Re: Should I be worried about what I am observing and hearing (radiant heat install in process)?
I hate to see shavings coming off the tubing, but to be fair, it happens. I literally take my knife and remove the sharp edges of the hole before pulling it in, but I am paranoid. Those scrapes (unless really severe) will not compromise the strength of the pipe but it is removing a bit of O2 barrier. After system has been in operation for a while it makes dark spots on the tubing evey place the O2 is getting in. The damage to the O2 barrier during install is one reason pex systems still get more O2 into the system than good old copper/steel systems.
As someone who has done floor heat for years, I still do staple up on a typical room on almost all jobs. The bath on the outside corner or the sunroom will get plates. On a typical job I am happy if my design temp is 140* and some jobs it is a good bit higher. You may say 110 would be much better and more efficient! Sure. But seriously, the $1000s that joist trak will cost to add to a whole house will not be recouped in savings for …. what… decades??? If doing plates on a floor with nails, use the extruded style because the tubing snaps in the underside of plate thus the tubing won't be pushed against the old nails.
As others have posted, you must know what all layers the floor consists of. If you take a shot in the dark, expect to miss sooner or later.
Re: Should I be worried about what I am observing and hearing (radiant heat install in process)?
If you use HTP , you must grind off any protruding nails thru the subfloor. I use the following grinder and wear eye protection when grinding. You can buy this grinder for peanuts at Harbor Freight stores. Cheaper than a pack of cigarettes in New York city.
https://www.harborfreight.com/5-amp-4-12-in-slide-switch-angle-grinder-58092.html
Re: Should I be worried about what I am observing and hearing (radiant heat install in process)?
Here’s the plates that we prefer. 6 screws hold one plate which holds both pipes in a 16” OC joist bay. Single tube plates can be used in small narrow bays.
Ironman
Re: Should I be worried about what I am observing and hearing (radiant heat install in process)?
This is a pretty accurate on-line tool (need to register but free):
The hard part with existing houses is how leaky the place is, there is no easy way to get an accurate handle on this except for a blower door test. Older houses definitely tend to be on the leaky side.
Kaos
Re: Cleaning Alpha 2 circulator by running at higher speed
Is the boiler piped primary secondary or with a hydraulic sep? If so you should not need to lock TRVs open to keep flow moving. With all TRVs closed the Alpha will go into an "idle" mode where it barely spins just to get a reference point, around 7W.
Is the Alpha switched on by a relay box? Caleffi ZCR and some others have an exercise switch to run the pump.
The gpm readout is based on power consumption, rpm, and the calculations by in the computer, as I understand it.
hot_rod
Re: No 1 Ideal Sectional Boiler from American Radiator Company on house built in 1926
I am a licensed Master gasfitter and conversion burner in Md. I may not know the code in your location but I was taught a conversion burner for this type boiler required modification of the vent to use a horizontal or vertical draft diverter. The field Barometric burner should be removed. Also the Cast Iron coal damper at the base of the boiler should be sealed. As well as all the front doors. That being said, these old boilers were designed for coal which is a slow hot fire. The air flow from over-fire to chimney was a straight shot with very little heat surface absorption from the fire. In this configuration the gun burner efficiency can be 80%, but the overall efficiency of this boiler with this burner is more like 65%AFUE. This gun burner blower also increases the draft. But than this boiler was never rated for todays standards. My advice is install a new boiler designed for high eff gas 80-83% and correct all the other problems. Clean the chimney, or better yet, line the flue to comply with the code. It appears to me this would never have passed a gas permit inspection. My license would require me to shut the gas off and tag out this boiler until corrections were made. Questions? Your local gas company would have the answers as well as the local gov't dept. of licensing and inspections. If there is no record of a combustion test, consider the combustion setup was never done. Did my eye see the water heater gas pipe is trapped? It should not be trapped.
BE safe, put in gas and monoxide detectors. Sadly there are many victims in cemetery's who ignore the laws of physics. The codes we follow are fire and safety codes. they should be followed.
Good luck.
Lance
Re: Goodman GMNT060-3B
Transformers don't click. Unless they're on fire. But even then it's more of a pop.
9 hours is a long time to come up empty handed. What's the serial number on the Goodman furnace?
HVACNUT
Re: Goodman GMNT060-3B
You have 7 safeties wired between the w terminal on the thermostat and the gas valve. I would guess the inducer pressure switch is the most likely offender. Disconnect the switch and blow out the tubing connected to the switch and make sure they are all clean. Some of these safeties may be auto reset or manual reset.
You can also start the furnace and jumper the two switch wire to see if the furnace will continue to run.
DO NOT UNDER ANY CIRCUMSTANCES LEAVE THE JUMPER IN PLACE>
Re: Moving column cast iron radiator valve to outlet
The valve will function with reverse flow as you propose — just not at reliably. However, I have to ask… is this system piped all parallel (home run) flow to a manifold? Otherwise… you may have some unpleasant surprises.
Re: Goodman GMNT060-3B
Check and make sure that all ground wires in the furnace and all the way back to the electric panel have good connections. The ignition system uses the ground with micro voltage passing through it to prove the flame.
Also: has the flame rod been replaced?
Ironman