Best Of
Re: Good or bad? Tubing
"Water osmosis its way out?" Probably can't because a water molecule is too large.
You'd best believe that oxygen and osmosis really is…"a thing."
Re: Need a new plumber in Andover, MA
The part about the blocked return. Mains usually don't leak unless there is a problem causing a lot of liquid water to be in them. You need someone that knows steam well to figure out why the leak happened in the first place.
Re: Our emergency steam boiler replacement in Brooklyn last week looked like this:
Agreed. Off-brand wrenches are not an option anymore in this shop. Not for cheap. Not for free.
Ask my guys who've destroyed their knuckles or hit themselves in the head with the handle why.
Re: Viessmann cast iron boiler replacement.
Thats a shame. Looks good and I love how it's setup.
What are you planning on installing in its place?
Re: How to prevent hydronic piping from freezing?
It's even worse than you think. Most hot water systems have parallel flow paths — that is, the water has more than one way to go. If one of those paths is in a cold wall, as that starts to freeze it will get less water from the pump… and thus freeze more… and get less water… and so on. Until it's frozen shut.
As I said before: there are only three safe options: keep the place heated, use antifreeze, or drain.
Re: Correcting my 2 Zone Monoloop System (Need Help)
When you said that this is inefficient
It is because someone capped off some of the radiators. When you cap off a Monoflo® radiator you are restricting the entire one pipe main to the smaller orifice opening on the inside of the tee. When the system was installed in the 1950s (or when ever) it worked just fine because someone did the math and figured the restriction and heating value befro selecting the radiators and piping design. Somewhere along the line someone who did not do the math removed the path that some of that water is supposed to take.
In the upper right diagram I have marked up some hypothetical answers to the questions on the diagram.
In the lower right diagram I have also marked up what might happen when that Red radiator is removed and the supply and return pipes to that radiator are capped off. The restriction of each capped off tee will reduce to flow to the entire system. the first one that is capped off will do the most damage to the gallon per minute GPM flow rate. then each following capped off radiator will add to the restriction to the point where the amount of water flowing thru that one pipe main may be so slow that there is not enough heat for the rest of the radiators. When you read the book I posted on line above, you will see a rule of thumb about 1 GPM = 10,000 BTUs. If the loop that is inefficient is only flowing 2.5 GPM when it should be at 5 GPM, then you only have 25,000 BTUs for all the radiators in that loop. Not 50,000. Even though you have a big enough pipe, you are adding restriction three times with those three capped off radiators.
The correct way to remove a radiator from a MonoFlo® system is this:
This way the full GPM amount entering the Tee at one end of the branch can exit at the other Tee at the end of the branch… So I hate to say it but… you need to put everything back the way you found it then pipe in those bypass pipes.
Re: Correcting my 2 Zone Monoloop System (Need Help)
oh, right this was the thing i tried to explain to someone before and whoever it was just wasn't getting it.
Re: Correcting my 2 Zone Monoloop System (Need Help)
@LRCCBJ I believe that you mean this when you say the direction matters. In this illustration the arrow is in the correct direction for a Diverter tee to be placed on the radiator return. By placing that tee on the supply, it is WRONG. So the arrow matters only if you are placing it on the proper side of the radiator.
By restricting the flow entering the supply side of the radiator it as doing the same thing as capping off the unused radiator location. The entire one pipe main is restricted.
Re: Flame Retention Head for Weil Mclane Boiler
Or, if your house has natural gas, you can convert that boiler using a Carlin EZ-Gas burner.
Re: Another cold climate home with hydronic piping in exterior walls. Who does this??
The seal around the bottom of the wall and the plate and the floor is usually poor. pipes usually freeze not when it is the coldest but when it is fairly cold and there is a wind to push air in through openings in the building that are close to a pipe.