Re: Mixing valves in oil fired radiant floor heating system
The supply water temperature to the floor will not change with the weather for the most part.
Lets say the fixed temperature mix for the floor needs to be 125° for the design days. (the coldest days) and the boiler will create 160° for that using the ODR when there is no call for DHW and the minimum temperature for the boiler return of 135°. The fixed temp mixing valve will take 160° supply water and add the proper amount of return water from the radiant in order to make 125° to the floor
When the boiler temperature drops lower temperatures based on the boiler or Tekmar ODR control sensing a warmer outside temperature (say 145°), the fixed temp mix valve will take the 145° reset temperature and mix less return water from the radiant return to make the supply 125° to the floor. So when the floor needs the lower temp on the warmer day, it will still be getting 125 °. That will over heat the room enough to satisfy (turn off) the thermostat until the room temperature drops below the thermostat set point and it calls for heat again. Room temperature thermostats and radiant floor heat are not the best combination to avoid large temperature swings in the rooms because of the slower reaction time of radiant floor systems.
Eventually the Tekmer or boiler ODR control will drop the supply temperature to 120° when the outside temperature is above 50°. That is when the 125 mix valve will not allow any return water from the radiant loop to mix with the 120° supply water. the 120° supply water will go straight through the mix valve. You will then get the lower floor temperature. Now this 120° boiler supply temperature will only happen when the boiler's burner is off. If the boiler's burner is firing then the minimum return temperature of 135° will need to happen by some function of the control system to protect the boiler from flue gas condensation.
I'm not saying that it won't work, I'm just pointing out the reason you might want to consider the Taco iSeries ODR valve. They were not available when I installed my radiant floor system so I installed fixed temp mix valves and used room thermostats. It worked fine for me. I just wanted you to know that without the ODR valve, you may be wasting your $$$ on using a Tekmer or other boiler ODR system.
What you think you are achieving with a Tekmar or other boiler temperature ODR may not happen after you spend all that $$$ on the control system. Save on the system ODR and use the ODR mix valve where it will do the most good. Or forget about ODR completely and save $$$ in installation costs.
Re: tiny droplet leak from the oil tank firomatic shut off valve.
A few drips of oil are not dangerous. Its something that should be fixed and not be ignored but I wouldn't panic about it. I would run the tank low and have it fixed. If the tank is old it may be time to change it.
Re: HTP Boiler humidity dislike + Error Code 11
Yeah I still don't see how we went from clogged condensate and an ignition error to descaling the pipes. Sounds like a fire side problem. All of the advice prior to calling a plumber was to service the fire side, you should never aim to descale the closed system boiler piping unless there is a massive problem with that water. The condensate that is coming out of the boiler is NOT from the closed system (unless there is a hole in the heat exchanger) again what you have is a fire side problem, you need burner service, and to clean the FIRE SIDE, not to descale the inside of the boiler piping, that will not fix your problem and very likely will cause new ones.
Re: I said "what???"
It is called joist bay heating. Uponor still has a method in their design guide using bare Pex tube in the joist bay. Suspend the tube an inch below the floor.
UltraFin is an aluminum convectors that snaps on Pex tube to increase convection. Either these or the fin tube can work fine
the fin tube is probable even better than these two options for getting the energy from the tube to the joist bay. Generally 140f and higher SWT required
hot_rod
Re: Prevent mold in mini-split heads
I've never heard anywhere except here that an inverter mini split NEEDS to run at 100% capacity. Everything I have ever learned about them says they are more efficient at lower loads, and they tend to run better if they coast along at low loads, rather than full load (this is manufacturer training, and engineers telling me this). Obviously if your low turndown capacity is larger than the internal load you will end up short cycling which isn't good. But can you explain why an inverter mini split needs to run at full load?
Re: Mini Split Location
The several cassettes I know of use a slinger-style pump that'll give you up to IIRC 26" of lift, then they're supposed to gravity drain from there. They'll easily lift to a Little Giant sitting on top of the cassette. More than that, not so much.
Re: Prevent mold in mini-split heads
I have installed a few of the wall mounted units in my day, Never needed a pump unless the unit was in a basement without a proper place to drain the condensate. Then I would add a condensate pump like the one you might use for an air handler in the basement with the same problem.
The drain pan (violet) is gravity drained in most cases.
Re: Prevent mold in mini-split heads
I've never seen a minisplit that collects water? The ceiling cassettes do but as far as I know they're uncommon.
All of the ones I've installed had a hose that runs directly outside and drains freely by gravity.
ChrisJ
Re: Warm Start Boiler Summer Leak
is it leaking or is that condensation? doe it actually fire? if it fires only to 90 it is going to condense.