Best Of
Re: What type of Vent on pipe near boiler in basement
And @ethicalpaul and @mattmich I agree with you both! And for another look at it, Cedric is a fairly decent sized boiler (fires at 3.3 gph). The system is fairly decent sized (total of arund200 feet of 2 and 2.5 inch mains).
And the whole show is vented with a stable pressure of 2 ounces per square inch gauge by one Hoffman 75 and one Gorton #2…
My own way of figuring it is different — I look at pressure profiles rather than times — but the end result is the same.
Re: Water hammer in steam system
My concern over the copper is not based on the copper itself as it is probably fine. My concern over using copper is that it "points to" may have been installed by a "hot water plumber" versus a "steam fitter" who would likely stick to black pipe. Hot water plumber may not be aware of or take pipe pitch seriously
The change in diameter from Steel to Copper of the same size is not an issue.
Can't tell from pics but the copper pipe in the second picture running back to the riser probably is run flat as there is no swing joint. The hammer could be in that location. The bottom of the riser should have a swing joint and be pitched back to the boiler. You can get away with 1 pipe being flat but if you have 2 pipes flat that causes issues especially if the rises goes up a distance as you will get more condensate in the riser flowing down faster on a cold start
The Gorton is a larger vent maybe slowing the venting could calm things down and make it workable.
Do you know the size of the copper pipe and what the EDR of both radiators is? Looks like maybe 1 1/4" which is good for 55EDR 1" is good for 25EDR?
Re: Bad homeowner steam advise= $$$$$
You burn a lot of fuel and go no where because you have a fan cooled radiator to dissipate the heat.
That same radiator and or a transmission cooler also try to get rid of some of the heat from the torque converter if applicable. If you do it long enough you'll overheat things. It won't just burn fuel and make the heat vanish.
A steam boiler with no vents or bad venting, no radiators etc cannot get rid of it's heat so the burner just shuts down. The heat isn't going to just disappear. IMO it'll result in a cold house, but not astronomical fuel bills, it goes against the First Law of Thermodynamics.
$20,000 in a season, you're not talking about energy steam mains can dissipate.
ChrisJ
Re: Bad homeowner steam advise= $$$$$
@ethicalpaul If you run a steam boiler with poor venting the house cant heat. The basement will be very warm (yes heat goes up through the floor) but the boiler will constantly cycle on pressure, and the fuel bill will be extreme.
It's like a car. Drive the bumper up against a big tree and keep the gas pedal down. You burn a lot of fuel but don't go anywhere.
All the old steam jobs I looked at if the boiler room was excessively hot look at the venting
Re: Horse Barn Radiant Heat
I have done several horse barns and dog kennels. As was said above, we would typically only heat a portion (if any) of the stalls themselves to allow for a cool spot and direct most of the BTU output toward the aisles. I did do one stable where the owner insisted that the whole floor be heated, and the manure would cake up on the floor as well as send a ridiculous amount of nasty moisture into the air (from drying excrement). That one got abandoned in favor of radiant tubes after 3 years
Re: Horse Barn Radiant Heat
You should call the Cornell University Large Animal Hospital, Tufts University Veterinary College or Texas A+M University Veterinary College and ask what they use for heating the floors of their surgery recovery wings for the cows and horses they treat to get a better idea of what should be done for heating these spaces.
Re: Bad homeowner steam advise= $$$$$
I wish I could have seen the coal stoker boiler that heated this house.
Re: Using a hot-water radiator for one-pipe steam
Rent a 4 or 5 foot pipe wrench and 4 pound hammer or buy a 5 foot length of pipe to use on the pipe wrench to get the bushing out of there. If you have a wagner paint melting gun use it for 10 minutes on the cast iron around the bushing and have someone lean against the radiator to hold it in place or better yet and safer lay it on a 6 by 6 or 8 by 8 to use the floor as a back stop to remove the bushing if you do not feel up to using a sawzall to cut it in two or three places.
Re: What type of Vent on pipe near boiler in basement
Those look like Varivalve adjustable straight valves. They are not appropriate for main venting. They are intended to be used on steam radiators. You will want to remove those and the reducing bushings they are piped into. A Gorton #1, Gorton #2, Hoffman 75, or a Barnes and Jones Big Mouth would be appropriate main vents among others. You can find them at SupplyHouse. How long are your steam mains? Can you provide us a picture further out, maybe someone here can give you a better idea of what size vent you need.
Re: Balancing
How are the mains vented? Is a crossover trap from a main to a return failed open and putting steam in the return and closing all the traps along that main so that those radiators can't vent and heat?
Are the returns steam hot anywhere, are they basically the same temp as the supply mains?