Re: boiler vibrating
The best way would be to start a free youtube account, upload your video there and share it here. If you don't want the youtube video to be public you can make it unlisted and share the direct URL here. anyone with the URL can see the video but it won't show up on your youtube profile or in a search bar
Re: Calling Peerless 63-series Owners: A Venting Mystery
Hi @dabrakeman I think the reply above got put onto a different thread than intended
Re: Argo AR826 schematic?
This may help ?
Looks like it is in Priority when the picture was taken. I assume the switch is up for priority.
Your actual issue may be elsewhere. That box may only just provide Priority for the DHW (Domestic Hot Water) circulator. When there is 'No Priority' it may simply provide power for the heat zone circulator which may be controlled by another device. That box (the AR826) does not appear to provide 'Thermostatic Control' for the heat zone circulator. It other words it only interrupts the power for the heat zone circulator to favor DHW circulator.
There is multiple pairs of wires connected to the X-X terminals which leads me to believe there is other control equipment.
You can inspect the relays (the contacts) if they are in sockets and if they are the same part number you can rearrange then to see if the symptoms change. Mark their original location.
The "24 VAC Zone Valve" terminals has me confused as to their purpose (and not used in your case).
Is it just a 24 VAC supply for a thermostat / zone valve circuit.
A control input from a zone valve end switch.
Or a means to interrupt a zone valve control circuit to prioritize the water flow for the DHW.
Re: Mystery water leak - excess water take up problem
why wouldn't the new independence also require the chimney be repaired?
Re: Mystery water leak - excess water take up problem
Unfortunately, Burnham Independence doesn't have the best track record. I would fill the boiler with water until you feel the supply header get cold as @Ironman mentioned.
The boiler does not have to be cold to do this, but I would not do it with the boiler red hot. You could have a leak above the water line. Any leak should be self evident.
You could post your location and look for a steam contractor in "find a contractor" on this site"
When totaling up your EDR for a potential replacement just add up the EDR of the radiation. Do not add anything for piping or pick up. Compare the EDR to the boiler nameplate in square feet of steam. The pickup factor is already added in.
Re: Cleaning my Woodshop furnace
I would be more concerned with wood dust in the burners and controls and inducer (fire side) rather than the air side. Remove the burners and blow them out. Clean inducer.
If it has been a while I would probably pull out the blower assembly and then vacuum and blow out with air.
Re: newer wall furnace with one sided heat.
@needinformation
Forget UL approved CO Detectors. They will not alarm until 70PPM is exceeded for up to 4 hours!
Search for Low Level CO Detectors. These will alert as low as 15 PPM.
Do not run that furnace.
pecmsg
Re: The "equalizer" is mis-named. It does nothing to equalize anything.
I will just say @archibald tuttle that I did run several tests with accurate gauges at the boiler and at the far end of the main and I never saw any measurable difference in pressure between them at any point in the heating cycle.
If we think about it, it makes sense. Pressure differential "travels" or equalizes at something like the speed of sound (which is in fact what sound is). There just isn't enough friction in a home system at home pressures to ever see any kind of pressure drop.
Re: Boiler water quality
Others will comment but iMHO if the water level is steady (not bouncing over an inch or so) when steaming and the water is only tea colored then I would leave it for now.
If it was me I would boil it out with TSP or washing soda in the spring. 1lb/every 50 gallons of boiler water.
You might check the PH with some PH strips.