Re: Iron Oxide Limitations With ECM Circs
Henry's law states that when a fluid is heated it holds less dissolved solids. Bottles law deals states that when the pressure increases, the volume decreases which is why a diaphragm tanks is used in a system to accept the expansion of the water when heated. Check the web for both Henry and Boyles Law. It applies to what we do everyday.
Deionized water is cool and helps tremendously but only helps. Corrosion can still occur. Inhibitors help in addition to but need to be checked at some interval.
Deionized water is cool and helps tremendously but only helps. Corrosion can still occur. Inhibitors help in addition to but need to be checked at some interval.
Re: Iron Oxide Limitations With ECM Circs
If "Deionization" is anything like RO, it's my understanding and experience (in plumbing) that you open yourself up to a multitude of unintended consequences.What are those unintended consequences Ice? Keeping in mind the system being closed loop with a sacrificial anode and/or a PH buffer.
Re: Iron Oxide Limitations With ECM Circs
If "Deionization" is anything like RO, it's my understanding and experience (in plumbing) that you open yourself up to a multitude of unintended consequences.
"Henry's Law" explains a lot of the unexplained for me.
They stick this clip on your finger and it can tell the O2/Oxygen level in your blood. There are parameters.
If water consists of one part Hydrogen, and two parts Oxygen, there must be a Oxygen Parameter in water, We know that water can hold varying levels of dissolved oxygen. If oxidation of metal is caused by Oxygen, is there a minimum level of O2 in water that helps slow down oxidation?
If the oxygen levels in a pond level are decreased below a certain level, fish will die. Same if the levels become too high.
My wife's horse is sick. Last night it was getting an IV. I noticed that there was a water level in the drip tube. They added another upper bag to get the flow to speed up. The level went up 3/4" in the drip tube. There were air bubbles from the old level down, and none to the new and higher level. Where did the bubbles come from? Its a closed system. The IV bag has to be high enough to overcome the blood pressure in the body. It can't run backwards. I'm curious. About such things.
Were the bubbles from the water? Or from Oxygen being forced through the clear plastic tube like it is supposed to happen with non barrier PEX tubing?
"Henry's Law" explains a lot of the unexplained for me.
They stick this clip on your finger and it can tell the O2/Oxygen level in your blood. There are parameters.
If water consists of one part Hydrogen, and two parts Oxygen, there must be a Oxygen Parameter in water, We know that water can hold varying levels of dissolved oxygen. If oxidation of metal is caused by Oxygen, is there a minimum level of O2 in water that helps slow down oxidation?
If the oxygen levels in a pond level are decreased below a certain level, fish will die. Same if the levels become too high.
My wife's horse is sick. Last night it was getting an IV. I noticed that there was a water level in the drip tube. They added another upper bag to get the flow to speed up. The level went up 3/4" in the drip tube. There were air bubbles from the old level down, and none to the new and higher level. Where did the bubbles come from? Its a closed system. The IV bag has to be high enough to overcome the blood pressure in the body. It can't run backwards. I'm curious. About such things.
Were the bubbles from the water? Or from Oxygen being forced through the clear plastic tube like it is supposed to happen with non barrier PEX tubing?
Re: Iron Oxide Limitations With ECM Circs
I agree with Harvey on Henry's Law. It does not apply to solids.

5
Re: Iron Oxide Limitations With ECM Circs
Some of the hydraulic valves we deal with at work, can't handle 5 micron particles. I know, it's a different animal,but enough of those particles, and you have a problem. We use a filter with a bypass indicator. The pump can't be dead-headed. Something like that would be childs-play for Caleffi engineers. The whole package... a DirtMag pre-filter with a secondary filter w/ bypass(pop-up indicator).

5
Re: Iron Oxide Limitations With ECM Circs
Anybody ever hear of "Henry's Law"? Water can hold "X" amount of dissolved solids in solution. But whe you heat water up, those undisolved solids come out of solution in the form of a gas (air in the system) or solids (sludge, dirt and sludge) in the system or boiler. Henry's Law is always at work in the system especially more pronounced when you fill a system with fresh water. Now let's mix some dissimilar metals in the system connect by water and you get electrolysis and electrolysis creates acids. These acids break down the metal in the system and "Wa La", iron oxides and lots of other stuff. We all know soot in the heat exchanger cause a loss of efficiency. We need to ask ourselves if this stuff we created in the water side of the system acts like soot in the heat exchanger and the answer is YES. We make heat efficiently and transfer the same into the water, the water gets moved by the circ but it can't get out of the pipe due to the coating created on the inside surface of the pipe. Fernox has proven this with many studies. The have a solution. You can clean the system with the cleaner, treat the system with the inhibitor and if the system is real big or has lots of stuff in it, they have a machine with a very nice size motor on it to speed up the process. Then there's the TF1 bypass unit that has a magnet in it to help us remove iron oxide.I was under the impression that Henry's law deals with gasses, no?
Fernox has proven that if you install a new 90+% boiler in a system that hasn't been cleaned and treated, that boiler can end up in the high 80's % efficiency range and you'll never get it back with out cleaning and treating.
Food for thought: the next time you install a new high efficient unit, ask yourselves this knowing what's being created in the system, have we really helped our customer.
If an ostrich is being chased by a lion, and the ostrich does what it does when stressed and sticks its head in the ground, does the lion stop attacking and go away?
Please do not think for one minute that this water quality issue is just a bunch of "hogwash". It's real and we should have been looking at this years ago.
Everything else I agree on.
There is another alternative to chemical treatment that I am in favor of. That consists of deionization of the system water. This will lower the TDS and the conductivity of the fluid. Then a sacrificial anode is placed inline. Elysater has good information on this technology.
Re: Iron Oxide Limitations With ECM Circs
Anybody ever hear of "Henry's Law"? Water can hold "X" amount of dissolved solids in solution. But whe you heat water up, those undisolved solids come out of solution in the form of a gas (air in the system) or solids (sludge, dirt and sludge) in the system or boiler. Henry's Law is always at work in the system especially more pronounced when you fill a system with fresh water. Now let's mix some dissimilar metals in the system connect by water and you get electrolysis and electrolysis creates acids. These acids break down the metal in the system and "Wa La", iron oxides and lots of other stuff. We all know soot in the heat exchanger cause a loss of efficiency. We need to ask ourselves if this stuff we created in the water side of the system acts like soot in the heat exchanger and the answer is YES. We make heat efficiently and transfer the same into the water, the water gets moved by the circ but it can't get out of the pipe due to the coating created on the inside surface of the pipe. Fernox has proven this with many studies. The have a solution. You can clean the system with the cleaner, treat the system with the inhibitor and if the system is real big or has lots of stuff in it, they have a machine with a very nice size motor on it to speed up the process. Then there's the TF1 bypass unit that has a magnet in it to help us remove iron oxide.
Fernox has proven that if you install a new 90+% boiler in a system that hasn't been cleaned and treated, that boiler can end up in the high 80's % efficiency range and you'll never get it back with out cleaning and treating.
Food for thought: the next time you install a new high efficient unit, ask yourselves this knowing what's being created in the system, have we really helped our customer.
If an ostrich is being chased by a lion, and the ostrich does what it does when stressed and sticks its head in the ground, does the lion stop attacking and go away?
Please do not think for one minute that this water quality issue is just a bunch of "hogwash". It's real and we should have been looking at this years ago.
Fernox has proven that if you install a new 90+% boiler in a system that hasn't been cleaned and treated, that boiler can end up in the high 80's % efficiency range and you'll never get it back with out cleaning and treating.
Food for thought: the next time you install a new high efficient unit, ask yourselves this knowing what's being created in the system, have we really helped our customer.
If an ostrich is being chased by a lion, and the ostrich does what it does when stressed and sticks its head in the ground, does the lion stop attacking and go away?
Please do not think for one minute that this water quality issue is just a bunch of "hogwash". It's real and we should have been looking at this years ago.
Re: Iron Oxide Limitations With ECM Circs
We put a high flow 20µ pleated paper filter (Big Blue 20") in the return line to the purge cart (after the open flush and before the boiler is fired.) The amount of crud that comes out of old systems can be quite impressive. Once that is running clean (typically an hour or two) we let the DirtMag do its job.

5
Re: Iron Oxide Limitations With ECM Circs
@Steve Thompson (Taco):
For what anything is worth, I once read a book by Stan Grayson about old one cylinder gasoline marine engines. Which were the next generation of steam engines except some smart dude figured that you could use the expanding gasses of gasoline without the added weight and complexities of a steam boiler. They also used these same engines on fresh water lakes. Today, if you can ever find a working make or break engine, it came from a lake. Because all the marine engines returned to the state they started out. Powdered iron.
It is said that iron is the most common element in the earth. It is not found in the form of a cast iron circulator or engine block. It started out as a powder or some other form. It has to be refined to turn it into cast iron or steel. It can be recycled. The town I lived in on Cape Cod had a terrible problem with dissolved iron in the ground. So much so that the end of the town I lived in, had all wells with high iron in the water. They put a municipal well system in near me and had to spend millions of a manganese greensand filter to oxidize the dissolved iron into a solid so they could filter it out. My water was clear as a bell but you could taste the slight iron taste. The water was slightly acidic with a PH of 6.7 or 6.8. I installed a whole house 2 Cu. Ft. calcite flow through neutralizing filter with raised the PH to over 7.0. Before or after, I never got any rust slime in the bottom of a drinking glass left out overnight. My heating system was filled with the untreated water before I moved into the finished house. I don't think I ever completely removed the water from the system. I sold the house in June of 2013. The water in the system turned redder and redder with age. The iron was already in the water when it was installed. I've seen that same calcified plaque iron on circulator impellors where there was no flow, stuck on surfaces. (my thing about impellor cavitation) and inside some circulator volutes. If anything is out of the ordinary, I noticed it. With water well pumps that pumped in high iron locations, you would see that same calcified hard iron on the low flow parts of brass impellors and especially around and on Bakelite impellor diffuser covers. I saw it on Stainless Steel water pumps. The common denominator to me was the presence of iron and vast amounts of friction which probably create vast amounts of static electricity, that was doing a form of electroplating to surfaces. My heating system was a cast iron boiler with a Taco 007 until I changed it to a Wilo ECM. If I drained the water from the system, the rust was still in the water when I filled it back up. It coated everything.
Getting back to the old one lung marine engines. They failed because the salt water sets up a very good environment for the cast iron to change to what it was when it was in the earth. A powder. Rust on steel bridges or cars is just Cast Iron in a state where it can go back into the earth.
Personally, without any educated expertise. it would be interesting to see what magnetic separation collectors would do in a closed heating system. There are already many, many other magnetic sources in a heating systems. What's another?
Here's another example of what I am saying.
The two units to the East of me, developed low water pressure in their units. One was unoccupied, the one next to me was. The City came and futzed around with it and decided that it was "Calcified" or had "Calcium Build Up" at the Corporation Cock at the main. So, a few days later a large gang showed up to fix it. Let me say right out, that I have paid my dues for many years, playing earth Guitar in the Dirt Band. Where I came from, and the band I played in, this work was done by one or two musicians. Playing 5' Banjo's. This job required a mini-excavator and 6 men. two as arguing supervisors. Eight if you count the two that came on a Saturday to gig it up, decide it wasn't the curb stops, (4" from the main) and fill in the hole They ripped out everything in sight except for any rubber roots with the copper core. When they got down to business after the destruction, the main was 2" Sch. 80 PVC pipe with a Cast Iron clamp on saddle fitting, a brass Corporation cock, brass adapters, and then to Poly Pipe. The "Calcification" was in the cast iron adapter that made the connection to the 2" PVC main. The "Calcification" is from the iron in the water which the city adds something to encapsulate the iron in the water and lots of chlorine to kill critters. Where I'm from, they would have poked a beater screwdriver in to the obstruction and let the rust particles flow out with the water.
The only dis-similar metals were the Cast Iron saddle adapter and the brass Corporation Cock.
It took 30+ years to occlude.
Don't they use Iron Oxide for some forms of sand paper?
For what anything is worth, I once read a book by Stan Grayson about old one cylinder gasoline marine engines. Which were the next generation of steam engines except some smart dude figured that you could use the expanding gasses of gasoline without the added weight and complexities of a steam boiler. They also used these same engines on fresh water lakes. Today, if you can ever find a working make or break engine, it came from a lake. Because all the marine engines returned to the state they started out. Powdered iron.
It is said that iron is the most common element in the earth. It is not found in the form of a cast iron circulator or engine block. It started out as a powder or some other form. It has to be refined to turn it into cast iron or steel. It can be recycled. The town I lived in on Cape Cod had a terrible problem with dissolved iron in the ground. So much so that the end of the town I lived in, had all wells with high iron in the water. They put a municipal well system in near me and had to spend millions of a manganese greensand filter to oxidize the dissolved iron into a solid so they could filter it out. My water was clear as a bell but you could taste the slight iron taste. The water was slightly acidic with a PH of 6.7 or 6.8. I installed a whole house 2 Cu. Ft. calcite flow through neutralizing filter with raised the PH to over 7.0. Before or after, I never got any rust slime in the bottom of a drinking glass left out overnight. My heating system was filled with the untreated water before I moved into the finished house. I don't think I ever completely removed the water from the system. I sold the house in June of 2013. The water in the system turned redder and redder with age. The iron was already in the water when it was installed. I've seen that same calcified plaque iron on circulator impellors where there was no flow, stuck on surfaces. (my thing about impellor cavitation) and inside some circulator volutes. If anything is out of the ordinary, I noticed it. With water well pumps that pumped in high iron locations, you would see that same calcified hard iron on the low flow parts of brass impellors and especially around and on Bakelite impellor diffuser covers. I saw it on Stainless Steel water pumps. The common denominator to me was the presence of iron and vast amounts of friction which probably create vast amounts of static electricity, that was doing a form of electroplating to surfaces. My heating system was a cast iron boiler with a Taco 007 until I changed it to a Wilo ECM. If I drained the water from the system, the rust was still in the water when I filled it back up. It coated everything.
Getting back to the old one lung marine engines. They failed because the salt water sets up a very good environment for the cast iron to change to what it was when it was in the earth. A powder. Rust on steel bridges or cars is just Cast Iron in a state where it can go back into the earth.
Personally, without any educated expertise. it would be interesting to see what magnetic separation collectors would do in a closed heating system. There are already many, many other magnetic sources in a heating systems. What's another?
Here's another example of what I am saying.
The two units to the East of me, developed low water pressure in their units. One was unoccupied, the one next to me was. The City came and futzed around with it and decided that it was "Calcified" or had "Calcium Build Up" at the Corporation Cock at the main. So, a few days later a large gang showed up to fix it. Let me say right out, that I have paid my dues for many years, playing earth Guitar in the Dirt Band. Where I came from, and the band I played in, this work was done by one or two musicians. Playing 5' Banjo's. This job required a mini-excavator and 6 men. two as arguing supervisors. Eight if you count the two that came on a Saturday to gig it up, decide it wasn't the curb stops, (4" from the main) and fill in the hole They ripped out everything in sight except for any rubber roots with the copper core. When they got down to business after the destruction, the main was 2" Sch. 80 PVC pipe with a Cast Iron clamp on saddle fitting, a brass Corporation cock, brass adapters, and then to Poly Pipe. The "Calcification" was in the cast iron adapter that made the connection to the 2" PVC main. The "Calcification" is from the iron in the water which the city adds something to encapsulate the iron in the water and lots of chlorine to kill critters. Where I'm from, they would have poked a beater screwdriver in to the obstruction and let the rust particles flow out with the water.
The only dis-similar metals were the Cast Iron saddle adapter and the brass Corporation Cock.
It took 30+ years to occlude.
Don't they use Iron Oxide for some forms of sand paper?
Re: Iron Oxide Limitations With ECM Circs
That's why everyone is looking at the mag sep add on. Grab as much as possible first trip. We put X amount of ferrite in a circuit and measure what collects.
Still the best plan would be to treat the problem, not the symptom. Why are we seeing the iron ferrite. Has it always been flowing around the systems? I've really never looked for it until it started showing up in permanent magnet circs.
One thing to remember about vortex separation, it takes some fairly high velocities to make them work. We built a clear plastic version, connected to a Grundfos Magna so we could dial in exact flow rate Connected the ultrasonic flow meters to confirm.
As we see more and more variable speed circ on both side, boiler and distribution, the ability to use vortex separation efficiently may be in question. Or perhaps program the pumps to assure high velocities for certain periods of time, then modulate.
Having built clear samples of both, no question the media type seperators are amazingly effective from very low, to well over the normal velocities you would expect to see in typical hydronics. We run 'em out to 10- 12 fps on the test bench
Still the best plan would be to treat the problem, not the symptom. Why are we seeing the iron ferrite. Has it always been flowing around the systems? I've really never looked for it until it started showing up in permanent magnet circs.
One thing to remember about vortex separation, it takes some fairly high velocities to make them work. We built a clear plastic version, connected to a Grundfos Magna so we could dial in exact flow rate Connected the ultrasonic flow meters to confirm.
As we see more and more variable speed circ on both side, boiler and distribution, the ability to use vortex separation efficiently may be in question. Or perhaps program the pumps to assure high velocities for certain periods of time, then modulate.
Having built clear samples of both, no question the media type seperators are amazingly effective from very low, to well over the normal velocities you would expect to see in typical hydronics. We run 'em out to 10- 12 fps on the test bench