Re: How to repair cement substance from oil boiler to oil burner
Who services the burner and boiler?
I can't tell from the pics, but the burner doesn't seem to be supported by a pedestal. Is there a piece of pipe or something propping up the burner?
The cement is around the air tube because the burner it replaced had a larger diameter air tube. Not exactly "by the book", but passable... last century.
That also doesn't look like a Firomatic valve. If it is, its really old.
What combustion numbers are you getting?
HVACNUT
Re: Should I be worried about what I am observing and hearing (radiant heat install in process)?
Without knowing exactly how much heat you will be needing above that floor I hesitate to make a blanket statement, but having retrofit my own old house and done some other design/install of floor radiant heat, this install is NOT going to work for anything beyond some minor floor warming. Even with a high water temperature and a correctly sized air cavity above the correctly installed insulation below, you will not be satisfied. Just for starters, the heat will not be evenly spaced on the floor and you will have warm and cold stripes.
Also, the higher the water temperature in the tubing, the more movement of the tubing which will mean noise as it slips back and forth through the holes in the joists and past those half-clip tube supports. Those are not the correct support for this type of installation.
This install is not even close to correct for Ultra-Fin either. I've installed that product too.
I don't know how the contract is drawn up, but stop this job immediately until you can be shown the design criteria for the job, how it is supposed to work and the operating parameters of the system. I don't know everything about floor heating but I know enough that this install at best will not work well and maybe even not at all.
Re: tie into existing boiler or get new tankless
You can use outdoor reset on the CI radiators using the boiler ODR setup. You can then use this to reset the lower cast iron reset temperature to an even lower reset temperature for the floor heat. “Reset the reset”
@HVACNUT has a good idea with keeping the CI radiators and just heat them when the floor is not enough on very cold days. If the first floor renovations call for removing the cast iron, perhaps you can relocate them and perhaps eliminate only one of two. Or perhaps use some panel radiators on a separate zone that can be staged for when the floor is not able to keep up with the extreme cold
Also that is a pretty big boiler for a 900 square foot 2 bedroom rancher.
Re: Boiler sight glass water condition
I can't say that I necessarily agree with Paul's instructions. The idea that adding water and immediately draining it, is detrimental to the boiler, is still a theory (I think). But having sludge and mud in your water is not good for anything. I would suggest putting a bunch of eight way in. Doesn't really matter if you're overloading, because this is only temporary. Jack up the thermostat and let the boiler run until it starts to steam. Shut boiler and wait a few minutes. As long as boiler is hot, the eight-way will do its thing. Wait 10 minutes or whatever, and then turn boiler back on until it starts steaming again. Repeat for 30 to 60 minutes. Afterwards drain, fill to the top of boiler, drain, fill drain fill until water comes out clear. If you happen to have a water transfer pump, will be quicker and easier. Once water is clear, fill to normal water level and add some eight way. Run the boiler immediately and let boiler Steam for a bunch of minutes, to boil out the oxygen. You may need to repeat a few times initially, due to sludge getting dislodge from the returns and things like that.
Re: Boiler sight glass water condition
don’t follow the directions. They want you to use too much.
At 896 sq ft that is a big boiler. I assume you have a big house.
I would try like 1/3 cup is all then see what happens. It will likely free up a lot of sediment and/or scale.
Be prepared to have to drain that off if your boiler surges (throws water into the mains resulting in a dramatic drop in the water line).
If you have to drain some or all the water due to that, add a little less when you refill.
Then let it be for a week or two. Then see if you can drain a little more to let out more chocolate milk.
The goal is to drain as little as possible to eventually get clean water
Your water is very clear in your photos. If you’re lucky you won’t have to do much
Re: Should I be worried about what I am observing and hearing (radiant heat install in process)?
Heat load divided by room sqft.
Most manufacturers show data for standard house setup. That is 3/4" subfloor with either tile or hardwood over it. Even if your subfloor is 7/8" planks, it won't change the heat transfer enough to worry about. So if your flooring close enough to standard, you don't need to worry about R value.
Most manufacturers also show how much insulation they want under the emitters to meet required btu output.
You can use the data from tables the manufacturer provides for loop spacing and number of emitters. I would aim for 140F water at design time which should get you good efficiency out of a condensing boiler.
It never hurts to add more emitters than required, this will only bring down the water temperature required which again helps with efficiency. It doesn't change how hot the floor will feel so not much drawback except a bit more material cost.
Kaos
Re: The "equalizer" is mis-named. It does nothing to equalize anything.
My drawings (which I haven't heard complaints about) show that the PSI is the same in the boiler, and at the boiler end of the wet return regardless of the existence of the "equalizer". Please explain that.
The pressure is the same even if there is no "equalizer". The "equalizer" is doing nothing to the pressure. We all have seen boilers without it, and somehow the water gets back into the boiler. This is because the main delivers close to the boiler psi to the start of the wet return. It's a little less which lets the water level be higher there, as in my drawing.
To @The Steam Whisperer
With or without it, the boiler pressure is present at the return pipe into the boiler. Look at my second drawing in my original post. Is there anything wrong about it? The "equalizer" is just another path that delivers the same pressure. It changes nothing. No?
To @109A_5
Without the Equalizer the pressure at point A will raise the water level at point C 27.68 inches per pound.
The "equalizer" does not decouple anything. In all my drawings, the pressure at the boiler and at the wet return's entry to the boiler are always the same, "equalizer" or no. Tell me where those drawings are wrong, and then tell me again what the "equalizer" is supposedly doing, thanks!
With or without the "equalizer", the
Re: Help choosing a new boiler (part 2)
I am unfamiliar with the IBC equipment. I worked mostly in Philadelphia PA and Southern NJ and never had a chance to see one in operation. I looked at the installation instructions for the SFB-99-1 and the SFB-120-1 and they appear to be a well built product. Their maintenance instructions take up 6 pages in their manual, This seems pretty comprehensive. If you have a reputable contractor that is familiar with the equipment, I see no reason to avoid this product. just make sure to have a professional maintenance completed every year.
Of course I can't indorse it without having looked at it up close or knowing about its longevity. I can say that this will not be your last boiler since none of the condensing boilers have a life expectancy of more than about 17 years, however with proper maintenance there is no reason that it can't have a useful life span of 20 years or more.
These new fangled things just don't last the way the old cast iron standing pilot boilers did. That is progress. Planned obsolescence in order to make you purchase something "Better" in the future.
Re: Should I be worried about what I am observing and hearing (radiant heat install in process)?
A bit on the high side for the warmer climate based on the envelope description but probably in the ballpark.
So most of your rooms are 10BTU/sqft, there are some a bit higher with the big room at 20.
The existing staple up will work no problem up to 10BTU/sqft. For the higher loss ones, I would go with either heat plates or ultra fin. Size the spacing of the heat plates to supply the /sqft load in those rooms.
It might also be a good idea to extra heat to the tiled spaces and have the balancing set for those to supply the bulk of the space heat. For example during the shoulder season the floor heat in my bathroom will supply enough heat without needing to run any other zones and keeps the tiles there nice and toasty.
Something to keep in mind that at 10BTU/sqft your floors will not feel warm even on the coldest day. They won't be cold and the house will be comfortable just don't expect toasty toes feeling. It is not real winter here yet, 25F outside, and my floors are at 75F.
Kaos