Re: new crown gas fired steam boilers - water needed every week
Let me re-word this "
- If the boiler has a leak above the water line, then steam could be leaving out the vent along with the flue gas. You may never see water on the floor if that is the case.
- If the boiler has a leak above the water line, then steam could be leaving out between the cast iron sections. That steam will then go up the chimney vent along with the byproducts of the combustion process. You may never see water on the floor if that is the case. (steam will go up the chimney as steam not water)
Re: new crown gas fired steam boilers - water needed every week
It's almost certainly leaking vents (radiator and/or main) and/or radiator valves. There is a much less likely chance that some radiator runout or section of main is leaking, but it's possible. It could be a wet return, especially if any of them are buried where you won't see the water.
Even a non-obvious leak could let out a gallon or so per day, and for those boilers, a gallon of condensate might be 1/2" to 1" of height on the gauge glass.
There's almost a zero chance that either boiler itself is leaking IMO
Edit: sorry everyone when I posted it wasn't showing me those earlier responses so I may have repeated what others said, I have to go back and look!
Edit 2: Yeah i was confused by that comment about the chimneys being plugged up and unused too!
Re: Curious about combustion analysis?
I rarely do combustion analysis on OLD atmospheric natural gas burners. There is so little to adjust on them. Maybe there are some adjustable air gate openings to the individual burners. Maybe not. And even if you make an adjustment on those primary air openings, the secondary air that enters the combustion chamber is so overwhelming that those adjustments do very little. Those burners are 68% efficient at best.
If you are looking at the flame and it is mostly blue, then it is burning correctly. If it is mostly yellow and has lazy smokey tips, then you need to find out what is wrong. I had one of those old American Standard boilers with the cast iron burners in my basement that I owned for over 18 years. I removed the burners and shook out all the rust only once. I didn't see any change in performance or combustion efficiency. I was young and stupid and playing with my Bacharach wet combustion kit on a gas heater, because I only worked on oil burners at the time. 68% combustion efficiency before and after. No change before and after.
Unless you get some wildlife to block the chimney those old things are pretty bullet proof.
Re: Asking for advice for combi boiler replacement and hydronic system upgrades
temperature rising quickly is usually caused by air locked boiler, air locked pump, or the boiler loop pump just isn’t spinning for some reason.
No power, locked rotor.
On some fire tube boilers I would hold the top relief valve open to blow out air that traps high.
I like purge and iso valves right in the loop where the tees are. This guarantees that you have purged the complete circuit. Assuming zone valves or actuators are all open.
hot_rod
Re: Testo 300
Did you get the right printer? I made the mistake of buying my Testo 300LL without the printer because I thought it would work with the printer from my Testo 320. I found that the 320 printer is not compatible with Testo 300. I believe the printer for the 300 connects by Bluetooth. With the Testo on I always turn the printer on and keep it around a foot away before I try to print anything. I don't remember doing anything special to connect it to the analyzer the first time I used it. Just make sure the Bluetooth is active on your Testo 300.
Re: What's this sudden change in radiator to condensate temperature relationship mean?
either bad probably main trap or the boiler is surging or priming and liquid water from the mains is heating the returns
Re: Curious about combustion analysis?
Yes, ideally a service tech does a test before and after service and prints the after service analysis showing that numbers are in spec for that unit. Sometimes there needs to be a tweak, some mod/cons adjust combustion themselves but the test must still be done! It's not rocket science, and if it is then you did something wrong!
Re: Rinnai RU199i Cycles On/Off then code 12
Hi all, just wanted to share my experience here. I've had a non-condensing Rinnai tankless for a few months now, and every time I used hot water in the washer or filled up my jacuzzi (large water demand for both), the unit would violently vibrate and shake my whole house. Sounded like someone was using a jackhammer downstairs. After monitoring the unit while drawing hot water, I noticed it would vibrate for a while and then the flame would go out slightly after. It would try a few more times to relight, but then it displayed error code 12- no flame.
After doing some digging online, I assumed it would be a vent issue since my gas line was sized properly and there was no issues with leakage or anything else. And sure enough, thinking about it, my big 90-gallon city garbage cans sit on the side of my house, next to the vent. I didn't think the cans would be close enough to the vent to cause an issue, but I decided to move the cans out of the way and try again. And sure enough, I turned on the jacuzzi, and there was no vibration whatsoever- the unit worked as expected.
I will update if anything changes, but I think the cans being so close to the vent was causing some of that exhaust gas to come back in the intake port for combustion, causing an issue with the air/fuel mixture, which caused the unit to shut off the flame as a safety precaution, which then gave me the error code 12. Remember that this is a non-condensing unit, meaning the vent is a pipe-in-a-pipe design, which I don't love for a few reasons but that is another story.
One of my friends has been a plumber his whole life, and he told me that the garbage cans absolutely could cause this issue. He even told me that this could possibly happen if it was very windy or even foggy outside, since the exhaust sometimes isn't able to be pushed out far enough in these conditions.
Additionally, the unit was previously set to 130 but I turned it down to 120 as well. As someone stated above, this could possibly cause issues with the flow rate or even short cycling the burner,
Just wanted to post my two cents here in case anyone else was experiencing this issue. Checking the vent would be my first go-to. Best of luck to all.
Re: HOT WATER BASEBOARDS, Stumped
Seems to be a typical flow-control valve issue. If not in those circulators you will need to install some.
Intplm.
Re: HOT WATER BASEBOARDS, Stumped
If the date codes on the 007-F5 are after 2003, then the discharge flange should accept an IFC. The part# for the IFC would be 0010-025RP. No need to purchase a complete pump with the IFC.
Hope this helps.
If you have any questions, please give Taco Technical Services a call during normal business hours Mon-Fri 8am-5pm EST 401-942-8000 and just ask for Technical Services.