Re: Difficulty in Properly Sizing Equipment - 2140 Sq Ft New Construction Spray Foam House
What are your local utility costs? Around me oil is about 3x the operating cost of a heat pump so it makes no sense for a new build.
You area already adding ducting for AC, so your additional cost is only the up charge to a heat pump which will be a fraction of the cost of oil tank, boiler, plumbing and rads.
18/BTU per sqft in zone 4 sound very high for a tight new construction. I would doublecheck the manual J assumption as something is off. It should be closer to 8-12btu/sqft.
Even assuming 39k is correct you could heat the house with a combination of:
https://ashp.neep.org/#!/product/64682/7/25000/95/7500/0///0
and
https://ashp.neep.org/#!/product/64684/7/25000/95/7500/0///0
These are modulating units, if you look at the turndown on cooling it is pretty decent so even though it is oversized for cooling load, it should still turn down enough.
My guess once you get your manual J dialed in, a single 2 or 2.5 ton cold climate heat pump can heat and cool your place without issues.
Bonus of a heat pump is the SEER rating on it is much higher than your typical AC, so your cooling costs will also be significantly less.

Re: correct gpm for open loop geothermal
Standard condenser water flow when you recycle the water is 3 gpm /ton nominal. Older ac systems that used city water and dumped it were based on 1.5 gpm/ton because the city water was colder.
So heat pump or not it doesn't change much your between the 1.5 and 3 gpm/ton. Don't forget 1 ton of cooling is 12,000 btus but you have the added heat of rejection from the compressor which is usually figured at 1.3 x 12000 btu or =15,600 btu/ton which used to be referred to as "tower tons" as a cooling tower was used.
Well water may be as cold as city water or it may not be. I seriously doubt the 1 gpm/ton the well guy said is correct
The manufacturer would be the best place to go to get specific information based on water temp and gpm flow. There will be some leeway on this
Re: correct gpm for open loop geothermal
As @DCContrarian and @ethicalpaul have stated, the gpm from the well for geothermal is related to the heat added or rejected. Exactly the same equation as standard hydronics. Any refrigeration problems with the condenser or pressures or all that magic will have nothing to do with it.
It would, though, be worth checking what your water intake and discharge temperatures are. You really don't want to freeze that drain field or the piping to it…. and, oddly, you don't want to cook it either. Discharge water temperatures much over 80 F will sterilize the soil in and over the drain field, which is not good.
Re: correct gpm for open loop geothermal
2.2 gpm per ton is a temperature change of 11F.
1 gpm per ton is a temperature change of 24F.
For heating, in many places that 24F drop would freeze up. Even at 2.2 gpm your source water can't be below 43F or you risk freezing.
Re: How to prevent hydronic piping from freezing?
There is a timer called ThermGuard that connects across your thermostat and will turn on your boiler for a programable set amont of time and a programable number of times per hour. It has a defult setting of turning on the boiler for 5 minutes every half hour. I purchased one for an area in the home that I didnt plan to heat but never installed it so I cant say anything about its reliability.

Re: How to prevent hydronic piping from freezing?
A word of caution, if there is any interface between your domestic hot water and the circulating heat system, then you must use only propylene glycol, never ethylene.

Re: correct gpm for open loop geothermal
Is this system a water furnace? How deep is the well, how far away is the dump point?
Check the gas pressure first before you do anything.
The well water is going to be cold 52 degrees or less so please keep that in mind when looking at the whole picture.
I guess you could flush the exchanger with strong vinegar and see how much build up is in it, you may very well have no restriction of flow.

Re: Plate heat exchanger
On the glycol side you want an air purger, pressure gauge, relief valve and expansion tank also
Maybe an Axiom fill tank

Re: Plate heat exchanger
I presume a brazed one? Gasketed likes constant temperatures.
Also you can think about filters for both sides. Not easy to clean brazed plate exchanger.
I'd just get an electric heater for that bathroom.