What am I doing wrong
amazon has them for 66 bucks0
First get a,good thermometer to accurately check it. If it is bad you'll need it to check the new one to.
I questioned it last night when outdoor temps were pretty consistent in the read out. Check a,weather station close to you on line it's colder than 30 out .0 -
supply house has them for 46 bucks0
First verify that the one you have is actually bad. Assuming it is, get it replaced under warranty.0
it's still under warranty, I don't know if i told you, when i called up lochinvar to register it. They told me, no warranty, cause i am not a certified contractor0
That may or may not be enforceable. Check with your state department of consumer affairs.0
it's bad, it's not 30 outside, it's colder. i think my kitchen would be closer to being right, and that says 250
at this point in time, I just want a comfortable house0
I can call the dealer I bought it from, and ask for a new one, I'll try that tomorrow0
the weather station close to my zip code says 26, same as the kitchen outside thermoeter0
any settings i should change to be able to bring down the temp, and make it more efficient0
I set the shift reset to -5
system 114/114
flame 24%
out air 29
inside 73
basement radiator is cold0 -
my knee is killing me all day
probably from the up and down the stairs yesterday0 -
Last night your ohms were 32k at 25degrees it should have been around 40k0
it wasn't 25, I think it was 300
maybe it was 28, because it was between 2 numbers0
it doesn't matter the sensor is bad, and i need to replace it0
system 114/114
flame 38%
out 29
stat 730 -
Maybe. You need to put it in the same spot as a known good (or mostly good) thermometer, at two temps. Stick them both on the back porch for 10 minutes, then measure the resistance. Then put them both on a table inside for 20-30 minutes and measure again.maybemark said:it doesn't matter the sensor is bad, and i need to replace it
system 115/115
flame66%
out sensor 29
I changed other settings
out low -4
out high 60
sp low 140
sp high 95
out air shut 95
shift reset 00
When you change a bunch of things at the same time, your chances of figuring out what's going on go way down.
That 'sp high' number is probably a bit high.
The 'out air shut' definitely is
Some time tomorrow, you need to disconnect the outdoor air sensor, set the boiler to a fixed temp that you think might be about right, and run the tests I posted above. If the sensor tests out OK, the location is bad. Is there any chance the wall it's on has a hot pipe behind it?0 -
no way is the wall warm there
12" of brick0 -
out air shut is defiantly (what)
I just caulked the hole where the wire went thru, I did feel a tiny bit of cold, if cold is coming in, then hot is getting out
what numbers should i change then?0 -
Mark.....You should have gotten a service manual with that boiler. It has a description of all the parameter settings and what they are.0
I don't see any test you posted above
Paul, i have the service manual
it explains and shows defaults0 -
Kurt, I'll change everything back the way you told me0
I changed everything back how kurt told me the 1st time but I did put the shift reset to -2
I also caulked the hole with the wire
the sensor went up to 30, after i caulked the hole0 -
117/117
out 30
inside 73
flame 71%0 -
Shift the reset curve -15, and see if that target temp goes way down.0
it will, I'll try it now0
system 110/104
out sensor 30
inside stat 73
flame 20%0 -
Leave it there and let the house cool off.0
I think that's a good idea0
Even if the sensor is NG, you can still gain valuable info from it. It thinks it's 30 out, and 117 was to high a target....that's useful info.0
what would think a good target number is for 30?
things like this, someone who has been around, might have an idea. but, since I know so little, and the manual at times is like reading Greek.
Now, if you ask me about finish carpentry, I would know
thanks Paul0 -
There's no magic number. It's the number that holds the house at the perfect desired temperature.0
ok, I understand that0
If you find the house getting cold, move to -100
system 106/104
outside sensor 30 (we know thats wrong)
inside 73
flame 20%0
- 86.8K THE MAIN WALL
- 109 Chimneys & Flues
- 5.6K Gas Heating
- 966 Plumbing
- 385 Solar
- 15.3K Strictly Steam