Best Of

Re: Severely corroded steam boiler

That's a drag about having to replace your boiler but you will likely be happier in the long run. I wouldn't put too much blame on the previous owner as they could have been completely ignorant of their system. It worked and that's all so many people notice. You could direct you anger at the home inspector. Do get those books mentioned by @109A_5 you'll be much more informed and happy. Good luck and keep us posted.

Re: Vertical Radiators

If you mix steel and cast iron on the same zone they will heat and cool differently and be difficult to impossible to balance. If it is just to make a space you pass through briefly more comfortable this probably isn't an issue.

Re: How many times do you cycle the boiler after replacing a part?

I agree with the above posts. Every job is different.

If you find the problem and it is clear cut that that was the problem you replace the part and 2-3 cycles should do it. I would start it and check a safety; start it check another safety etc so your checking the part and looking for other issues at the same time.

On intermittent problems you sometimes never know. Do some testing and then it's "try it"

Re: No heat this weeks case

@mattmia2 Exactly

@HomerJSmith Great diagnosis method. So may you techs just start replacing parts without diagnosing

Here is the link to the video

Re: How many times do you cycle the boiler after replacing a part?

Once I determine what the cause of the intermittent problem is, then fixing that item is good for me. I might try 3 to 5 cycles.

For example: You have an ignition transformer on an oil burner that fails to ignite the burner 3 to 5 times a week. it is probably caused by the transformer heating up and cycling off by the limit and then cycling back on in a short time. the warm windings on the transformer fail to make a spark. the burner goes off on safety. By the time anyone realizes there is no heat, the transformer cools off, so when the reset is pushed the burner lights properly with no tell tail sign of a problem.

After cycling the burner 20 times on the third call for the same problem you find the transformer fails to light the burner and it is hot to the touch. Viola! bad transformer. Replace the transformer and test the burner with one or two cycles. Problem solved. But that is because you are sure the transformer IS the problem.

That may not be the case in every intermittent problem though. If you are not 100% sure you got it right, like cleaning a flame sensor, and you are doing the lower cost repair first with the possibility that a more expensive repair may follow, then I may cycle several times. Every problem is different.

Re: pavilion radiant heat

I'd be thinking more like the heated seats in luxury automobiles. Heat the points where people are making contact, the floor, seatback and seat bottom. Don't try to warm the environment. I'd also try to insulate and wind-proof them.

I think with your back and feet kept reasonably warm and your front facing the fire you'd be comfortable. I have no idea how to engineer that though.

Re: pavilion radiant heat

when people talk about heating the great outdoors with radiant floors, you need to think more like snowmelt load numbers


some football fields have hydronic bench warmers. Better to heat objects by conduction than the great outdoors.
That’s what the radiant tube and mushroom heaters you see outdoors are doing. Radiating to anything in their line of sight. Turn your back on one and your front get chilled quickly

Re: Sq ft of steam:sq ft of EDR

This remains quite interesting.

The general assumption since the beginning of time is that you MUST size the boiler to the radiation. What if you sized it to the heatloss (with a suitable safety factor). Is it a certainty that such a setup will not function properly? It's still oversized for 99% of the heating season. What is a certainty is that Dave has come close to this with two pipe systems and he has not experienced any serious problems with it.

So, why do we still cling to the mantra of sizing to the radiation that has been passed down for decades?

LRCCBJLRCCBJ

Re: Sq ft of steam:sq ft of EDR

Properly measuring radiation, then selecting a boiler that is appropriately sized to that radiation is hardly "bean counting". And 33% pickup factor is plenty more than "barely good enough".

Can we all agree Jamie, just to set some common ground that a 2x boiler is too big and that a .5x boiler is too small? 😅