MiniSplit systems that can be connected to 1.5 ton ducted air handlers. some of the match ups are as small as 12,000 BTU or 1 ton. Ask your HVAC contractor to look into this option from their local supplier. I know that Fujitsu had one available several years ago before I retired. I'm sure the other brands have also joined in.
Re: Swapping out an older wall mounted utility faucet
There are also styles of faucets with a swivel and offset butlt in to the unions that lets you connect it to supply pipes with different centers. Is there a reason you're replacing it instead of just re-gasketing it?

Re: Lochinvar Knight Boiler Flame Fail Ignition Errors - ready to pull my hair out
Natural gas runs at a lower pressure than LP does so the regulators are different and you've got a NG regulator. I've had success swapping springs to get more pressure out of them, they're like $5-8 online. That appears to be a Maxitrol 325-3 reg. Your pressure drop looks good so once you get that spring taken care of, you should be in business. As for the hi limit, you're going to want to make sure there is a load on the unit. Depending how it's wired, you may need to run a circulator with a jumper or cord just to get it to move heat while in service mode.

Re: Good or bad? Tubing
@GW be careful as others have written above. Last job I was on that had very similar looking tubing was a nightmare. I was there for a small leak and found all of the steel near boiler piping on a Weil McLain CG to be clogged and or brittle. Cast iron circulators were also clogged as were the three cast iron flow checks. Three of the ten or so loops to the hot water baseboards were no longer functioning. Homeowner, was in real estate and just wanted it to work as he was planning on selling house soon. I did the emergency repair and sent an estimate for a new boiler and complete re-pipe. Never heard back, feel sorry for the new homeowner. I cannot imagine owning a million dollar (maybe two million now) home and not being able to use three rooms.
@ethicalpaul I think I understand your premise about residential one pipe steam systems not clogging, despite being "open" to the air. However, keep in mind that in most one pipe steam systems, the smallest pipe is typically 1.25 inches. Without a doubt the most clogs we see in this type of steam system is where the 1/2 or 3/4 inch drain valves are located (could be on returns, boiler, etc.). The second most common spot for clogs we see find are on the the lowest horizontal pipe, typically a 1.25" wet return pipe near the floor. My point here is that smaller pipes tend to clog faster than larger ones (on steam and hot water heating systems). Don't forget a small percentage of steam systems are actually filled with water all of the time, as compared to hot water heating systems.
Re: Viessmann cast iron boiler replacement.
First of all, fantastic photo taking advantage of the natural light. Amazing how much a great photo shows all of the details. I especially liked the item that appears to be a flywheel on the back of the workbench. Timer near the boiler is intriguing as well.
Re: Central Boiler Classic Edge 350 piping sizing
For that long a run — 250 feet at least out and back — I'd go with at least inch and quarter. Maybe even inch and a half. It's head loss you're looking at, and keeping the pump size reasonable.
And insulate it.
And no, dropping to smaller sizes inside the house isn't going to be a problem.