Best Of
Re: Is my piping for gas hot water radiator boiler fine?
How would circulation be induced in the bypass loop with the circulator outside of it?
Look closely at the factory diagram and you’ll see the difference.
Ironman
Re: Oil furnace issue
My brother is retired now but he lives in Richboro PA in Bucks County. This is the company he built F T YOUNG Associates 24/7 Emergency Service Available Call 215.357.4300. Not sure if the new owner goes to your location but it would not hurt to ask.
I think there is a contributor in your area that goes by @STEVEusaPA . I don't know for sure if he is even still working but he knows his stuff.
In Schuylkill County Pa I can’t believe that Electric Heat is less expensive that oil heat. And if the boiler can hold water to make hot water, you can certainly heat your home with it after the bad radiator is removed, repaired, or replaced.
Re: Oil furnace issue
Yes, in fact that's the best way to do it because at some point someone will probably want to put another radiator back there. New cast-iron radiators are expensive, but used ones are generally available.
bburd
Re: Oil furnace issue
It wouldn't take much work to disconnect and cap those pipes on either end of the radiator. Any competent plumber could do it.
bburd
Re: Identifying Mystery WM Boiler
No way to tell from this. Are there any names or numbers cast into the sections? Do you still have the jacket?
Re: Monoflo tee and pumping away
just to be clear the pump could be on the return and still be pumping away as long as the expansion tank is connected at or near the pumps inlet
Many mod cons have the pump on the return to help overcome pressure drop in the boiler
Here are two examples, one with pump at return, one at supply
Typical ci boilers have low pressure drop so tank at return, pump on supply is still “pumping away”
What is important is for the air purger to be at the boiler supply out, the hottest point in the system
hot_rod
Re: Unraveling Intermittent Boiler Flame Failures: The Ultimate Troubleshooting Guide for Technicians
Excellent video, as usual. Flame failures were the worst "pin pricks" a service tech can could witness. Imagine, you drive half way across the state, fix the problem, and the next day the custodian calls to report another flame failure. There were a few jobs where the problem was never fixed until the boiler/burner was replaced. No wonder I have little hair left on my head. Again, @RAY, another great video.
Re: Cool old stuff
I saw about 10 old steam systems that had that set-up that worked perfectly until someone tried to re-engineer the system or decided that he knew how to make it work better.
Re: steam boiler short cycling
Fix the valve leaks, but yes, that won't affect your pressure very much. But you don't want any steam leaks.
Do you know the EDR or total square feet of radiation in the building? Compare that to the "Net Square Feet of Steam" rating on the boiler and you will likely see the boiler is too large.