Best Of
Re: Corroded connectors on new boiler.
And I'd say you can forget about the lifetime warranty.
Make sure the cap on the auto air vent is tight. Most SMART failures I've see have been because the air vent leaks and rusts through the outer tank.
Re: What To Look For When Replacing a Natural Gas Boiler
20 years is good. Probably would last longer but I hear parts are a little scarce.
Lochinvar, HTP, Viessman (maybe the best but $$$$)
others will comment. Stay away from Navien.
Re: Corroded connectors on new boiler.
Leaks at transition fittings is part of the reason I use unions when connecting appliances. Typically, Propress x male or female. Expensive, but they save time if there's a leak and the next guy that has to service the equipment will thank you, even though you may no longer be in this world.
Re: New House, New Problems- Introduction and seeking help on new to me steam
If your vapourstat shuts the system off when you trip it manually, it and its wiring is fine — but something else is wrong, like it isn't able to sense boiler pressure. Clogged pigtail. Clogged opening into boiler. Something…
Re: residential boiler outdoor temperature sensor how to test
If you have to replace it the correct control is a Honeywell T6031A1029. Supply House.com has them. $170. Temp range is -30—+90
Re: Getting rid of the old boiler sections
Any turns on the stairs? Open underneath? Can you add 2x4 supports, Hand truck and rope it? I've had to split many boilers to get them out, but I've never had to smash the cast iron. I have however been in a few basements where the old behemoth was just moved into a corner.
HVACNUT
Re: Want to add water to increase boiler system pressure but stumped
Correct. Black valve was closed. Open it so that the automatic fill valve can add the proper amount of water to whatever pressure setting it is preset for. 14-15 psi is normal. This should be done whether the boiler is running or not. If you are certain the auto-fill valve is working properly, let the system run a proper cycle and then bleed any air out of the system manually if you have bleeder valves out on the radiation system, baseboard etc. There should also be some automatic air bleeding mechanism near the boiler. Noise of air sloshing in the pipes is an indication that you need to fill and bleed. Also if there is no heat in the pipes during a call for heat to the boiler that also means there is probably no flow and somewhere the system is "air bound"— often at the circulator.
Re: Getting rid of the old boiler sections
If there's a little "room" in the job, Sub it out. You and your guys spinal discs will thank you down the road. Mad Dog
Re: residential boiler outdoor temperature sensor how to test
Just turn the knob all the way from one extreme to the other, it should click around the outside temperature number. That usually indicates it is working and accurate.
It's possible some other relay or control will be heard when you turn below the outdoor temperature. It is turning on the system.
hot_rod
Re: So fresh water carrying O2 causes corrosion. How about a HOT WATER TANK feeder into the boiler?
How is HW "Boiled in a HW tank?
pecmsg



