Re: HELP! Runaway Heat
inspect it. wire rarely fails without physical damage. especially look for uninsulated staples that may have cut in to it and shorted it
Re: HELP! Runaway Heat
Start with disconnecting the thermostat wires (R and W) at the thermostat itself. Heat shuts off? It's the thermostat. Heat doesn't shut off? Rats. Go to the other end of the thermostat wires and disconnect the wires there. Heat shuts off? It's the wires. Heat doesn't shut off? Something in the controls…
Re: Wireless Outdoor Reset
I've used the tekmar 087 wireless outdoor control many times including on the Us boiler sage control. Works well for me..
Re: Can you please critique this boiler setup that was installed in my house two wks ago
Mistakes happen……………. How the contractor deals with them shows their true character.
Keep us informed.
pecmsg
Re: Can you please critique this boiler setup that was installed in my house two wks ago
It looks like they disconnected and jacked up the original piping, slipped out the old boiler, and slid the new one in its place using a few fittings.
MaxMercy
Re: Bit the bullet: bought an HTP UFT-100W on ebay
you can temp the wiring to run it all as one zone with the zone valves manually opened or the circulators paralleled and put the condensate hose in a bucket to get it running so you have heat…
Re: Water hammer - novice question
Thanks for the commentary…
Regarding water level "does not look too high" - I was trying to say it is not above the water level mark on the side of the boiler enclosure when the hammering occurs. During the non-heating cycle the level typically is somewhat below this line by several inches (like the pic above where you are seeing evidence of oil), though several times I have seen it resting above the water level mark. During heating the level fluctuates less than one inch a couple of times or so per second. It doesn't appear to me to be violent fluctuation (i.e., no water splashing in the gauge) but I am a novice at this. My boiler tech told me it is to be expected during heating. This behavior is very similar now as it was with the old piping. Boiler is early '90s, though I can't vouch for how the earlier owners took care of it.
Drain cycle: 2 different boiler techs have told me a weekly drain until the low water switch activates is a good thing, and I have also read it is a good thing. However I have also read about dangers of too much fresh water addition. Reading more carefully I see a probe-type switch mainly needs a yearly cleaning, and this McDonnell switch seems to be just that. So I will have to interrogate the tech about that next time I talk to him.
Best regards, Steve
Re: DHW mode rapid cycling of boiler
There is a huge difference between an 007 and an 0010, but if you already had an 007 doing okay for 20 years, it's probably okay. With that said, short cycling using that tank still indicates a lack of heat transfer which could be a dirty exchanger an air bubble, or several other possibilities.
Re: Steam Boiler Side Outlet type..... What was your experience with it?
Never heard of "Green Mountain Makes" Must be a Vermont boiler LOl
Re: Hydronic Boiler Tech Needed in Chicago
Is Dave the @The Steam Whisperer still on the site? He is a Chicago area pro.
You might call Able Distributing and get some referrals, they are hydronic smart. Porter Pipe also.
hot_rod