Best Of
Re: Monoflo tee and pumping away
If you're replacing a boiler where there's a mono flo system, its important supply and return flow stay the same. Where in a series loop it doesn't matter if you reverse flow in most cases. I've replaced numerous boilers where's there's a mono flo system and the old had the B&G 100 on the return. New installs always pumping away. Never an issue.
HVACNUT
Re: Monoflo tee and pumping away
And the behaviur of a monoflow system has nothing to do with the location of the pump nor even the static pressure in the system. It does, however, have a lot to do with the water velocity in the distribution pipes — so one way to mess it up which your guys may have found is to substitute a very different pump…
Re: Monoflo tee and pumping away
just to be clear the pump could be on the return and still be pumping away as long as the expansion tank is connected at or near the pumps inlet
Many mod cons have the pump on the return to help overcome pressure drop in the boiler
Here are two examples, one with pump at return, one at supply
Typical ci boilers have low pressure drop so tank at return, pump on supply is still “pumping away”
What is important is for the air purger to be at the boiler supply out, the hottest point in the system
hot_rod
Re: What is this?
Emco Wheaton is still in business.
You can Google them. Canadien Company. Looks like they make some type of fluid handling equipment.
Re: Hydronic Baseboard Gap
Rooms with a lot of glass tend to feel "cold" even though the ambient is warm. Your body heat is being pulled to the cold glass. AKA the "cold 70 effect"
Use an accurate thermometer to adjust the wall thermostat reading. There is a differential in the thermostat 1.5- 2° that may be adjustable also. Pull out the manual on your thermostst.
The wall thermostat is on an inside wall?
This smiling gentleman explains cold 70 the concept well.
hot_rod
Re: Commercial Building help please
On your mains I would suggest at least 2, 3 and 4 Gorton 2's respectively on the A, B and 2nd floor mains.
Re: Is Outdoor Reset applicable to gas fired HVAC System?
You mean gas forced air vs gas hot water? There are modulating gas forced air furnaces. I think they modulate based on integrated thermostats that have some algorithm that guesses the firing rate based on room temp vs setpoint and how fast the t-stat is approaching setpoint.
Re: Radiator vents sucking in air at end of cycle
I had to check your math @EBEBRATT-Ed, it's pretty close! Not sure why you picked 28 as your number of units instead of, say, 1 cubic inch of water, but OK!
28" cubed = 28"^3 = 21,952 cubic inches water
28' cubed = (28 * 12)^3 = 37,933,056 cubic inches steam
37,933,056 cubic inches / 1700 (factor of steam vs water volume) = 22,313 cubic inches water
Re: Radiant heating resetting itself
Why do two of your controls show -55 degrees? Since that is the lowest temp these controls can display, wouldn't that imply disconnected sensors? I don't see how that would lead to cycling, though.