Re: New Steam Boiler Install - Black Liquid in Gauge Glass
This is essentially the same boiler as you have. You can see the vent damper in this picture. It is the device mounted to the draft hood with the round black actuator mounted to the side. It will also have wiring running to it. It comes with these boilers and was paid for as part of the boiler package. Not supposed to discuss price, but they aren't inexpensive so you paid for it, it should be installed. I should also add you can see the skim port installed in this photo as well. It is the large pipe on the side with the valve. I put a valve on mine, but that isn't necessary. All you really need is a pipe and a cap for when it isn't being used.


5
Re: Threading pipe for slope
The correct answer for this is what the old timers called "cutting a drip thread" No one I know does this anymore. Your going to have to make it up with 90s, 45s and swing joints etc They used to cut a crooked thread on a pipe to get the slope or pitch they wanted
I've been doing this 42 years and never cut a drip thread (don't know how) I've only read about it. You would need a threader like a Ridgid 65R where you can set the gide collar on the back "off center". They also make a 65R -TC which you cannot use for this. the tc stands for "true center"
I've been doing this 42 years and never cut a drip thread (don't know how) I've only read about it. You would need a threader like a Ridgid 65R where you can set the gide collar on the back "off center". They also make a 65R -TC which you cannot use for this. the tc stands for "true center"
Re: Converting 2 pipe hot water to 3 zones?
Just in case any of that didn't make sense, we can help you figure the sizes out. http://www.slantfin.com/homeowners-page/ipadapp.html will get you started.
SWEI
5
Re: Converting 2 pipe hot water to 3 zones?
Pipe sizing depends on flow rate, which in turn depends on the room-by-room heat loss and an emitter survey.
How much heat does this room need on the coldest day of the year? What temperature water is needed with the radiation I have installed in order to deliver the required heat?
How much heat does this room need on the coldest day of the year? What temperature water is needed with the radiation I have installed in order to deliver the required heat?
SWEI
5
Re: How to bleed just 1 zone
You could shut off power. Shut the isolation flanges on that pump. Loosen the 4 bolts and rotate the pump. Then you would need to take out the 4 Allen bolts on the motor and rotate it so the electrical box faces up. You may or may not have to disconnect power wiring to the pump.
5
Re: How to bleed just 1 zone
Turn off power also. No need to dead head those other pumps if you get a heat call.On the Tstat 's they are probably setup for hot air. You will need to get into the installer setup to verify.
5
Re: Why does a 17000 btu electric boiler have 1 1/4 inch taps?
sometimes that one block gets used for a range of outputs. Just add additional, or higher KW elements. Cast iron boilers also, even a low BTU boiler might have the same tappings as larger sizes.
hot_rod
5
Re: Buffer Tank - Pros and Cons?
Actually large buffers can be charged under no or low load conditions, then flywheel for weeks or months. I've seen some large solar thermal system in Europe that charge enough buffer in the summer to run the building all winter, heat and DHW with no back up and very low winter solar input.
Actually isn't hat have ground source GEO works, storing solar energy in the earth.
For hydronics it usually involves well insulated, multi thousand gallon tanks. Not for the weak of pocketbook.
Actually isn't hat have ground source GEO works, storing solar energy in the earth.
For hydronics it usually involves well insulated, multi thousand gallon tanks. Not for the weak of pocketbook.
hot_rod
5
Re: Leak in return pipe.
You can always find the clamp type pipe repair kit, with a rubber gasket, which will close up a leak. In both cases, the pipe surface around the repair must be cleaned/sanded thoroughly. If the JB weld does not work, then all traces of the epoxy must be removed to make the clamp type repair work, and that can be difficult.--NBC