Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
If our community has helped you, please consider making a contribution to support this website. Thanks!
Best Of
Re: More school lack of maintenance
So sad. They are clamoring to spend $266,000,000, but unable/unwilling to spend money on repairs. It's seems a universal phenomenon in larger institutions, repair is drudgery and wasteful, but a sexy new shiny building or system is money well spent (and will be maintenance free!!!).
Progress..
Progress..
Re: Bad press for Petro
It’s a really hard sell to keep oil and replace with another oil fired system. When PSE&G Nat gas prices are about $.74 cents for a Therm and oil is around $2.80 to $3.00 a gallon and rising again it’s a hard sell. Plus couple that with basically a mandatory burner service every year (funny but it’s hit or miss weather the oil companies actually do a good job of cleaning) it’s more expense.
As @Steamhead has said I seen first hand what low gas pressure is like, on the coldest day of 2016 when we went below 0 I had just finished putting a new boiler in and knew something was wrong with the fire, a quick test with a manometer showed manifold gas pressure at about 2.05” WC called PS they tell me they only guarantee 4” supply, however we weren’t even getting that, supply was only around 3.20 WC.
As @Steamhead has said I seen first hand what low gas pressure is like, on the coldest day of 2016 when we went below 0 I had just finished putting a new boiler in and knew something was wrong with the fire, a quick test with a manometer showed manifold gas pressure at about 2.05” WC called PS they tell me they only guarantee 4” supply, however we weren’t even getting that, supply was only around 3.20 WC.
1
Re: Working vents don't close
I am back from dinner with my family so I can finish this comment. If you are running a real one pipe system -- what allows the water to return to the boiler, the A dimension and the left over steam pressure left in the piping. You are going to 0 psig where are you getting the required A dimension at 0 psig -- you are not. The rads are not being emptied of all the condensate because you are not running a steam system you are running a scorched air system -- the furnance comes on the fan runs and everything shuts down until the next cycle. Steam is a living thing, in the mechanical sense ,it should never be shut down -to- 0 psig until summer. Run the system the way it was designed, heating season rolls around the boiler is always "alive" ,until the heating system is over.The deadmen were smart ,they understood passive physics ,and one pipe steam is a study in using the rules of physics to achieve what you need to happen without the aid of pumps or any other mechanical device. Read The Lost Art of Steam Heating it will answer all your questions. All the best from Canada Jack
Re: In Wall Convector Vent Removal
I would try a "basin wrench" before cutting holes.
Soak the threads several times with PB Blaster or Kroil.
You can put a pipe wrench on the handle of the basin wrench when you get a good grip on the vent. FWIW
Soak the threads several times with PB Blaster or Kroil.
You can put a pipe wrench on the handle of the basin wrench when you get a good grip on the vent. FWIW
0
Re: Delta-P situation specific
Delta P function is ideal for zoned systems either TRVs or zone valved systems. The ECM pumps are nice for replacing those 15-58 zone pumps at some point also, about 50% electrical consumption reduction withECM powered circulators.
hot_rod
0
In Wall Convector Vent Removal
My home was built in 1938 and has a number of convector radiators built in to the wall with an opening at the floor for intake air and a vent panel just under the window sill for the heated air to escape. A couple of these units have vents that need replacement but I cannot get enough access to get a wrench on them. The vents have an 8 point pattern for a socket but I cannot find a deep 8 point socket that will work. Does anyone have any history in attempting to remove vents from in wall convectors?
0
Re: Which bearings for my DA tank pump?
We have found that rebuilding them gives a shorter life than new as the plates will give up next and the cost for a new bottom end is not much more money.
As to bearing type the dealer should be able to get that from the build tag.
As to bearing type the dealer should be able to get that from the build tag.
0
Re: Old NRC Boiler suddenly has slow leak from (drain/relief ?) pipe. Why?
Having a bladderless expansion tank, it will fill partially with water after it has been drained until the incoming pressure of the water equals the air cushion in the tank.
The procedure is to turn off the fill to the tank, drain all the water out of the tank and then turning the fill valve on. This is not the fill valve to the boiler, but the fill valve on the line that goes to the tank from the boiler, usually a globe valve.
By the way, the air scoop (that green thing) that removes air from the boiler water needs an Taco 1/8" Hy-Vent. It doesn't work well at eliminating the air without one. My opinion.
It goes in that 1/8" hole where the plug is.
Feeding the air from the air scoop to the expansion tank is probably not as effective as venting to the atmosphere. I know what the original installers were thinking, that the air from the air scoop would displace the water in the expansion tank. Several companies made special valves to accomplish this. That is just my opinion.
I would replace the existing expansion tank with an Extrol 30 bladder tank with a 12 to 15 psi air charge if it is a multi story house. Buy it here: Supplyhouse. com and at the same time replace the 30# pressure relief valve .
These are cheap fixes. Less than $75.
The procedure is to turn off the fill to the tank, drain all the water out of the tank and then turning the fill valve on. This is not the fill valve to the boiler, but the fill valve on the line that goes to the tank from the boiler, usually a globe valve.
By the way, the air scoop (that green thing) that removes air from the boiler water needs an Taco 1/8" Hy-Vent. It doesn't work well at eliminating the air without one. My opinion.
It goes in that 1/8" hole where the plug is.
Feeding the air from the air scoop to the expansion tank is probably not as effective as venting to the atmosphere. I know what the original installers were thinking, that the air from the air scoop would displace the water in the expansion tank. Several companies made special valves to accomplish this. That is just my opinion.
I would replace the existing expansion tank with an Extrol 30 bladder tank with a 12 to 15 psi air charge if it is a multi story house. Buy it here: Supplyhouse. com and at the same time replace the 30# pressure relief valve .
These are cheap fixes. Less than $75.
Re: Replacing Taco 007 F5 circ pump need help
Yes, the motor should be horizontal. But, if it was working well before, don't worry about pumping toward the boiler and toward the expansion tank. For decades, B&G recommended that arrangement, and millions were successfully installed that way and are still working fine, including my 65-year-old boiler.
A pump doesn't know whether it is pushing or pulling. It just cares about its suction pressure and its differential pressure.
A pump doesn't know whether it is pushing or pulling. It just cares about its suction pressure and its differential pressure.

