Re: Oversized overtall chimney?
WAIT a second here. Right near the end of @dandub1960 's 11:04 comment above I read "distribution system is two pipe stream" .
That's fine, but makes all the comments above about mod/cons and so on quite irrelevant.
Now. Let's get back to some basics. Our OP's complaint appears to be that the house is draughty. Quite possible, given the age and the mention of metal framed windows — which were junk when they were installed and haven't improved with time.
There seems to be an impression that the problem is the oversize chimney. That probably isn't helping much, but is unlikely to be the major problem.
Assuming it is a significant problem, though, the only approach which will do much to address that problem is to restrict the chimney itself. Since there is a draught hood on the boiler, messing with the boiler air supply isn't going to address the problem, unless the boiler and chimney were placed in a sealed room. Difficult to do, but not impossible. Then you could add an outdoor air supply to that otherwise sealed room and let it go.
A cheaper approach will be to insert an appropriate sized liner in the flue, connected to the boiler draught hood, and seal between that and the flue (airtight seal at the bottom, screened at the top , or alternatively fill between the liner and the existing flue. Which I don't really recommend…
Re: Radiant flow not pushing fast enough
I suppose it depends on the design of the valve, not all valves shut off the hot port 100%. ASSE listed scald protection valves can shut off the hot 100%.
You should pipe up a few demos and report back :)
Regardless, this is how most if not all three way thermostatic manufacturers require a 3 way thermostatic to be piped, for hydronic mixing use. Piped this way it will work, piped in any other configuration you may not always get the results you expect.
hot_rod
Re: Radiant flow not pushing fast enough
Though not impossible, I don't think your problem is the circulator.
What happens on a call for heat?
Does the heat call get satisfied?
Does the boiler cycle on high limit?
What is the supply and return water temp?
I'm not sure your circulator is in the right place in relation to the thermostatic mixing valve(in fact i think it isn't but i'm not an expert on that).
Re: Oversized overtall chimney?
Again, forget about the equipment until you fix the thermal envelope of the structure. If you do, it will take far less boiler to do the job. If you just throw more equipment at the problem the utility will thank you for wasting so much energy and paying for it. You don't have to rebuild the house but close the barn doors then think about the boiler. BTW, the standard is to have a blower door test done with infrared thermography, which will generate numbers on just how leaky the house is as a baseline. Once you tighten it up, you can re-test, calculate the improvement, which can then be used to calculate the savings and if further improvement would pay for itself. You can install a TurboBlaster 2000 with the flux capacitor and inverter raterfrazzer but if the building is a sieve you're wasting money.
Re: Radiant flow not pushing fast enough
The circulator needs to be on the output of the mixing valve. Right now, when the hot water supply is above the setpoint of the mixing valve the valve will close and there will be no circulation.
Re: Near boiler piping/replacement boiler
Are you sure you have the right fuel selected for the analyzer.
Your efficiency numbers can’t be correct.
Re: Indirect Water Heater not level ?
Pride, professionalism, craftsmanship are all becoming old fashioned words, I guess🤔
hot_rod
Re: Indirect water heater drywell overflowing?
The well is leaking. Its very common on those tanks.
HVACNUT
Re: Pricing on refurbished cast iron radiators
Castrad brings new radiators in through Canada and NYC.
Not all radiators hold up to the 400 degree powder coat ovens.
If it has rubber seals??
hot_rod
Re: Square Plug wrench
If they used Teflon tape it might come out with a standard twelve point socket and a very large breaker bar. Pipe wrenches or fifteen inch adjustable wrenches work sometimes with cheater bars (pipe). Unfortunately, after twenty years the heads have a tendency to snap off when you try to remove them.
Like others suggested, plan on drilling and cutting the plug out.