Best Of
Re: Can you please critique this boiler setup that was installed in my house two wks ago
His first post two years ago was asking for opinions on replacing his leaky boiler, it appears this post is about the new boiler just installed.
MaxMercy
Re: After two heating seasons freezing point of radiant heat system has gotten lower
All research indicates once it is mixed it cannot be separates, with the possible exception of freezing the solution.
hot_rod
Re: Oversized overtall chimney?
That oiler have a draught hood on it? Atmospheric — it should. If so, you really have two separate issues: draught through the boiler, which should be controlled by the boiler's dampers, and draught up the chimney
It's the draught up the chimney which needs to be controlled. The stack damper is really the simplest (and cheapest) way to do that, but as you have found it isn't set and forget — or, actually, it is: you set it for adequate draught on warmer days, and on nice cold days off it goes. Bad news: any fixed restriction on the chimney will do exactly the same thing — stack damper, reduced size liner, you name it. That's the way chimneys behave…
Re: Boiler water quality
The 8-way only works in the boiler. The steam that makes its way to your vents is distilled when it condenses. If rusty water is getting to your radiators and/or vents you have other problems.
I use 8-way and I find 1oz per gallon is the max and 0.5-0.75oz/gallon is ideal. My boiler has a 10 gallon water capacity and I add an 8oz cup worth. Keeps the pH around 10-ish.
When I first started using 8-way it was doing some cleaning and making the boiler water dirty. For the first time ever I got water hammer when the boiler shot a bunch of water up the mains. Now my boiler water is crystal clean.
Whether I put too much or too little in, my water line doesn't bounce any different.
**EDIT and I have a 42 year old Peerless G-461, which got renamed as the 61-04 and eventually the Series 64. Very similar to yours except another section in the boiler.
Re: In need of suggestions replacing an Weil McLain EG 65 steam boiler
Re: steam radiators
What happens if you cautiously remove the vents on the misbehaving radiators? With someone to turn off the boiler if steam starts coming out?
If there is no change, and steam still stops before it gets to the radiators, check the radiator inlet valves… they may look open, but may not be.
Re: Lochinvar boiler isn’t keeping up
While the 40 may not be enough I don't believe the controls are set properly. If you set the controls right and keep the tank at 135-140 and mix it down and be a little more selective in your water, use you might get by.
Re: Can you please critique this boiler setup that was installed in my house two wks ago
It stinks (since you asked).
Re: Can you please critique this boiler setup that was installed in my house two wks ago
From the Peerless manual. Note the takeoff from the header needs to be after the two riser connections to the header: