Best Of
Re: OT: Underground Wiring Options
" so within a week or so we hope to have our landscaper trench out at a depth of 18" "
Deeper than 18". The top of the PVC conduit needs 18" of cover, not an 18" trench. So if you use a 1-1/2" which is the best part of 2" Outer diameter and if it is in sand, you need a deeper trench.
I would and have done three conduits;
one high current 1-1/2 or 2" (in your case not populated)
one 3/4" or 1" for low current branch circuit and
one 3/4" or 1" for low voltage or communications type stuff.
With better protection of the wire the burial depth is less.
Re: Weil McLain Plus 80 indirect water tank
this is the vent. It appears to be a 1/4 mounted on a 1/2 adapter.
So this is on the boiler side, I just need to shut off the isolation valves on the boiler side, drain the water a few drops to relieve the pressure and then unscrew and replace right?
Re: heat pump manufacturers
So would Serge protection, high low voltage monitors, high low safety's, on and on. Who's paying for all that.
pecmsg
Re: heat pump manufacturers
What make sense and what they do is two different things. Gauges cost money x the # of units they sell makes it a no-go. Everything they do, cheap overseas capacitors, microchannel coils and 1 pole contactors that should be 2 pole and no pressure switches that could save a compressor on refrigerant loss……they won't put gauges on. They have a planned life cycle.
Re: OT: Underground Wiring Options
" So I'll assume that even though a low voltage and/or ethernet cable PLUS a pex could fit in the 3/4" pvc, it probably wouldn't be legal. But another 3/4" PVC line now would be a very wise choice. "
Even if you intend to put 1/2" PEX through 3/4" PVC you may be severely disappointed. 1/2" PEX has an outer diameter of about 5/8". Between the bend radius and any excessive glue that oozed into the conduit you may never get it through.
With electrical conduit work they only allow 40% (3 or more conductors), 53% (1 conductor) fill of the conduits available cross-sectional area.
As @mattmia2 stated you need to think much bigger. And use electrical conduit type radius not water pipe type radius.
Re: Discolored hot water / HTP PH 76-60 hot water heater installed 5 months ago
how did you test the chloride level, what is that number? What is the HTP limit?
Chlorine level tested with color strips?
hot_rod
Re: Hvac issue
Is this a HERS rated house? I've never heard of using an HRV as bath exhaust. They're either ducted to the living space, or ducted to the HVAC system. The normal practice is, if no HRV, then bath exhausts on timers to get the air exchanges. And this is one HRV serving three bathrooms, or each bathroom has its own HRV?
HVACNUT
Re: Lochinvar knight lockout
If the system is allowed to sit idle for a while, do the temperatures the system displays for Sensor 1 and Sensor 2 seem plausible (basically approaching ambient temps) ? If so I still think it's a water flow issue through the heat exchanger.
Re: Copper Nickel brake line for Roth P/U Tube.
When you say "sleeve", you mean running the tubing through the top of the double tap bushing? With a compression adapter to lock it in place? Is there a 1/2" rigid pipe threaded to the underside of the bushing so the tubing is forced straight down, rather than curling?
That rigid pipe (L copper or galvanized) can be used as the pick-up tube itself. No need to sleeve through. Just put a flare adapter on the top side, and its a sealed connection. I did my Roth that way.
HVACNUT
Re: Air in oil lines - potential tank relocation
How did he determine 'pump wasn’t pulling enough'?