Re: Secondary pump selection
A typical 1/2 pex loop is .50 gpm. So the 4 loops add to 2 gpm
You should be fine direct piping. Use a good air separator
Lots if air problems on HH this time if the year
You should be fine direct piping. Use a good air separator
Lots if air problems on HH this time if the year

1
Re: Can I install the Nest Power Connector with this old Honeywell system?
@oldiesystem
I agree with @Jamie Hall
We get several nest questions a week. All their power connectors and gimmicks are questionable. Either pull a c wire to the thermostats and hook then up with a seperate transformer and relay or skip it and use a regular stat with batteries.
Hooking a nest up any other way is unreliable, it may work for a while without the C wire and then it will quit. It's all about the internal batteries. See the attached diagram
I agree with @Jamie Hall
We get several nest questions a week. All their power connectors and gimmicks are questionable. Either pull a c wire to the thermostats and hook then up with a seperate transformer and relay or skip it and use a regular stat with batteries.
Hooking a nest up any other way is unreliable, it may work for a while without the C wire and then it will quit. It's all about the internal batteries. See the attached diagram
Re: Navien NCB 240 flame loss (error 12)
Hi. Problem resolved! We replaced the dual Venturi gas/air mixer. It is located on the left side upper section. It is the housing that the gas and blower connect to. It has a small motor that must be bad. 
System works great now.

System works great now.

2
Re: CO2 - AirThings Monitor & Atmospheric Boiler
@Jamie Hall I updated the photo, this really is CO2, not CO. The AirThings monitor is in the finished part of the room.Exactly.
Are you suggesting that perhaps it is because air from other parts of the house is being pulled downstairs and thus increasing the CO2 while the boiler is running? I hadn't thought of that.
Re: Rinnai Tankless WH
@Tberg2374 You don't mention any codes showing up. Usually, if you are not getting what you ask it shows a code.
This leads me to believe that there might be a installation issue not related to the water heater.
You might want to the dip switch settings.
This leads me to believe that there might be a installation issue not related to the water heater.
You might want to the dip switch settings.

1
Re: Welded 6 inch header
The pattern I have seen with the Weil Mclain LGB steamers, which seem very sensitive to welded headers, is that boilers with welded offset 2 riser headers last about 14 years. Failure mode is almost always leaks between the sections at the seals. Boilers installed with 2 threaded risers and headers or smaller single risers sizes last about 24 years. I consider a 14 year life unacceptable and only the rich can afford the cheaper welded installations. On large boilers we use a welded header but with threaded drop risers, which allows all sorts of expansion and contraction. Also, the header drain and return going back into the boiler needs to be threaded in order to make this corrosion prone piping easier to replace in the future without the huge set up fee for a certified welder. Many installation diagrams also show required threaded joints here also so expansion and contraction of the piping doesn't stress the castings.
Re: Gravity supply tank replacement
I was surprised to see it even had a pilot safety on it under the burner cover. use to see the old valves with even a manual open lever. Ha, that was not such a great idea. That is as simple as it gets boiler. We just re worked some gravity piping for a house last week. Was not working well until we re routed a pipe and flushed the partly blocked underground return. Cool old beasts. She might want to have someone add a low water cutoff to the old beast.
Re: Correcting the code inspector
In New York State the local building department has to petition the state to exceed the standard code. The form they need is attached.
Department of State
Division of Building Standards
and Codes
One Commerce Plaza
99 Washington Avenue, Suite 1160
Albany, NY 12231-0001
Phone: (518) 474-4073
Fax: (518) 486-4487
www.dos.ny.gov
Notice and Petition Relating to More Restrictive Construction
Standards (Uniform Code – Executive Law § 379
Department of State
Division of Building Standards
and Codes
One Commerce Plaza
99 Washington Avenue, Suite 1160
Albany, NY 12231-0001
Phone: (518) 474-4073
Fax: (518) 486-4487
www.dos.ny.gov
Notice and Petition Relating to More Restrictive Construction
Standards (Uniform Code – Executive Law § 379

1