Best Of
Re: Any steam heat contractors near Bloomington IN?
@MattinIndy , you should consider getting a Find a Contractor ad on this site. We get quite a few inquiries from your area, which could go to you.
Re: A/C Capacitor Voltage
A lot say that now. I think the Titan HD ones do as well. They're just 440v caps.
ChrisJ
Re: A/C Capacitor Voltage
This is exactly correct. You can go up in voltage rating as long as you match the uF rating. Also some capacitors are designed as 'start' capacitors and others as 'run' capacitors. 'Start' capacitors are designed for a few seconds of operation at a time, and will overheat if used continuously as a run capacitor. Run capacitors are designed for continuous use, and can be used as start capacitors, but will probably be un-necessarily physically larger and more expensive).
As a rule of thumb, if this is a 120V motor you will need a 370V rated capacitor (a lower rating would probably work, but they are not commonly made, so you end up with 370V); if this is a 240V motor you will need a 440V rated capacitor. The voltage applied to the capacitor is significantly higher than the supply voltage going to the motor. (See https://youtu.be/rUqL9MqwimA for someone actually measuring the voltage applied to the capacitors when the motor is running).
In general a higher voltage rating is good because the capacitor will last longer.
The 370/440V rating is just the manufacturer's way of making it clear that you can use a 440V capacitor in place of a 370V capacitor.
Why Is It So Hard To Hire A Contractor?
A Wall Street Journal writer got in touch with me last summer and asked if she could interview me. She was working on an article about why it was so hard to hire a contractor. It was to be in the Small Business section of the Journal. She was mainly concerned with those contractors who don’t return calls, or those who show up, give an estimate, and then just disappear.
Re: One-inch magnetic filter on 1-1/4 boiler return?
Just so you know @seized123 there are some folks that have their boiler installed incorrectly with the pump on the return and the expansion tank on the supply, the auto water feed on the suction side of the pump and all other types of stuff that you haver already corrected. Those system can work for years and years without ever having to replace a circulator pump or move an expansion tank. It seems that you like to read about what is the best practice and do that to your system, even if you don't get any benefit from it. Your constant draining and adding water to make another minor correction every year until you have the best design ever, might actually cause more problems that you are correcting.
When I do a maintenance on a boiler that is poorly designed, I don't recommend to my customer that we make a minor change here and another minor change in the design next year, and continue to redesign everything with every new article I read in the trade journals. Those 80 year old systems worked fine for 80 years. Those 50 year old systems worked fine for years and those 20 year old systems worked fine for years. I might add that until you actually experience a problem with your system, just do the maintenance and leave the system just work as it is. You already did all you need to do last year. Let it work for a couple of years before you start changing stuff around. You may find that nothing fails to operate and there is no need for change.
If I have a problem with constantly draining an expansion tank two times a year, or constant air problem with one loop of baseboard in a home, then I would recommend a major redesign to solve a problem. But if the system is operating satisfactory, then I go with the old saying… "IF IT AIN'T BROKE…" you know the rest.
Re: A/C Capacitor Voltage
Just to recap (sorry). You can safely use a capacitor with a higher VOLTAGE rating than required. No problem. You can NOT use a capacitor with a capacitance much more than 10 percent higher or lower than required.
Re: Your thoughts and opinions please
“The customer was thinking of a quick thing about what to look for on each type system.”
Herein lies the problem: They want you to give them in less than 4 hours what you’ve spent a lifetime learning.
It takes 12 years to get a high school diploma, another 4 to get a bachelor’s degree;, 3 more to get a master’s, and 1-2 more to earn a doctorate. But somehow, they expect you to be able to condense what you’ve learned through decades into 3-1/2 hours. It’s just part of the instant gratification culture in which we live.
I would suggest that you reduce it down to maybe one two sub points from each main topic that you feel are most needed and spend a little time emphasizing that it takes a lot more time and effort to get a working understanding of hydronics and then promote you books and videos along with this site. Those that really want to learn will take your advice.
Ironman
Re: A/C Capacitor Voltage
The life of an electrolytic cap is a function of voltage and temp. It will work a bit above its rated voltage for quite a while but won't get its rated life. You can get more life by using a cap with a significantly higher voltage rating than the working voltage.
Re: A/C Capacitor Voltage
When it comes to Capacitors for HVAC repair I stopped stocking 20 different dual and 15 different single caps in favor of the Turbo 200. Three of those per truck and one of the larger Turbo caps greatly reduced truck inventory costs and space. I can also offer a 3 year warranty on them because Turbo offers a 5 year warranty. I just need to cover the labor portion. That Turbos are all rated at 440 and you can build the exact uf you need. I know that they are more expensive that the ones made of chinesuim but the warranty suggests that they will last longer. A better deal for the customer that is paying retail for repairs.