Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
If our community has helped you, please consider making a contribution to support this website. Thanks!
Best Of
Re: Boiler High Limit set too low?
Thanks @Jamie Hall that is good to know. Even under normal circumstances, I think the boiler left to its own devices rarely gets above 135 when the weather is warmer than 20 degrees - and it only does so because of the existing mixing valve. The mixing valve is only on the return line to keep it above 122 degrees. Before that was installed, it would run for 45 and never get above 115-120 degrees and satisfy the house Tstat. We had -5 degree days in a row and the house was satisfied and the highest the boiler could get the water temp was 139/140 for an hour, boiler only ran 8-9 hours those days.
I'll put it back to the previous max of 143 (which it never hits) and put some sensors on the supply side to log max temp needed based on outside temp. Would be an interesting chart.
I'll put it back to the previous max of 143 (which it never hits) and put some sensors on the supply side to log max temp needed based on outside temp. Would be an interesting chart.
1
Re: one pipe steam Radiator vents
Interesting. Is this a continuous suction? Or is it pulses at specific radiators. I honestly can't think of a mechanism which will create a continuous suction at a vent or even an open pipe so long as the boiler is firing, unless there is an eductor or vacuum pump on the system -- and that wouldn't be found on a one pipe system (and is rare on residential two pipe systems...).
If it's in pulses, and different at different radiators, there is a possibility that the problem has to do with pockets of trapped water in the piping, which could also cause the banging -- but that would only be very short pulses at specific radiators.
And... not that I doubt your observation, but double check. Are they really sucking, indicating a vacuum, or are they actually blowing?
If it's in pulses, and different at different radiators, there is a possibility that the problem has to do with pockets of trapped water in the piping, which could also cause the banging -- but that would only be very short pulses at specific radiators.
And... not that I doubt your observation, but double check. Are they really sucking, indicating a vacuum, or are they actually blowing?
Re: How accurate are the efficiency percentages claimed by the mod con boiler mfr's?
So? If a system radiation needs more than 127 degrees water temperature in the radiators, it would seem that there is no condensation of exhaust gases. This being the case, why recommend a mod con boiler?It's the return temperature at the boiler that determines how much it condenses.
The dewpoint of the fuel depends some want on the CO2, which is what the combustion analyzer reads to come up with efficiency, and the setting that the boiler manufacturer wants.
My Lochinvar asks for CO2 9- 10.5% on high fire NG, 8.8- 9.5% on low fire as an example.
Also some Viessmann slides explaining condensing mode.
My Lochinvar Knight allows up to a 35∆, so to obtain a 120 condensing temperature I could run a 155° SWT, return is at 120 and condensing starts.
hot_rod
2
Re: Which is the C (common) terminal on a Honeywell Aquastat L8148E?
this is all that is needed
TV on L8184E control = R on the NEST
Z on L8184E control = C on the NEST
T on L8184E control = W on the NEST
Don't change any jumper between Z and W on L8184E control. Leave it where it is.
Must I remind everyone that Electric is colorblind and it can't read either. This works for the control that @erikengquist shows in the picture. L8148E. It does not work for other controls like the L8148A
TV on L8184E control = R on the NEST
Z on L8184E control = C on the NEST
T on L8184E control = W on the NEST
Don't change any jumper between Z and W on L8184E control. Leave it where it is.
Must I remind everyone that Electric is colorblind and it can't read either. This works for the control that @erikengquist shows in the picture. L8148E. It does not work for other controls like the L8148A
Re: Troubleshooting of recurring overheating events
Hello @zxcv_1984,
Intermittent problems can be the worst. A lot of time can be spent trying to catch them in the act. Sometimes it helps if whatever stimulus is causing the problem can de determined. Is it Weather related, water ingress, amount of use, vibration, loose connections, chafed wires, etc.
If the sensors and their electrical connections are all fine, wouldn't the controller shut the pump off correctly to limit the storage tank temperature ?
If the relay that controls the pump was sticking, for example, how would the controller shut the pump down for an overheating event, it would need a secondary means.
Is the normal operating high limit temperature setting too close to the overheating limit temperature setting ?
Intermittent problems can be the worst. A lot of time can be spent trying to catch them in the act. Sometimes it helps if whatever stimulus is causing the problem can de determined. Is it Weather related, water ingress, amount of use, vibration, loose connections, chafed wires, etc.
If the sensors and their electrical connections are all fine, wouldn't the controller shut the pump off correctly to limit the storage tank temperature ?
If the relay that controls the pump was sticking, for example, how would the controller shut the pump down for an overheating event, it would need a secondary means.
Is the normal operating high limit temperature setting too close to the overheating limit temperature setting ?
3
Re: How accurate are the efficiency percentages claimed by the mod con boiler mfr's?
@pecmsg: thanks for your comment; that's what I think too. I don't think I have ever seen my car mileage even close to the advertised mileage. Probably the mfr is using a brand new boiler and if it doesn't give them the result they want, they are going to try another until they get the result they want. What about a boiler that's been used for one season let alone 10 seasons(half way through the life cycle)? Won't the efficiency go down (even a little) as the the little spaces in the heat exchanger get filled up with debris?
1
Re: How accurate are the efficiency percentages claimed by the mod con boiler mfr's?
The return water temperature drives the boilers efficiency, they can and do reach high 90% efficiencies
Cycle efficiency and system efficiency is another discussion
hot_rod
1
Re: Indoor Reset
Just Wish
They'd give some details on the actual operation of the brain--in particular how it deals with situations where it's forced to go into digital operation. Also, some details about how it handles WWSD would be very valuable.
It appears to allow a substantial drop in system temperature when it's near what I consider WWSD, but I have a sneaking suspicion that if it's say 20° outside and the load is still very low that it won't allow so much drop.
Would hate to make the tank too big and create much of a parasitic load in non-conditioned space, but at the same time want to ensure the boiler finds enough load to keep burn time reasonably long...
Let's see:
Say I want to reserve 11,000 BTUs with a 7° temperature variance. So, I can put 7 BTUs into each pound of water. 11,000 / 7 = 1571 pounds of water. 188 gallons--tank TOO big and/or temp variance too small.
If I work the other way:
Say a 60 gallon tank weighing 500 pounds. With a 10° differential I can reserve 5,000 BTUs.
If the load on the system is 10,000 BTU/hr and the burner can deliver a minimum of 22,000 BTUs in an hour and IF (the BIG if) the boiler allows a 10° variance at whatever outside temp this loss corresponds to, I think the burner would fire for about 40 minutes, then go off for about 30.
Sound logical? 10° supply temp variance over 70 minutes doesn't sound too bad...
Send me those losses and other data, Mike! Make sure you include city--I'll look up weather data.
They'd give some details on the actual operation of the brain--in particular how it deals with situations where it's forced to go into digital operation. Also, some details about how it handles WWSD would be very valuable.
It appears to allow a substantial drop in system temperature when it's near what I consider WWSD, but I have a sneaking suspicion that if it's say 20° outside and the load is still very low that it won't allow so much drop.
Would hate to make the tank too big and create much of a parasitic load in non-conditioned space, but at the same time want to ensure the boiler finds enough load to keep burn time reasonably long...
Let's see:
Say I want to reserve 11,000 BTUs with a 7° temperature variance. So, I can put 7 BTUs into each pound of water. 11,000 / 7 = 1571 pounds of water. 188 gallons--tank TOO big and/or temp variance too small.
If I work the other way:
Say a 60 gallon tank weighing 500 pounds. With a 10° differential I can reserve 5,000 BTUs.
If the load on the system is 10,000 BTU/hr and the burner can deliver a minimum of 22,000 BTUs in an hour and IF (the BIG if) the boiler allows a 10° variance at whatever outside temp this loss corresponds to, I think the burner would fire for about 40 minutes, then go off for about 30.
Sound logical? 10° supply temp variance over 70 minutes doesn't sound too bad...
Send me those losses and other data, Mike! Make sure you include city--I'll look up weather data.
Re: Indoor Reset
Danfoss has
an indoor reset control. It was built to help overcome solar gain problems. I tried on on my office which has a long windowed south facing wall. Mine was tied to a 3 way Esbe valve with a motor actuator.
hot rod
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
an indoor reset control. It was built to help overcome solar gain problems. I tried on on my office which has a long windowed south facing wall. Mine was tied to a 3 way Esbe valve with a motor actuator.
hot rod
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
1

