Re: Rinnai Tankless WH
@Tberg2374 You don't mention any codes showing up. Usually, if you are not getting what you ask it shows a code.
This leads me to believe that there might be a installation issue not related to the water heater.
You might want to the dip switch settings.
This leads me to believe that there might be a installation issue not related to the water heater.
You might want to the dip switch settings.

1
Re: Welded 6 inch header
The pattern I have seen with the Weil Mclain LGB steamers, which seem very sensitive to welded headers, is that boilers with welded offset 2 riser headers last about 14 years. Failure mode is almost always leaks between the sections at the seals. Boilers installed with 2 threaded risers and headers or smaller single risers sizes last about 24 years. I consider a 14 year life unacceptable and only the rich can afford the cheaper welded installations. On large boilers we use a welded header but with threaded drop risers, which allows all sorts of expansion and contraction. Also, the header drain and return going back into the boiler needs to be threaded in order to make this corrosion prone piping easier to replace in the future without the huge set up fee for a certified welder. Many installation diagrams also show required threaded joints here also so expansion and contraction of the piping doesn't stress the castings.
Re: Gravity supply tank replacement
I was surprised to see it even had a pilot safety on it under the burner cover. use to see the old valves with even a manual open lever. Ha, that was not such a great idea. That is as simple as it gets boiler. We just re worked some gravity piping for a house last week. Was not working well until we re routed a pipe and flushed the partly blocked underground return. Cool old beasts. She might want to have someone add a low water cutoff to the old beast.
Re: Correcting the code inspector
In New York State the local building department has to petition the state to exceed the standard code. The form they need is attached.
Department of State
Division of Building Standards
and Codes
One Commerce Plaza
99 Washington Avenue, Suite 1160
Albany, NY 12231-0001
Phone: (518) 474-4073
Fax: (518) 486-4487
www.dos.ny.gov
Notice and Petition Relating to More Restrictive Construction
Standards (Uniform Code – Executive Law § 379
Department of State
Division of Building Standards
and Codes
One Commerce Plaza
99 Washington Avenue, Suite 1160
Albany, NY 12231-0001
Phone: (518) 474-4073
Fax: (518) 486-4487
www.dos.ny.gov
Notice and Petition Relating to More Restrictive Construction
Standards (Uniform Code – Executive Law § 379

1
Re: Correcting the code inspector
One of my best stories happened when I was 19. I have been doing this working for the family business for as long as I can remember so I had a lot of experience under my belt at this point but I looked like I was 15.
Some back story: My city went through a brief period where the AHJ decided that we were not allowed to use unions on gas lines any more, instead we were required to use LR nipples and couplings. No idea why and it was changed back the next year. We had installed a buried gas line (PE with anodeless risers) from the meter which was at the street to the house ~20'. Got an inspection with the line under 20 PSI and now had to get a final inspection with the line connected back to the house. I made two swing joints with 4 90's and some nipples and the LR coupling and nipple in between the two sets of 90's which allowed me to start the threads and tighten the coupling and everything pulled straight once the LR coupling was tight. Painted it, turned the gas on, checked for leaks, lit pilots and waited for the inspector.
He shows up and it was his second day on the job and boy was he an arrogant son of a......
He walks up to see little 19 year old me standing proudly next to my work.
Now at this point I have to tell you that the LR couplings that were being sold at my supply house at the time did not have hubs, they instead looked like thread protectors, except they had a big 'LR' stamped in the side. They were proper couplings with tapered threads, they just looked weird.
So up walks this inspector doesn't say a word just stares at the piping scowling for a good 2 or 3 minutes from 10' away. Finally he looks at me and says "Well, thread protectors are not allowed to be used on gas, but I'll let this one slide." To which I respond "That's not a thread protector its actually a LR coupling see? (pointing to stamp on coupling) anyways I wouldn't have been able to get this together without using a LR coupling and nipple." and being the little **** that I was (am?) I then said "so you would let a thread protector go? to my knowledge they have never been approved as fittings because the lack of tapered threads does not make for a good seal." He angrily scrawls a signature on the inspection ticket and walks off without saying a word.
He had so many complaints filed against him that he was taken out of the field after about two months. I heard though I never confirmed it that he threatened to call our local utility and request that they interrupt electrical service to a house undergoing a bathroom remodel when he walked in to do the rough inspections and saw an outlet without a cover on it in a room not associated with the remodel that the HO's were getting ready to paint. Gotta wonder sometimes.....
I think that most inspectors are doing a hard job as well as they can. I always try to be on site when the inspector is there to answer any questions and solve any problems right away. There are a few that I have seen though that just want to be "right" and are doing the job because they get some weird power trip from it. Those can be difficult to deal with, but it is usually an easy call to ask them to give you code citation for their requirement, or as SWEI says go a couple rungs up the ladder and it is solved easily.
Some back story: My city went through a brief period where the AHJ decided that we were not allowed to use unions on gas lines any more, instead we were required to use LR nipples and couplings. No idea why and it was changed back the next year. We had installed a buried gas line (PE with anodeless risers) from the meter which was at the street to the house ~20'. Got an inspection with the line under 20 PSI and now had to get a final inspection with the line connected back to the house. I made two swing joints with 4 90's and some nipples and the LR coupling and nipple in between the two sets of 90's which allowed me to start the threads and tighten the coupling and everything pulled straight once the LR coupling was tight. Painted it, turned the gas on, checked for leaks, lit pilots and waited for the inspector.
He shows up and it was his second day on the job and boy was he an arrogant son of a......
He walks up to see little 19 year old me standing proudly next to my work.
Now at this point I have to tell you that the LR couplings that were being sold at my supply house at the time did not have hubs, they instead looked like thread protectors, except they had a big 'LR' stamped in the side. They were proper couplings with tapered threads, they just looked weird.
So up walks this inspector doesn't say a word just stares at the piping scowling for a good 2 or 3 minutes from 10' away. Finally he looks at me and says "Well, thread protectors are not allowed to be used on gas, but I'll let this one slide." To which I respond "That's not a thread protector its actually a LR coupling see? (pointing to stamp on coupling) anyways I wouldn't have been able to get this together without using a LR coupling and nipple." and being the little **** that I was (am?) I then said "so you would let a thread protector go? to my knowledge they have never been approved as fittings because the lack of tapered threads does not make for a good seal." He angrily scrawls a signature on the inspection ticket and walks off without saying a word.
He had so many complaints filed against him that he was taken out of the field after about two months. I heard though I never confirmed it that he threatened to call our local utility and request that they interrupt electrical service to a house undergoing a bathroom remodel when he walked in to do the rough inspections and saw an outlet without a cover on it in a room not associated with the remodel that the HO's were getting ready to paint. Gotta wonder sometimes.....
I think that most inspectors are doing a hard job as well as they can. I always try to be on site when the inspector is there to answer any questions and solve any problems right away. There are a few that I have seen though that just want to be "right" and are doing the job because they get some weird power trip from it. Those can be difficult to deal with, but it is usually an easy call to ask them to give you code citation for their requirement, or as SWEI says go a couple rungs up the ladder and it is solved easily.

1
Correcting the code inspector
About a year ago I was having dinner with an engineer who worked on a number of large commercial projects in the New York metro area. He mentioned that he sometimes had a code inspector ask for changes which weren't required by the code. He said he handled this by asking the inspector for a code citation because the company required that he give a citation for any work order for changes. The inspector invariably backed down after consulting the code.
How often does this situation happen to you folks? How do you handle it?
How often does this situation happen to you folks? How do you handle it?

1
Re: Long term designed and supported mod-con fantasy?
Chicken or the egg. If they built a 50 year mod con would you pay for it and the manufacturer to support it, inventory parts for 50 years?
Look how we have evolved from the earliest condensors, dating to the late 80's
Even a simple device like an end switch, micro switch. A manufacturer will ask what cycle life are you looking for? They can build a 50, 100, or 200,000 cycle switch. Doesn't sound like a big deal to pay a buck or so more for the best switch. Now multiply that times millions of switches.
Ever stumble across a SunnyWell knock off zone valve
We cycle tested them to death, just about 1 years worth of service.
If I were a betting man I would suggest Harbor f asks for the least expensive, shortest cycle life for many of their products. I've gotten two jobs out of some of their tools
In much of Europe people live in homes for generations. You may see three generations under one roof when you visit. Interesting that 20 year products, boilers, appliances, etc are what you see.
I will say they spend big $$ for kitchen cabinets. They get installed on this unistrut looking frame and you take them with you if you move. Crazy
Look how we have evolved from the earliest condensors, dating to the late 80's
Even a simple device like an end switch, micro switch. A manufacturer will ask what cycle life are you looking for? They can build a 50, 100, or 200,000 cycle switch. Doesn't sound like a big deal to pay a buck or so more for the best switch. Now multiply that times millions of switches.
Ever stumble across a SunnyWell knock off zone valve

If I were a betting man I would suggest Harbor f asks for the least expensive, shortest cycle life for many of their products. I've gotten two jobs out of some of their tools

In much of Europe people live in homes for generations. You may see three generations under one roof when you visit. Interesting that 20 year products, boilers, appliances, etc are what you see.
I will say they spend big $$ for kitchen cabinets. They get installed on this unistrut looking frame and you take them with you if you move. Crazy

3
Utica 95M-200 gas condensing boiler
Full disclosure, I'm not a heating contractor. My post is to provide helpful information.
12 years ago I installed a new Utica 95M-200 gas condensing boiler, (myself). I'll get some flak for that but I was more than experienced to do this and it ran 12 years flawlessly.
In early winter last year I started to experience shut downs. I could get it reset and fire up again but the shut downs continued. In my area no heating contractor wanted to touch this thing and just wanted to install a new system. I wasn't going to do that, I was determined to fix this unit. I read a number of posts on this forum on these units and one fellow in particular seems particularly schooled in working on them, he's posts and comments were very helpful.
Utica would not talk to me because I was not a heating contractor, so be it. Now here's the kicker. The error code that kept coming up was E-65. The fix, inspect wiring and connections, if that doesn't fix the issue replace the blower and if that doesn't fix the issue replace the control module.
The module was the least costly of the two fixes. Replaced it but didn't fix the problem. Replaced the blower and it ran fine for about 2 weeks and started flashing E-65 again. The blower supplier agreed to send a replacement which was installed. This blower was noisy but worked ok for awhile but also had to be replaced.
Now I was on the third blower. This one ran fine but when I put the boiled shroud back on the unit would eventually shut down again flashing E-65 again. (note, this third blower was manufactured in Germany). I did not pay attention to where the first two blowers were made.
I tried other solutions, (parts replacements), nothing worked. Finally I found a contractor familiar with this boiler who was willing to work with me. In his first visit he contacted a tech at Utica who said I needed to replace the wiring harness. (I had the contractor do this, expensive and it did not fix the problem). A few days later he came again and got another Utica tech on the phone. (supposedly their most experienced tech). As soon as the heating guy explained everything that had be going on, the tech said, "replace the blower"! Whaaaat? They sent the contractor a brand new blower (free of charge), (took awhile, and they would not send it to me). He got the new blower and dropped it of to me, (he new I could install it myself which I did). Note: this 4th blower was manufactured in the Chek Republic for Utica.
Bottom line this blower has been working fine, much quieter and I was able to re-install the boiler shroud with no negative effects. The boiler is again running perfectly, (knock on wood).
I spent about $3000 in parts and labor to fix this unit, (still cheaper than replacing it). Who would guess you would have to replace the blower 4 times!! Many lessons learned!! Hope this post helps somebody!
Gene
12 years ago I installed a new Utica 95M-200 gas condensing boiler, (myself). I'll get some flak for that but I was more than experienced to do this and it ran 12 years flawlessly.
In early winter last year I started to experience shut downs. I could get it reset and fire up again but the shut downs continued. In my area no heating contractor wanted to touch this thing and just wanted to install a new system. I wasn't going to do that, I was determined to fix this unit. I read a number of posts on this forum on these units and one fellow in particular seems particularly schooled in working on them, he's posts and comments were very helpful.
Utica would not talk to me because I was not a heating contractor, so be it. Now here's the kicker. The error code that kept coming up was E-65. The fix, inspect wiring and connections, if that doesn't fix the issue replace the blower and if that doesn't fix the issue replace the control module.
The module was the least costly of the two fixes. Replaced it but didn't fix the problem. Replaced the blower and it ran fine for about 2 weeks and started flashing E-65 again. The blower supplier agreed to send a replacement which was installed. This blower was noisy but worked ok for awhile but also had to be replaced.
Now I was on the third blower. This one ran fine but when I put the boiled shroud back on the unit would eventually shut down again flashing E-65 again. (note, this third blower was manufactured in Germany). I did not pay attention to where the first two blowers were made.
I tried other solutions, (parts replacements), nothing worked. Finally I found a contractor familiar with this boiler who was willing to work with me. In his first visit he contacted a tech at Utica who said I needed to replace the wiring harness. (I had the contractor do this, expensive and it did not fix the problem). A few days later he came again and got another Utica tech on the phone. (supposedly their most experienced tech). As soon as the heating guy explained everything that had be going on, the tech said, "replace the blower"! Whaaaat? They sent the contractor a brand new blower (free of charge), (took awhile, and they would not send it to me). He got the new blower and dropped it of to me, (he new I could install it myself which I did). Note: this 4th blower was manufactured in the Chek Republic for Utica.
Bottom line this blower has been working fine, much quieter and I was able to re-install the boiler shroud with no negative effects. The boiler is again running perfectly, (knock on wood).
I spent about $3000 in parts and labor to fix this unit, (still cheaper than replacing it). Who would guess you would have to replace the blower 4 times!! Many lessons learned!! Hope this post helps somebody!
Gene