Re: Can't stop the cycling!
I doubt it. The thermostat, that is. But that's easy to check. Find the T-T terminals on your burner control and place a jumper across them. The boiler should fire — and keep firing. If it still cycles, it's something else. If not, it might be the thermostat.
Re: Grundfos Alpha 2 Settings
The AutoAdapt function was all good in theory, but pretty poor in reality. It keeps slowing flow trying to minimize usage until flow is almost non-existent. I like the Alpha for its intended purpose, but that AutoAdapt needs to disappear IMO. Switch it over to one of the constant pressure functions and monitor performance, then adjust as necessary.
Re: Replacing fin tube radiation with cast iron
That looks like maybe 1 1/4" fin tube with maybe 3 1/2 x 3 1/2 or 4 x 4 fins. A lot more than 500 btu/foot. Probably more like 1000/foot or more.
Re: Replacing fin tube radiation with cast iron
is this actually fintube or is it a convector cabinet? do you have some pictures?
the balance problems are more with the higher mass of the cast iron radiators than the output per se.
Re: Replacing fin tube radiation with cast iron
The fin baseboard has no mass and will stop heating pretty shortly after the boiler stops firing while the cast iron will keep heating for a long time because of it's high mass. That can result a cold dining room if the other radiators in the house are cast iron.
Make sure your contractor understands steam or the work may be for naught. The pipes hacv to be the right size threaded steel and has to be properly sloped.
Bob
BobC
Re: Radiant slab operation, as the slab warms
And completely unavoidable. Physics may be a b***h, but thermodynamics is worse. And it illustrates why one makes every effort to bring a radiant system — particularly a slab — to a constant temperature and leave it there. Use some other heating method to make short term changes.
Re: Wildly off topic. Or is it?
I've seen this bumper sticker "It's not off until it's grounded".
Re: Wildly off topic. Or is it?
So it should have been — or rather, so it had been. But there were several other problems which meant that this one stupid failure caused a cascade of other problems. Some were design related, but most of the remaining problems were operational — operating shortcuts which had accumulated of the years with not harm.
Not even that. A wire wasn't stripped correctly, so it couldn't enter the connector fully and eventually wiggled loose.
Re: Hydronics resources for a newbie?
I'll add, Visit Heating Help every day. You have access to thousands of years of experience here. I've learned so much by spending time here.😊
Yours, Larry
Re: Radiant slab operation, as the slab warms
I appreciate the analysis.
Let me offer a slightly different take. When the slab is at steady temperature, the heat flow in and the heat flow out is balanced. The heat flow in is what the boiler provides. The heat flow out can be divided into useful heat, which heats the occupied space, and unusable heat which goes somewhere else.
To get the 27 BTU/sf calculated load, the surface of the slab has to be 13.5F above room temperature. Let's say we've achieved steady state, the room is at 66.5F, the surface of the slab is at 80F. There is 40,500 BTU/hr going into the room, and some unknown amount going into unusable heat.
Then let's turn the clock back to when the heat was turned on. The room was at 50F, the slab was at 50F and heat flow into the slab was zero. So unusable heat was zero. When you first turn the heat on, the slab temperature doesn't change right away, so the heat going into the room is still zero, the unusable heat is still zero, and all of the heat supplied goes into warming the slab.
But as the slab warms, it starts releasing heat into the room as well as losing unusable heat. So if you apply a constant amount of heat, the warmer the slab is, the slower it warms. In fact, if the amount of heat is exactly equal to the heating load, the slab never reaches the design temperature — the closer it gets, the more the heat gain slows.
That's complication one.
Complication two is that the building itself has heat capacity. To get to the final steady state, not only do you have to warm the slab, but you have to warm the building too. If the building is starting at 50F like the slab, as soon as the slab warms at all heat is going to start flowing from the slab into the inside air, and from the air into the building and its contents. So even at the lowest temperatures you don't get the full heat load going into the slab.
If you wanted to fully model this you'd have to model the unusable heat with regard to slab temperature, and you'd have to estimate the heat capacity of the building and model the temperature of the building. You could do this with a spreadsheet with a row for each of a series of time intervals. In each time interval:
- The ending temperature of the slab is equal to the starting temperature of the slab plus net heat flow into the slab divided by the heat capacity of the slab.
- Net heat flow into the slab is equal to heat provided by the boiler less heat used warming the room and unusable heat.
- Heat used warming the room is equal to (starting) slab temperature minus (starting) room temperature times a constant (2 BTU/hr/sf)
- Unusable heat is equal to slab temperature minus ground temperature times a constant
- Ending temperature of the room is equal to the starting temperature of the room plus net heat flow into the room divided by the heat capacity of the room.
- Net heat flow into the room is heat used warming the room less room heat loss
- Room heat loss is (starting) room temperature minus outdoor temperature times a constant
Items in bold are calculated values for each time interval, items in italics are constants that you have to estimate.
If you put all that into a spreadsheet, what you'll see is that heating the slab actually takes quite a bit longer. What you also see is that the higher the heat provided by the boiler, the faster the slab responds and the faster the room warms up.
The ideal configuration is something where you have both an outdoor sensor and a slab sensor. When the slab is warm, use the outdoor sensor to guide outdoor reset to keep the boiler output near the heating load. When the slab is cold, put full output into the slab until it warms up.