Re: Zoned system or not?
I'm in the land of 2.5 story houses with finished basements. Often these only have a single air handler in the basement for the whole place. To make it work, you will need some seasonal adjustments (simplest is dampers on the main supply trunk) to divert airflow to the right floor. Also you need a large return near the ceiling on the top floor to reduce stratification. This bit is very important and often skimped on.
Zoning with heat pumps is possible and not too expensive especially if you don't need zones to completely turn off. The idea here is to use dumb zone dampers for small sections where you want extra control driven by a local thermostat that is not connected to the main heat pump thermostat at all. These dampers should be set to never fully close to allow some airflow, essentially just modulate the airflow a bit. Important bit here is the zones need to be overprovisioned as this will only work if the zone has extra airflow that can be throttled by the zone damper.
Depending on glazing and orientation, sunrooms generally need special considerations and in some cases their own heat and cooling source. A wallmount on its own compressors is usually the best option.
Two air handlers is the best option but does add cost. If you go this road, make sure to keep the air handler out of the attic.
If you have previous oil use, you can run through the math here to get an accurate heat loss number to avoid oversizing:
Cold climate heat pumps work just fine in your climate. Sized right and installed with some care, it should have no problem heating the place.
Kaos
Re: Zoned system or not?
Carrier Infinity is a very good inverter heat pump. It definitely can be zoned if ducted right. The few I've set up also had hydro coils if needed.
HVACNUT
Re: Torque Wrench
Everyone's idea of just tight enough differs. I have 4 torque wrenches and use them every time it's called for.
When I was 20 and guessing, every torque listed at 30 was 45 F#?, now that I'm 80 every torque listed at 30 is 15 F#. Buy a torque wench and do the job right. So much for guessing.
Re: Oil to propane, Kingston NY area - EDITED.
just realize you paying for quotes weather you know it or not. The ones that you think are doing it for free maybe do a half **** quote don't measure the radiation or do a heat loss so they oversize the equipment. Who pays ? You do with higher fuel costs and an oversized system. The ones that charge you may get the job right. You get what you pay for there is no free lunch. the person that is not charging you is just building his "lost time" into whatever jobs he gets so customers are still paying.
A free quote is not necessarly a good quote or an accurate quote. if they find the job need more work because of an inadequate quote they will say its an unforseen thing and you pay the extra anyhow.
Re: Torque Wrench
We had a rash of electric unit heaters burn up the terminals on the disconnects and/or contactors. I ended up getting a torque screwdriver for the replacements, no issues since then.
I wouldn't say I'm a true believer just yet, but the evidence is mounting so I use it when I can.
Re: Replacing large steel pipes going to/from hot water boiler to cast iron radiators with PEX
Bob @Ironman knows how to make a home-run piping look neat.
And a lifetime DIY hydro separator :)
hot_rod
Re: Replacing large steel pipes going to/from hot water boiler to cast iron radiators with PEX
Perhaps the biggest task for a DIYer will be the fitting transition at each radiator. You may run 1/2" pex to some or all and the radiator, and connection will need to be reduced. Those large 1- 2" pipe and fittings can be a bear to work with.
Some radiator testing I have done with small pex S&R. 2" bushed to 3/4" at the radiator.
hot_rod
Re: Torque Wrench
There are many doods still flaring mini line sets w-o a torque wrench. I started using one about 8 years ago, I thought it was revolutionary!
GW
Re: York furnace slow fan speed
Finally fixed. Upon arrival this morning unit was running correctly. I watched for a couple cycles and then slow fan again and no condenser. I checked voltage and only had 19 on y. Ran new thermostat wire and and problem solved. Thank you for all the information provided. Enjoy your summer
Re: Oil to propane, Kingston NY area - EDITED.
I get that. I recently had a sunroom "kit" built for me and part of that deal was $3500 or so, design and engineering fee, full plans, "wet ink" stamps, ready to throw at the building inspector. Non refundable, if I chose not to have them build it, but I owned the plans.
Seemed fair to me.