Best Of
Re: Need Help Troubleshooting Gas Boiler – Burners Not Igniting Consistently
Stop on the way home and pick up an electrical meter if you don't already have.
HVACNUT
Re: New jersey BFP required without feeder?
in new jersey a backflow is required on steam boilers feed line . To not have your backflow drip after manually feeding is to not remove pressure from the backflow so the real deal is to have a shut off before and after the backflow and use the out let valve for feeding this is nothing new and most who are not are being penny wise dollar foolish install this way and the customer ends up paying either way just less issues . It may seem uncommon but i have been doing it this way for many years yeah costs me 2 brass nipples and a ips ball valve big deal . this also holds true for house prv they should have a shut off before and after and unless you want o replace leave the pressure on to the valve and just use the outlet valve to shut the water off it will save you replacing the domestic prv being most prv fail after the pressure has been removed especially if a older valve .
clammy
clammy
Re: Insulating steam pipes in the basement
Insulating the pipes may help it fill the mains with steam more quickly during times of year when the off time between cycles is relatively short which will put less heat up the flue. Because there tend to be a lot of bypasses from the basement to the attic and leaks out around the sill, the heat that is lost to the basement doesn't do a great job of making it in to the living spaces.
Re: Boiler is gurgling and wont run
From the video
I think this is a copper water tube boiler? …and it sounds like it is kettling from lack of water flow thru the Copper HX. Probably want to get a pro in there to determine if the circulator is not operating or if the system is just air bound or is there a blockage keeping the water from moving freely thru the system.
Re: Triangle Tube Ceasing Operations
"…Lochinvar, VIessmann Burnham, Weil Mclain. none of these brands can really skip out of the US as they are either based here or their parent company is based in the US (viessmann owned by carrier)…"
Oh ye of little faith in the ability/willingness of corporations to do whatever they conclude will benefit their bottom lines. 😊
Re: Mystery 'U's\dips where Steam Mains meet Dry Returns, (and Water Hammer)
I am getting a sneaking suspicion that you may been knuckleheaded at some point back it the past. If you have two pipe convectors, the question becomes whether thay have traps on the outlets — or vents. If they have traps on the outlets, then they are expecting those returns to be dry - and at atmospheric pressure… and those odd U bends may very well have been much deeper water seals which someone decided they didn't need.
And your system will work a LOT better if they are restored!
Re: To switch or not to propane
How's that again? Maybe an old-timey atmospheric gas burner like your grille — but any form of power burner is going to use almost exactly the same amount of electricity as an oil burner — which isn't much.
Re: Best Boiler Cleaner
8-way boiler cleaner. Dump a bunch in. Fire up the boiler. Shut the boiler once it starts to make Steam. Let it stay hot for at least 30 minutes. Fire it up a little bit here and there, just to keep it hot, but don't let it steam too much. Drain and fill drain and fill drain and fill. Pour some more in (not to much), and fire up the boiler, to get rid of the oxygen. There will be those with different approaches. This is what I do and it seems to be pretty effective
Re: circulation pump recommendation
If it has zone valves or zone actuators, look at a delta P circ.
I've had excellent luck with the Grundfos Alpha series. Alpha 26-99 in you case. Assuming the pump you have now is sized correctly.
hot_rod
Re: Intermittent Burner ignition
yes. When you had the one time out of the 5 where there was no click, that is when you would use a very light touch with a jumper wire to connect R and W on the ST9103A to see if the thermostat is the problem (not a tap on the box). If the jumper wire starts the burner, the thermostat is the problem. If the very light touch with the jumper wire does not start the burner, then the problem is the ST9301A control board.