Best Of
Re: Recommendation for highly reliable natural gas water heater?...
Someone has a page on how to put a powered anode on different styles of water heater. If it doesn't have a tapping for the anode you can put it through a tee on the outlet.
Anodes that produce the current through an electrochemical reaction are sacrificial. Powered anodes are not sacrificial, they are not consumed to produce the current that favors deposition of iron, it is produced by an external power supply.
Re: Recommendation for highly reliable natural gas water heater?...
Different doesn't necessarily mean goofy.
Unless it's a mouse with 1 button when everyone else has 3. Then it's goofy. 😉
ChrisJ
Re: New steam boiler - newbie help
While the pick-up factor is always interesting, What I want to know-
Why did the original quote include 2 heat only thermostats for a single steam boiler?
Re: Tamper free switches
How much room is there inside the boiler room? Is there enough room to place a one foot vestibule just inside the boiler room, or just outside the boiler room in order to make the switch pass inspection outside of the boiler room door but still out of public area?
Re: Venting into a chimney
Absolutely not...that is a 95% Condensing boiler (very low flue temperature). You can ONLY use the old chimney as a pipe chase, as the other guys stated. I'm using the exact same Viessman model on a project right now, but using PP (polypropylene) venting directly outside through basement wall. Mad Dog
Re: Venting into a chimney
To be clear on your query, I can not find any specifications on a Viessmann model BK200E anywhere in the old or new equipment catalogs i have access to. I do know that many of the Viessman gas and LP boilers are condensing boilers and do not fall into the Category I venting design that allows for chimney venting.
here are the venting categories:
Category I is characterized by negative pressure and non-condensing appliances. These systems rely on gravity to vent flue gases, and if there is a leak, air from the space will flow into the flue pipe rather than flue gas leaking out. Category I venting systems can use single wall, double wall, B-vent flue pipe, or even a chimney.
Category II is also under negative pressure but may produce excessive condensate. These appliances are typically condensing and have a combustion efficiency greater than 83 percent under ANSI test conditions. However, Category II products are no longer manufactured.
Category III operates with positive pressure and non-condensing appliances. If there is a leak in the venting system, flue gas will flow from the flue pipe into the space, which poses a safety hazard. Therefore, Category III vent pipes must meet additional safety requirements, such as being gas-tight with gas tight venting systems.
Category IV is positive pressure and condensing, typically used for high-efficiency appliances with an annual fuel utilization efficiency (AFUE) of 90 percent or higher. These systems require sealed joints and are often made of materials like PVC or CPVC.
I believe the Viessman boiler you have would fit into Category IV, but I can not be absolutely sure since the model number you posted is either incorrect or is from a time before internet records are available. Absent more information my vote would be the vent according to the manufacturers venting instructions.
EDIT: it appears that Viessmann does make a steam boiler for commercial use. I do not have information on older models, so it is possible that if @heron98105's old Weil McLain is a commercial boiler in the 20 HP range and above,
Then there may be a Viessmann steamer to replace it. I don't have access to older model numbers but the newer boilers may be one of these:
And this Viessmann may be able to be vented into a chimney after you follow @Jamie Hall's suggestion about inspection. The consensus is still "Follow the manufacturer's venting instructions."
Re: Venting into a chimney
I couldn't find that model number so I could reference the listed instructions. However, if this is a condensing boiler, which I believe it is, then the venting must be listed to UL 1738 for positive vent pressure. That would probably mean a polypropylene plastic liner. Masonry chimneys are not approved for positive vent pressure. Most stainless liners are Not listed to 1738 for positive pressure or condensing.
Re: Venting into a chimney
but you could use the unused chimney as a chase to run the correct flue.
Re: Venting into a chimney
Consensus doesn’t matter. The fact is that you cannot vent a condensing boiler into a masonry or metal chimney.
The manufacturer’s installation instructions give detailed info on how the appliance must be vented and it’s mandatory that they be followed.
Ironman