Re: Steam-one boiler or two, and, Atmospheric vs Gun
I'm not sure I see replacing either as economical. The newer ones you could put gas power burners on and replace when they fail individually, maybe put some better staging controls on them that will let you replace the boilers and connect to the existing controls when they do fail. If your balance is good it should still heat at a lower capacity with one boiler. If it does not you could close some radiator valves to reduce the system capacity until you can replace a failed boiler. I suppose it deserves better scrutiny to see if the 2 boilers were piped properly but it looks like whoever did it at least thought they knew what they were doing.
The welded header should have some threaded swing joints added at replacement so it isn't trying to pull the boiler apart but it seems to have held this long.
I thought that tank was for condensate management but looking more closely it is a shell and tube hx for either dhw or more likely a hot water loop.
Re: Is this a house trap?
Before you cut it out, make sure you're not going to allow sewer gases where you don't want them. Mad Dog
Re: Spanish power grid
@JDHW "I wonder why the industrial revolution really got going when steam power came along and we no longer had to rely on windmills and waterwheels? "
Easy. For the first time we had dispatchable power. Worried about "net zero"? Install a bunch of small fission plants and call it a day. 👍
Trying to use non dispatchable, variable output sources is creating problems for which we already have solutions.
Re: Descale combi boiler
Now that I see there are 2 boiler drains and there also must be at least 1 shut off you may be able to use them to circulate an approved descaling fluid through the WH and the Air handler coil.
Not the most effective set up but it could very well work…
Re: Mitsubishi Minisplit Inverter Board
I'm no expert with the mini splits but i know that with some of the Mitsubishi's the condenser motor causes the damage to the main board. The last unit i worked on i replaced the control board and it fried again. i only changed it without consulting Mitsubishi due to the 4 hour wait time for tech support (it was like 95 degrees out and a heat wave around the country). Bad idea. when I did finally get tech support they said that you need to change both the condenser motor and control board together or else they won't guarantee the new board. needless to say that I was pissed because that's a terrible design. how would one really put that together without some serious time spent on the unit control strategy. I can't say this is the problem but i had this more than once.
Re: Double dipping
Maybe you could stick some type of strainer on the tank HW outlet that is easily cleanable. But I wouldn't think the cleaning will take long.
Maybe you could stick a tee on the HW pipe with a full port valve on it and just let the water blast out for a good flush. You would probably have to stick a valve on the HW downstream of the tee when flushing.
Re: Double dipping
A short dip tube will prevent you from having any reasonable amount of hot water. The dip tube brings the cold water down to the bottom of the tank.
Re: Spanish power grid
This is a really interesting site. Lots of posters that love and know lots about heating systems - including steam. Then there is an advanced discussion about how power systems operate - wow. Here is a slightly different take on what inertia means in a power system.
Before the days of modern power electronics everything that rotates was connected to the grid synchronously and contributed to frequency stability and this includes motors as well as the generators in the power stations. Motors are considerable fraction of the load on most grids, industrial and domestic (fridges/freezers/aircon). There is no doubt than thousands of tons of spinning metal does contain lots of energy.
However, AC power systems are very sensitive to frequency. The transmission system has distributed inductance and capacitance in the form of cables and to maintain stable voltages discrete capacitors and inductors are dynamically switched in and out of circuits and transformer voltage ratios are changed. Because of this frequency sensitivity, AC systems are controlled to very tight frequency limits - 1% or better. In terms of keeping a grid stable you can only use 0.5% of the considerable stored energy.
What really keeps a traditional power grid stable is some generators operating at less than maximum output that can rapidly change power output in response frequency changes (the technical term is spinning reserve). Inertia provides the energy while this ramping up of power output takes place. This balancing must happen within seconds. Things like generators failing or transmission lines failing need to be take into account when deciding how much generation capacity is running as spinning reserve and where it is located in the system. This is what power system operators do all the time and it normally works. When it goes wrong it hits the news.
Power electronics come of age and there are new ways of connecting power sources - PV, wind, DC power links that don't contribute to spinning inertia. On the load side inverter motor drives are very common in the industrial and domestic equipment that don't contribute to spinning inertia. Electronic power supplies for LED lighting and computers take the same amount power regardless of voltage.
With high levels of renewable energy on power grids operators can end up with all their traditional generation acting as spinning reserve. Or worse, having to run generators on no load to maintain inertia and curtailing renewable sources.
The way out of this is to make all sources of power and loads frequency sensitive. You don't need much actual storage from spinning metal or batteries when everything is frequency sensitive. If there was a requirement for PV or wind turbines to operate at 95% output when the grid frequency is 50 or 60Hz there would be an automatic reserve of 5% if the frequency started falling.
Converting all sources and loads to frequency sensitive versions is easy to do technically but virtually impossible to do retrospectively. You could start with the bigger renewable installations.
Renewable sources are intermittent so will always require backup from some source of dispatchable power.
I wonder why the industrial revolution really got going when steam power came along and we no longer had to rely on windmills and waterwheels? There is a working textile mill that is maintained as a museum near Manchester airport (uk) which contains a time clock for workers to clock in and out. It is linked to the waterwheel driving the mill - so lower water levels = longer working hours!
John
Re: Cold water is hot due to amateur plumbing
The check was used on an aqua-booster to direct the incoming cold water though the coil to help keep it clear. But it will drop the pressure ….
You have a bypass ……. Shut off the hot water and then open a hot facet , if water runs out , then you have a bypass …
Hope this helps
Big Ed_4
Re: Steam-one boiler or two, and, Atmospheric vs Gun
It does take a lot more piping to make two boilers work on steam if run at the same time. Two boilers with manual changeover is ok. But to work automatically controlling condensate and water level is a issue. With 2 boilers you usually size them for 80% of the load. can probably go less. With 2 boilers the idle boiler fills with condensate as it acts as a condenser so now you need overflow traps and a feed tank. fed water isolation valves and controls. It gets $$$$
I would stay away from 2 unless size is an issue its a lot more work.