Re: Need direction - Bosch Singular 5200
"Hybrid" would be a kind word. Is there any way you can rearrange the piping so that each section is fed individually from a manifold of some kind — doesn't have to be right at the boiler — and each returns individually to another manifold, and then the whole lot returns to the boiler together?
Re: DIY Boiler Installation -- Peerless 63-03
Any pictures of the final product from a few feet back?
Re: Weil McClain Gold Oil - Water Level Issue
Update: with the yellow valve turned ON and the blue valves OFF, the water level did not rise.
With that in mind, it seems the waterfeeder is the issue. Do you agree?
Re: Correct Venting for faster Radiator heat up??
That's your problem right there. This pipe needs to slope TOWARDS the main. You'll never get steam past that dip.
Re: Replacement radiator on two-pipe vented system in SoHo?
@mattmia2 @Steamhead yes, I think you're right.
Re: Raising Height of AAV
That looks like a baffle tee that it is tied into. Used to connect two bowl sinks. that could be the slow drain issue. Take it apart and see what that tee looks like inside.
A rubber fernco coupling fits nicely also, easy to service.
Re: Vitodens 100w B1HA - 82f Heating Curve Setpoint
Newer style furnaces run similarly, longer runtimes at lower fuel usage, generally the blower speed will be variable as well, this can bother customers used to that blast of hot air coming out the vents.
Basically the lower supply temperature allows your boiler to condense the flue gasses more, that is where a lot of the listed efficiency ratings are coming from, without condensing you might only be running 80-85% instead of 93-95% efficiency. The boiler modulates the burner, so while it might run for more time throughout the day, it won't be using more fuel than a system that runs less amount of time but cycles more, assuming all other things are equal. If one system is condensing, and the other is non-condensing, the condensing system will use less total fuel (less wasted energy going out the flue pipe) but the delivered btu/hr to the space should be the same over a day's worth of run time. With a condensing boiler install, or a modulating furnace, I like to see that system running at a low fire rate for a long time, while maintaining the indoor temp at the thermostat setting. When modulating forced air furnaces were a lot less common we used to get calls from contractors wondering why the furnace never shut off, so you are not alone being confused by this!
If you are running a fairly low heating curve setting your system may not recover quickly from temperature setbacks so do keep that in mind. The required water temp to maintain 70 degrees, is different than the required supply temp to raise the temp of the space several degrees. I do a 2 degree setback when I remember to dial back my thermostats (I don't have programmable stats) and don't have issues recovering from that. Temperature setbacks are one reason many contractors in the US set these condensing units to run at max temp on install, but then you basically have a modulating 80% boiler instead of a 95% one. Don't be shy to raise the heating curve if the system doesn't keep up. your comfort level should come first imo.
Re: Automatic Feed Valve Makeup Demand
What do you mean the contractor insist? You are paying him and you get to decide. Automatic feeders are not a good idea, unless you are away for extended periods of time during the winter or you are physically or otherwise unable to check the boiler on a somewhat regular basis.
Re: Am I being simpleminded for wanting a Weil-McLain just like my old one?
Do yourself a favor and get the new burner that come with the new boiler. Then you won't have any issues.
If homeowner installation is allowed in your state go for it. Just get a decent oil tech to combustion test and adjust.
Re: Near-pipe dope identification help on 222k BTU Utica PEG-E Boiler
Or Whitlam..It dont matter what tbdy used...ITS Coming APART either way....Mad Dog