Re: How Do I Connect This Wire?
Effikal was the winner of the best product but was not a large enough company to stay in business and sold the rights to manufacture that best quality damper to Field Controls. They are pretty much the only vent damper that boiler and furnace manufacturers use today.
Here is the Vent Damper wiring discussion https://forum.heatinghelp.com/discussion/179453/
And my comment about it includes a wiring diagram.
Here is a possible wiring diagram that MAY help you. Post picture of the inside of the L8148E control you have, and the make & model number of YOUR boiler. It looks like a Hydro Therm but I may be wrong

The basic concept (Operational Logic) of an automatic vent damper is to close off a natural draft chimney in order to reduce the down time loss of heat from the boiler and inside the home safely. You don't need Draft Exhaust if there is no flame, because there is no dangerous exhaust when the burner is off.
This must be done Safely by not allowing the burner to operate if the damper is closed. No path for exhaust equals no burner operation.
To accomplish this Safely, the motor mechanism must have 24 V power always. This is to be able to close once the controls and safety devices determine there are no exhaust gases that require venting. The Motor is actually connected to what we call an Actuator. This is the motor and some switches, thermostats, and relays that by design, regulate when the damper may close. In the case of Field Controls and other control manufacturers like United Technologies, and Honeywell, the Molex plug terminal 1 and 4 are the terminals that have constant 24 volts for damper actuator operation. Once it is safe, 24 volts on terminal 1 and 4 will operate the motor until the damper is closed. The internal switches and relays will stop the motor from operating once the damper is in the closed position.
In this closed position the gas valve can not get power to operate the burner as long as the damper is in the closed position.
On a call for heat, IF all the other safety devices are satisfied that it is safe to operate the burner, the #2 terminal on the Molex connector will be energized with 24 volts and the damper motor will start to turn. The motor turns until the damper is in the full open position. Once fully open, the internal relays and switches stop the damper movement and the damper will stay in the full open position. Another set of switches and relays will then energize 24 volts to the #3 terminal on the Molex connector. This then sends power to the gas valve to open and allow the flame to establish. As long as there is a flame or other source of exhaust gasses (or perceived exhaust gasses... by high temperature in the exhaust pipe may be one way to tell) The damper can not close.
Most automatic vent dampers operate on this principle. Some have a spring opening and electric close, but most brands have a damper plate that rotates in the same direction making a 180° revolution every cycle or a 360° revolution every 2 complete burner cycles
Regardless, what ever brand or design of vent damper you have, the safe operation MUST be maintained by proper wiring, and free unobstructed path for the damper plate to open.
All the Professionals on this site fully understand this Sequence of operation (or Operational Logic) for vent dampers. Not all would like to deal with manually wiring of the device and prefer to just "Plug and Play" using a new control on a new damper ... where the now universally accepted "STANDARD DESIGN" makes wiring effortless and fool-proof in most cases.
I hope this helps you with your particular situation. If you feel up the the job, you now have all the information you need. If you are not comfortable with control wiring or do not fully understand the safety and importance of getting this right, then PLEASE GET A PROFESSIONAL that understands how this should work. Where do you find this technician? Go to you local Plumbing and heating or HVAC wholesaler and ask the counter man, "Which one of your customers is good at control wiring?"
They know who they are, because they are the guys that buy lots of controls and never return them because "This darn thing was bad out of the box"
Re: Outdoor Reset on Lochinvar vs. Taco
I would take HotRod’s recommendation for set up your control, and use the Taco relay as a facilitator for your zone pumps and system pump to operate on demand from T-stat. Hopefully this was helpful. If you do need further assistance, contact Taco tech support directly at 401-942-8000, ask for tech support
Re: New Boiler - Radiator Screaming
I had an issue with an install and Burnham got involved. You just have to pick the phone up and make that call. I believe the regional rep will contact the installer and both will come out to visit. Also the boiler manual had the installation instruction, pipe size etc and pictures of how it should be piped. I don’t understand the removal of 2 burners - you just took a big pot of water off the high burner and put it on the simmer burner. What does that do for performance? Call Burnham. https://www.usboiler.net/contact.html
Re: New Boiler - Radiator Screaming
I’m so sorry, but it seems like everything was installed by idiots.
-I agree, it was probably steam when built because that’s pretty much all they used in the early 1900s. And the near boiler piping appears to have been steam originally.
-some of the radiator supply pipes seem a little small, but that’s probably ok.
-ALL of the steam traps (located on the return side (bottom) of each radiator) have been removed and simple bleeder taps placed. This is the evidence that the system WAS converted from steam to hydronic at some point.
-regardless of steam vs hydronic, NONE of those air vents should have been installed on the radiators. It’s a 2-pipe system. Air vents are only for single pipe systems. )not including main vents, of course).
-back to the missing steam traps. Without those, steam will flood the return system rather than staying in the radiators. This will cause rads that either don’t heat or heat unevenly. It’ll also cause the system to hammer and bang.
-whomever installed the boiler did it so poorly that he should lose his license. I don’t even know where to start. Other comments have already addressed some of these. Any person who recommends increasing the pressure to 5 should immediately be told to leave and never return.
-my recommendation… don’t let these clowns back into your house yet. Quickly find a knowledgeable steam person from this website and PAY them for a complete assessment of your system. Then contact the current installer and see what they will do. Perhaps you can get them to just remove everything they installed. No matter what they say, I wouldn’t let them “fix” the problem. This very well could end up in court.
-purchase and read Dan Holohan’s book “so you have steam heat “ and read it a couple times.
-I’m so sorry this happened to you. I can’t imagine what you’re feeling right now. Contractors should make things better, not worse.
Good luck,
Todd
Re: Is this Air Admittance Valve Installed Correctly?
No he means remove it and immediately test the sink to see if it helps. Plugging the connection wont allow it to vent outward like a normal thru the roof vent.
ChrisJ
Re: Dunham 9a
I think this is a HeatingHelp.com first- a Dunkirk steamer where they didn't reduce the steam outlets from 2-1/2" to 2". Nice job.
Re: Hydronic in floor heat design
Uponor, Viega, Rehau, Mr Pex, Watts are some of the radiant tube manufacturers. Their websites will tell you how to submit a plan or contact the rep in your area.
Got any plumbing wholesalers near by? Ferguson, Hajoca, Standard, there are dozens of national brands. If they have a hydronics division you can probably get a design done.
Where are you located?
hot_rod
Re: Hydronic in floor heat design
I’m also looking at cost effective systems that are easy to install. I came across Hug Hydronics. Looks very simple and they will help design the layout and provide you with everything you need for the install.
Re: Is this Air Admittance Valve Installed Correctly?
In my state there is nothing legal about that installation. Air admittance valves are not allowed unless with a variance from the plumbing board.
No slip joints after the trap.
Re: Is this Air Admittance Valve Installed Correctly?
I don' know what type of soil piping you have in your house, ABS, PVC, Cast Iron, Copper, etc. You have to determine where the blockage is. If women use the sink, I have found on many occasions that hair balls build up before the trap and slow drainage.