Re: Kodak Moment: Yet Another Oil Boiler that had been "maintained"
That boiler had a partially blocked nozzle. I don't know how it kept running without tripping the cad cell, but it obviously ran quite a while. This was in its own room, and there was soot on everything from about 3 feet up. The floor was also pretty wet with oil, so had to remove the boiler and rebuild the room. That place was a mess
Rick
Re: Air conditioning condensate
If you have 2000 CFM at 80F and 70% RH, and magically condense all the water out, you get something like 0.26gpm. I don't even think the numbers work if there results were in pints per minute rather than gpm.
Re: Literature on Geothermal
I was going with a glycol based on my brother's experience, but I think I'll run water to start and monitor temperatures first. You made me a believer in using water when at all possible.
skyking1
Re: Trane Air Handler Fan Constantly Running
In the article that @pecmsg posted, the copper thieves were stealing condensors on a regular basis, so the cops had under cover personnel looking for the thieves. When the officer saw the copper line get cut, that is when he knew that the federal clean air act violation was in play. The cops called the Feds. The Feds have stronger penalties than the local PD has when it comes to just steeling an appliance. Good Call for the cops on this one!
Re: Air conditioning condensate
Really need to know:
SA, DB & WB (or humidity)
RA, DB & WB (or humidity)
But your answer might (should) be in pints (pounds)
Re: DMConsult for Preferred Sales, Inc, (PSI)
Thanks, Dave. Our site has been around since 1997 and we have decades worth of educational content and discussions. Most people find us through Google.
Re: New Propane Boiler Options
Thank you for the article you posted, @Kaos , these are all good things to explore. The example in that article presents a scenario requiring room air dehumidification when it was 90°F outside; this is much different scenario than operating a heat pump water heater in cold climates when outside air is cold and dry.
The ASHRAE article I referenced indicates that heating discharge air from a heat pump water heater is a possible solution as the air impacting a surface can cool it down below the dew point. This is not easy without an external source of heat. Although the discharge is localized, it is informative to see the following analysis on the impact of a heat pump water heater on a room the size of an entire home:
"The best-case scenario for installation in an enclosed space would be a closet the size of an entire house. …The HPWH would be able to extract about 6.2 kBTU of heat from the air (5.3 kBTU sensible + 0.9 kBTU latent). This is not enough heat for a single heating cycle in a typical 3 to 4-person household of this size. Furthermore, cooling indoor surfaces down near 45ºF for more than an hour, multiple times a day, carries a high risk of moisture damage and mold in most climate zones. If the air mass in a 1,625 ft² room does not contain enough energy to heat the water, neither will the air in a smaller room."
Roger
Roger
Re: Hartford Loop design origin
In my house she was called the dishwasher, laundry wench, and cook. (only in my mind LOL) Otherwise called the BOSS!
But by todays standards the Stationary Engineer took over the job of Fireman when the boilers were converted to automatic heating like oil burners or gas burners.