Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
If our community has helped you, please consider making a contribution to support this website. Thanks!
Best Of
Re: Should I reuse union fittings on steam radiator?
@Intplm.I cut the nut off and then used a 24" wrench on it. Seemed to come off with ease with that method.
I have had pretty good luck removing them. You have to cut the nut off to get enough room for a small pipe wrench with a cheater pipe on it. If you plug the hole so it can't collapse it will usually come out. Of course, when they are all painted up the pipe wrench wants to slip.
ChrisJ
1
Re: Occupation
Now? Or before I retired 17 years ago? Before I retired, professional (Civil) engineer. A few other things before that. Now? Lay brother of the Order of Saint Benedict.
Another Moline System
Just replaced the boiler on this Moline system.
The cellar was a mess covered in plastic.
The old:


The cellar was a mess covered in plastic.
The old:


The new header:




The new boiler:






The old air trap and vacuum valve were bad. We also replaced about 50’ of wet return.




Ironman
10
Re: Is the LAARS FT MFTCW140NA2XN any good? Any way to determine manufacture date?
Unless you have an extremely large house, that’s probably way more boiler than you need. It looks like it’s a combi which is the reason for the 140k input.
Count up the linear feet of heating elements in your baseboards and multiply that by 500 to see the total output. Then you can see how close the boiler matches your load.
You could install a buffer tank to compensate for any over-sizing, but that’s another component and more $$.
Count up the linear feet of heating elements in your baseboards and multiply that by 500 to see the total output. Then you can see how close the boiler matches your load.
You could install a buffer tank to compensate for any over-sizing, but that’s another component and more $$.
Ironman
1
Re: Added Vents, Lost Heat?
B4 you use the 2x 4 start at the boiler end and figure out which way the pipes need to pitch and use a level.but that return at the end of the main can't pitch right because of the way it is piped
Your technician who installed the vents and the new near boiler piping should have gone through the system and figured this all out
1
Re: Is the LAARS FT MFTCW140NA2XN any good? Any way to determine manufacture date?
They're okay. Not great, but not terrible either. I know we're not supposed to discuss pricing but this is public knowledge so I'll say that you can pick that boiler up new for under $2k. Unless it's $1000 or less, I'd pass knowing it was most likely abused pretty badly in its short life based on the fact that it was removed from service. For $1k it may be worth the gamble with a 10 year life expectancy.
2
Re: What is this vent?

at least from 1929 and mentioned in catalogs up to 1953.. that I was able to google
no specific information found though
There are photos and descriptions in this catalog, but can only preview tidbits.
https://www.google.com/books/edition/Domestic_Engineering_Plumbing_heating_Ca/WMYkrxAdvOYC?hl=en
Says new york public library digitized, but I couldn't find it on their website.
Guess you have to request it https://legacycatalog.nypl.org/record=b11974017~S1
1
Re: LAARS MASCOT FT 140 k model
Ken Resnick is the Babe Ruth of Laars service, I am naming my next child after him!!!
2

