Re: Attached EDR vs Boiler SF of steam
I’d go with the 350.
you can always tighten up the envelope if needed
pecmsg
Re: steam radiators
How does the sight glass look when the boiler is steaming? If the water level is bouncing a lot the boiler may need to be skimmed and cleaned.
How much pressure is it running at?
Either way did you call the installer back?
Re: Monoflow System
Is this a new problem or has it always existed? If it used to work what changed? Do you get domestic hot water off the boiler?
Can you post a picture of the piping around the boiler and a picture of a Monoflow tee.
does the house not heat at all or is it sluggish? Was the 007 changed?
Are all the zones monoflow or just the main zone?
Re: Lochinvar boiler isn’t keeping up
I have six daughters and one son. They were all teenagers at the same time, so you can imagine what the hot water demand at my house was.
I installed an outdoor wood boiler just because of the domestic load. When we didn’t use the wood boiler during the warmer months, the entire family got by using a 50 gallon gas water heater. They learned to schedule their showers around mom and dad’s and each other.
I install a lot of boilers and indirects and an 80k btu boiler with a 40 gallon indirect is always more than enough for an average family. It’s only when there’s an unusual demand (like a car wash shower or a large hot tub) that more capacity is needed.
Ironman
Re: Mystery water leak - excess water take up problem
Installing and piping the boiler correctly according to the manufacturer’s instructions is extremely important on a steam boiler. They are the MINIMUM standard. Two risers with a drop header is an upgrade that’s well worth it as it will assure dry steam is sent to the system.
Make sure that whoever you select guarantees that they will at least pipe it per the manufacturer’s instructions as well as do the initial skimming.
Also make sure it’s done in black iron - no copper above the water line.
Ironman
Re: Lochinvar boiler isn’t keeping up
Yikes, those 3.5 gpm shower heads and the 6 gpm tub spout should be plugged into your math equation (time x flow volume) when figuring your dhw needs in a given use-scenario. Your boiler (and tank) is too small. Maybe…change shower heads? Co-ordinate showering and bathing habits? Ah, "first world" problems.
Re: Lochinvar boiler isn’t keeping up
your indirect tank is too small for your dhw load. you could get somewhat more capacity buy keeping the tank at a higher temp and using a thermostatic mixing valve but to make for example 2.5 gpm of hot water with a 65 f rise you need 81,000 btu/hr. (i used about 35 f incoming water temp and 100 f final water temp). once you have mixed enough cold water in that indirect tank to male the water noticeably colder, you aren't replacing as fast as you are using it. your boiler is 80,000 btu/hr in and around 70,000 btu/hr out. there uis also some lag between when you start using water and the aquastat in the tank sees the tank is cooling, then some more lag for the boiler to pre-purge, light, and get hotter than the tank and start adding heat to the tank.
the tables in the manual for the indirect are for conditions of incoming cold water that is much warmer and a boiler that is much bigger than in typical northern climate installations.
Re: Mystery water leak - excess water take up problem
2 out of 3 isn't bad.
It makes you wonder how #1 even stays in business if he has a business. Sounds like #2 would be the better choice.
I would expect #2 would have a complete and detailed quote although it may not be the lowest price.
Re: Mystery water leak - excess water take up problem
just drain it out the boiler drain until the level is right in the sight glass. fill it until you feel the riser get cold just above the boiler
Re: Can you please critique this boiler setup that was installed in my house two wks ago
and the advise given was not followed!
low bidder?
pecmsg