What am I doing wrong
Comments
-
Is it possible that radiator is air-bound?0
-
Paul, I did bleed it a while ago, but that is a good possiblity0
-
Right0
-
You,have,to know the outdoor air temperature to read the table in the manual to know if it's okay.0
-
just checked, no air
when you said right, right for the radiator, or right for the sensor?
0 -
well, i have a thermometer in the kitchen that reads temp outside it reads 240
-
it is on the same wall as the flue, but i seperated them by about 10 feet or so0
-
Sensor.0
-
Whatcha got?0
-
i did not check yet, i was looking in the manual for the numbers, Ill go check now0
-
I got 32k on the outdoor sensor0
-
in the manual, where is the chart?0
-
well?0
-
it got up to 70 in the kitchen and still 72 in my bedroom where the stat is0
-
Page,35 install manual0
-
i found the chart, it's off, but not by alot0
-
actually, I think it's right on0
-
30* is 34 k
32* is around 32k0 -
my kitchen thermometer must be wrong0
-
Have you adjusted the valves on the radiators, at all?0
-
So is the kitchen thermometer wrong can't go by the sensor. Need an accurate separate thermometer.0
-
i don't know what is accurate or bad
but, if you follow the chart, the sensor is right as far as the ohm reading is
0 -
Paul, I only adjusted the valve of my bedroom, this is where i have the stat, and it did increase the temp in the kitchen and it did not lower the temp in the bedroom
even the living room is warmer, the fan kicked in behind the radiator, and the temp is 690 -
well, it's getting late, I need to walk the dog again,
thanks to all that helped me
0 -
It's way to hot in my house.
should I turn down the out door reset?
also, I have to move the outside sensor, it's only 3 or 4 feet from the flue0 -
the kitchen is almost 72
the living room is 70
the bedroom where the stat is, and i have the valve almost closed is 74
0 -
I am going to bring the shift reset down, i hope this is the proper way to bring the temp down in my house0
-
Check the Offset and Differential settings under temperature settings for SH1 (assuming you are using SH1 for your call for heat). if these are too narrow (specifically offset) it can cause a high limit shut down before the boiler has a chance to modulate.
can't remember what the defaults are but it is worth checking, Offset cannot be 0 unless it is a very very slow to respond system.0 -
oh wow, probably disregard my last, didn't realize how many more posts there were. Not sure if mine will be any help until I read of this.0
-
What temp is the outdoor sensor reading? This is important before you tweak anything.0
-
28, it is too close to the flue, I am moving it now0
-
I moved the reset down, before I saw your post, and before i moved the sensor.
I have my coat on, and will be going through 12" of brick0 -
Technically if it's colder outside than what is picked up by the sensor your supply temps would be to low, and house would be cooler if the curve is close. So you could shift more.0
-
I just drilled the hole about 10 ft from the flue, are you saying don't use it?0
-
The window is open upstairs, I guess it way too hot up there, I hope they turned off the valve, he has his g/f there, they sleep late, i don't want to call now
is opening the window bad for all that I am putting into this fine tune?0 -
What I was saying last night is the outdoor sensor can not be influenced by solar, and or other heat sources. It needs to be able to give an accurate reading of what the outside temperature really is. Otherwise the reset will be falsely dictating a water temp required to the system.
I'm not there so if flue exhaust is blowing on the sensor it should be moved. I'm sure depending on wind etc. it's not always an issue effecting the sensor IDK.
As for the tenant you may have done him a favor.0 -
it's all moved far away from the flue0
-
I left it alone for 15 or 20 min.
system 109/109
flame 86%
outside 30
inside 740 -
Where I moved the sensor, not only is it about 10 feet away from flue, but it is hiding behind a downspout
0 -
my place is so hot now
any suggestions on what I should do?0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements