Best Of
Re: Mini Split Location
It's not ugly when it is quietly spewing cool air onto you that's for sure. The "Home" wall is not available he said.
Re: Question about lining 90 year old cast iron sewer pipe
I work for a commercial plumbing company. Our service department has been involved in these kinds of repairs, I do side sewers from time to time with invaded, collapsed or otherwise compromised pipe.
As much as you don't want to cut the concrete, that is where I would go with the inside portion. If the entire sawing operation is done wet you will not have dust anywhere. It requires a crew with wet vacs all the time, some dams to control the water. Done right it is an easy cleanup.
I'd start with the saw operation and remove the concrete and old pipe. Very carefully, expose where it leaves the house and have a lining or bursting contractor send in a sleeve straight down the pipe to the plastic side sewer, taking care of that clay section and far more easily than doing it in a deep pit. Been there done that.
Now you don't have all that weird work around those wyes under the concrete that you would have to cut up anyway. You can put in proper modern plumbing.
skyking1
Re: What's a good humidity meter?
I've been using this for years. The only accuracy tests are comparing it to the display on dehumidifiers or humidistats I work on. Its always within a percentage or 2, so for the +/- range I need, to me its DOBA. I don't need wb or dew point often. It does take some time to acclimate when you first turn it on. About 5 minutes. After that it registers fairly quickly when taking supply and return readings or something.
HVACNUT
Re: Furnace fan will not work
Can you turn the fan by hand? If the fan or motor are bad, that will happen — it will hum for a while then burn out the transformer.
Re: Near boiler piping/replacement boiler
A heat load would add some more info to the question. 1800 sq ft X 25 btu/ ft guesstimate= 45,000BTU/hr required. That is on the coldest day.
80% of the heating season the load could be in the 30,000 range. So the boiler 152,000 you have could be 3-4 maybe 5 times what you need.
While` not hydronically ideal for that boiler, the circs are not causing efficiency issues on the return, unless the system has noisy air issues?
Here is a simple buffer piping, direct to load method. Indirect on priority with its own circ.
hot_rod
Re: Adding C-wire to my system
Yes, you got cereal bowl on the wall thermostat. And, yes, use the C terminal where the Blue wire is on the board. Its definitely a 40 va transformer, unless someone changed it, so it can handle the Nest.
HVACNUT
Re: What's a good humidity meter?
Sling is probably cheaper and accurate. Humidity is always a moving target.
Re: Myers C48D53B86 jet pump- Help
I['ll bet it is an 1/8 npt if you take the brass out? A basic 1/8 radiator bleeder, ball valve, etc.
hot_rod
Re: Myers C48D53B86 jet pump- Help
How far could it have gone ?
Is the bleeder Petcock thread into the casting 1/8" pipe thread ? Maybe just put another valve on it.